Fellow Wrenches,<br>
<br>
The discussion about battery venting reminds me of a useful and
inexpensive program, <a
 href="http://pocketengineer.design.officelive.com/battery_ventilation.aspx">BattMV</a>,
for determining ventilation requirements per EN-50272.  EN-50272 is a
European standard used to determine how much air flow is needed for a
room, I don't know of a equivalent standard used in the U.S.  It takes
a surprising amount of ventilation.  For a 400-AH 48-volt L16 bank
charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the
%H2 down to 4%.  A 12-volt Zephyr vent is good for about 5 CFM!   If
you think you are venting enough, take some time and study this issue.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>