<div>I believe some of the discussions in the past had to do with the old 6kW imbalance limit that is used by several utilities on a 120/240 small residential single phase transformer. (don't remember the CA utility that came up with this)<BR></div>
<div>I had this discussion with our local utility (FPL) recently and they look at it on a case by case basis due to the many variables involved with 3 phase power distribution, such as the size and type of transformer(s), 3 phase loads on the premises, the harmonic distortion if any on a shared 3 phase transformer, core saturation, load balancing, etc.</div>
<div> </div>
<div>If you install a system in the FPL service area that is not balanced and either the harmonics or voltage is out of spec as a result (yes, they do test them), then you basically have 2 choices, balance the system or pay to upgrade the service drop and transformer.</div>
<div> </div>
<div>There has been talk of testing various 3 phase transformer(s) to determine the maximum/safe out of balance configuration by our local utility, however, again there are a lot of variables, so it would be difficult to cover every scenario.  And this usually is only an issue on small 3 phase transformer(s).</div>
<div> </div>
<div>I think that the 8,9,10TL 208v inverter has a load limiting ability that is incorporated in the inverter when you install 2 or more inverters, and it is programmable to limit the output of a single inverter to 6kW.  I believe you have to purchase the additional communication cables from SMA (cables available after the first of the year? or so I have been told).  Also, the design parameters seem a bit limited on the TL's.</div>
<div> </div>
<div>Jamie</div>
<div><BR></div>
<div><SPAN style="FONT-SIZE: 8pt"><SPAN style="COLOR: #3366ff"><STRONG><SPAN style="COLOR: #0000ff"><IMG title="signature image" border=0 alt="" src="cid:sigimg1@eb7d32f48d37e831d9d405f747e5cddf"></SPAN></STRONG></SPAN></SPAN></div>
<div> </div>
<div> </div>
<BLOCKQUOTE style="BORDER-LEFT: blue 2px solid; PADDING-LEFT: 8px; FONT-FAMILY: verdana; COLOR: black; MARGIN-LEFT: 8px; FONT-SIZE: 10pt" id=replyBlockquote webmail="1">
<DIV id=wmQuoteWrapper>-------- Original Message --------<BR>Subject: [RE-wrenches] feed-in imbalance<BR>From: "Marco Mangelsdorf" <<a href="mailto:marco@pvthawaii.com">marco@pvthawaii.com</a>><BR>Date: Fri, December 10, 2010 2:00 pm<BR>To: "'RE-wrenches'" <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>><BR><BR>
<STYLE>
 #wmQuoteWrapper /* Font Definitions */ @font-face  {font-family:Calibri; panose-1:2 15 5 2 2 2 4 3 2 4;}
 #wmQuoteWrapper @font-face  {font-family:Tahoma; panose-1:2 11 6 4 3 5 4 4 2 4;}
 #wmQuoteWrapper /* Style Definitions */ p.MsoNormal, #wmQuoteWrapper li.MsoNormal, #wmQuoteWrapper div.MsoNormal  {margin:0in; margin-bottom:.0001pt; font-size:11.0pt; font-family:"Calibri","sans-serif";}
 #wmQuoteWrapper a:link, #wmQuoteWrapper span.MsoHyperlink  {mso-style-priority:99; color:blue; text-decoration:underline;}
 #wmQuoteWrapper a:visited, #wmQuoteWrapper span.MsoHyperlinkFollowed  {mso-style-priority:99; color:purple; text-decoration:underline;}
 #wmQuoteWrapper p.MsoAcetate, #wmQuoteWrapper li.MsoAcetate, #wmQuoteWrapper div.MsoAcetate  {mso-style-priority:99; mso-style-link:"Balloon Text Char"; margin:0in; margin-bottom:.0001pt; font-size:8.0pt; font-family:"Tahoma","sans-serif";}
 #wmQuoteWrapper span.EmailStyle17  {mso-style-type:personal-compose; font-family:"Calibri","sans-serif"; color:windowtext;}
 #wmQuoteWrapper span.BalloonTextChar  {mso-style-name:"Balloon Text Char"; mso-style-priority:99; mso-style-link:"Balloon Text"; font-family:"Tahoma","sans-serif";}
 #wmQuoteWrapper .MsoChpDefault  {mso-style-type:export-only;}
 #wmQuoteWrapper @page Section1  {size:8.5in 11.0in; margin:1.0in 1.0in 1.0in 1.0in;}
 #wmQuoteWrapper div.Section1  {page:Section1;}

</STYLE>

<DIV class=Section1>
<div class=MsoNormal style="font-size:12pt;">Now that SMA has come up with their new 8, 9 and 10 kW transformerless line of single-phase 120/208V inverters, it brings up the question once again about how practical and wise it is to have one or two of these inverters feed into a three-phase service.  That is, is such an unbalanced feed much, if any, of a big deal?<o:p></o:p></div>
<div class=MsoNormal style="font-size:12pt;"><o:p> </o:p></div>
<div class=MsoNormal style="font-size:12pt;">I spoke to my consulting E.E. about this and he said that the large majority of utility-provided transformers are so large these days that an unbalanced feed of, say, a 10 kW inverter that only has output power through L1 and L2 should not present a problem.<o:p></o:p></div>
<div class=MsoNormal style="font-size:12pt;"><o:p> </o:p></div>
<div class=MsoNormal style="font-size:12pt;">Any other thoughts out there on this matter?<o:p></o:p></div>
<div class=MsoNormal style="font-size:12pt;"><o:p> </o:p></div>
<div class=MsoNormal style="font-size:12pt;">Thanks,<o:p></o:p></div>
<div class=MsoNormal style="font-size:12pt;">marco <o:p></o:p></div>
<div class=MsoNormal style="font-size:12pt;"><o:p> </o:p></div></DIV>
<HR>
_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><BR><BR>Options & settings:<BR><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR><BR>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR><BR>List rules & etiquette:<BR><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><BR><BR>Check out participant bios:<BR><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><BR><BR></DIV></BLOCKQUOTE></span></body></html>