<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META content="text/html; charset=iso-8859-1" http-equiv=Content-Type>
<META name=GENERATOR content="MSHTML 8.00.6001.18975">
<STYLE></STYLE>
</HEAD>
<BODY bgColor=#ffffff>
<DIV><FONT size=2 face=Arial>Hello Drake,</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>I think you should talk to a Sanyo Solar 
engineer to get accurate information. Every Sanyo and other brand UL 
listed modules must be dielectric voltage-withstand factory tested to 2 times 
system voltage plus 1,000 volts. I hi-pot test modules in the factory at 
3,000 volts so they will meet UL and also IEC standards. I megger field test 
arrays at 1,000 volts to find module, connector, and wiring problems. Megging at 
500 volts is ok, but it may not reveal wire insulation problems.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=drake.chamberlin@redwoodalliance.org 
  href="mailto:drake.chamberlin@redwoodalliance.org">Drake</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, November 17, 2010 7:36 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] Megger for array 
  testing</DIV>
  <DIV><BR></DIV>Hello Wrenches,<BR><BR>Looking through the archives on using a 
  Megger  for testing modules, it appears that it is best to keep voltages 
  to 500VDC.  I read all that I could find. <BR><BR>Talking to a Sanyo 
  representative, I was told that keeping test voltage under 600 would not void 
  the warranty or be an issue with UL.  He said they have tested Sanyo 
  modules up to 1000 VDC with no problems.<BR><BR>As a final test on a system, I 
  want to Megger test the array from the terminations at the inverter.  The 
  approach I'd plan to use is: 
  <UL>
    <LI>Clamp the Fluke 1587 negative to the enclosuer ground. 
    <LI>Put the positive test lead to the negative conductor from the array and 
    test 
    <LI>Put the positive test lead to the positive conductor from the array and 
    test </LI></UL>All tests would be done at 500 V.  The modules are 
  illuminated, but there is no significant reading from either positive or 
  negative terminal to ground. 
  <UL>
    <LI>The conductors would be removed from their terminals at the inverter and 
    be in free air. 
    <LI>The conductors would be continuous through the string of 10 Sanyo 210 
    modules. </LI></UL>My questions are: 
  <UL>
    <LI>Does anyone see a problem in this approach? 
    <LI>Since the array often has 500 VDC open circuit readings and shows no 
    indication of a fault whatever, would this test accomplish anything more 
    than the standard voltage to ground tests I've already done? 
    <LI>Is there any danger to diodes or other PV components? </LI></UL>Thanks in 
  advance.<BR><BR>Drake  
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>