Thanks all, this is helpful stuff. We'll see if the batteries are dead or not which would be a real shame since they're only 6 months old... -August<br><br><div class="gmail_quote">On Wed, Nov 17, 2010 at 7:32 PM, Mick Abraham <span dir="ltr"><<a href="mailto:mick@abrahamsolar.com">mick@abrahamsolar.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">Hello, August~<br>
<br>
Assuming that you don't want to buy a proper (but costly) 48 volt deep<br>
cycle battery charger, here are a few suggestions:<br>
<br>
Find this Craig's List seller in Redwood City:<br>
<br>
<a href="http://sfbay.craigslist.org/pen/bfs/2059216588.html" target="_blank">http://sfbay.craigslist.org/pen/bfs/2059216588.html</a><br>
<br>
and ask if they'll rent their 60 volt variable power supply to you for<br>
a couple of days. OR maybe you can beg or borrow a similar DC power<br>
supply closer to home & set it for 60 volts constant voltage. The amps<br>
on this one are tiny...only 5 amps...but maybe that's just what you<br>
need to gradually wake up that battery string. OR:<br>
<br>
++++++++++++++++++++<br>
<br>
Connect a string of 120 to 150 PV cells in right polarity to the<br>
battery...with nothing but a fuse or breaker and a watchful eye. As<br>
soon as things come up enough for the Sunny Island to go live, you'd<br>
want to disconnect the PV's then allow the SI to complete the<br>
recharge, since the unbridled PV string would have no voltage<br>
regulation. OR:<br>
<br>
+++++++++++++++++++++++++++<br>
<br>
The eight units could be temporarily unwired from the Sunny Island<br>
unit, then wired up series/parallel (2s4p) as a 12 volt pack. I advise<br>
that route instead of Ray's suggestion (about charging 12v increments<br>
within the 48v string) because you'll have fewer cell imbalance<br>
problems if you connect series/parallel so every two batts can level<br>
their combined voltage against the other pairs. If all eight units are<br>
wired series/parallel for 12 volt nominal, that pack could handle the<br>
output from a  60 amp 12v charger intended for deep cycle AGM's but if<br>
an automotive type 12v charger is all you can come up with<br>
readily...use that...since you're only trying to bootstrap the system.<br>
<br>
Happy Thanksgiving,<br>
<br>
Mick Abraham, Proprietor<br>
<a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br>
<br>
Voice: 970-731-4675<br>
<div><div></div><div class="h5"><br>
<br>
<br>
On Wed, Nov 17, 2010 at 7:54 PM, August Goers <<a href="mailto:august@luminalt.com">august@luminalt.com</a>> wrote:<br>
> Hi All Battery Friendly Wrenches -<br>
> We have a situation I haven't crossed yet - we have a Sunny Island grid tied<br>
> battery back system system with a 48 V battery bank consisting of eight 6<br>
> Volt AGM batteries. The charging breaker feeding the Sunny Island in the<br>
> main electrical panel was shut off by another contractor for about 3 months<br>
> which caused the Sunny Island to slowly drain the batteries until it fully<br>
> shutoff in order to protect the batteries. The bank now reads 24  Volts.<br>
> That's low! The Sunny Island is, according to SMA, powered directly from the<br>
> battery bank and won't even turn on. SMA tech support is recommending that<br>
> we charge the batteries and then turn the system back on.<br>
> Any ideas about the best way to charge a 48 V battery bank?<br>
> Thanks for your advice,<br>
> -August<br>
> --<br>
> August Goers<br>
> VP, Engineering<br>
><br>
> Luminalt Energy Corporation<br>
> 1320 Potrero Avenue<br>
> San Francisco, CA 94110<br>
> O: 415.641.4000<br>
> M: 415.559.1525<br>
> <a href="mailto:august@luminalt.com">august@luminalt.com</a><br>
><br>
</div></div><div class="im">> _______________________________________________<br>
> List sponsored by Home Power magazine<br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
><br>
> Options & settings:<br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
><br>
> List-Archive:<br>
> <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
><br>
> List rules & etiquette:<br>
> <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
><br>
> Check out participant bios:<br>
> <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
><br>
><br>
><br>
<br>
<br>
</div>++++++<br>
<div><div></div><div class="h5">_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br clear="all"><br>-- <br>August Goers<br>VP, Engineering<br><br>Luminalt Energy Corporation<br>1320 Potrero Avenue<br>San Francisco, CA 94110<br>O: 415.641.4000<br>M: 415.559.1525<br>
<a href="mailto:august@luminalt.com">august@luminalt.com</a><br>