<font size=3>Darryl:<br><br>
If Aurora can not verify that their inverters will not backfeed the DC
circuitry, then the circuits must be fused.  This too is specified
in Berdner's study.  We are in agreement.<br><br>
I think SMA is not the only transformer inverter with a no-backfeed
declaration.<br><br>
William<br><br>
<br><br>
At 05:48 AM 11/14/2010, you wrote:<br>
<blockquote type=cite class=cite cite>I never thought I would disagree
with William, I have the highest admiration for him, <br>
But the transformerless inverter has no seperation between grid and
array, no problem if everything is fused.  <br>
Darryl<br>
--- On <b>Sat, 11/13/10, William Miller
<i><william@millersolar.com></i></b> wrote:<br>
<blockquote type=cite class=cite cite><br>
From: William Miller <william@millersolar.com><br>
Subject: Re: [RE-wrenches] Head Spinning..(Con) fused.<br>
To: "RE-wrenches"
<re-wrenches@lists.re-wrenches.org><br>
Date: Saturday, November 13, 2010, 11:26 PM<br><br>
Eric:<br><br>
The best resource I have found on this subject is the white paper that
John Berdner wrote.  I have a copy on my web site: millersolar.com
under Resources.<br><br>
The general rule is no system with two strings combined needs
fuses.  Run the calcs as presented in the white paper for
verification.<br><br>
Just because circuits share a J-box or conduit is not a reason to
fuse.  Actual connection into an inverter is required before the
number of strings is tabulated.<br><br>
William Miller<br><br>
<br><br>
<br>
At 08:40 PM 11/13/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Wrenches,<br><br>
Can anyone shed guidance on the following for me? Should these strings be
fused:<br><br>
Total Modules: 44<br>
Total Strings: 4 strings of 11 <br>
Total Inverters: 2<br><br>
Modules: Silicon Energy 195 Watt @ 8A<br>
Each string feeding an independent MPPT input on an Aurora PVI 4.2kW
Inverter (there are 2 / Aurora)<br>
Inverter is transformerless (READ 690.35 (B))<br><br>
Each strings passes through a shared SolaDeck jbox, no combining, and
head directly to their own dedicated GE THN2261RDC DC Disconnect before
entering a dedicated MPPT input on the inverter.<br><br>
My big question is 690.9 (A) exception (b) which states I don't need ocpd
as long as "The short circuit currents from all sources do not
exceed the ampacity of the conductors."<br><br>
Because all four strings pass through the same jboxs and conduit before
reaching their disconnect and could potentially short together, should I
fuse each string? <br><br>
Or am I just up too late reading code....?<br><br>
Thanks for being a resource.<br><br>
-- <br>
Eric Thomas<br>
Solar Epiphany LLC<br>
(206) 919-3014<br>
<a href="http://www.solarepiphany.com/">www.solarepiphany.com</a><br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</a><br><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG - <a href="http://www.avg.com/">www.avg.com</a> <br>
Version: 8.5.449 / Virus Database: 271.1.1/3255 - Release Date: 11/13/10
19:34:00</blockquote><u>Please note new e-mail address and
domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/">http://millersolar.com<br>
</a>License No. C-10-773985<br><br>
-----Inline Attachment Follows-----<br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address:
<a href="http://us.mc519.mail.yahoo.com/mc/compose?to=RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br>
</blockquote><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.449 / Virus Database: 271.1.1/3255 - Release Date: 11/13/10
19:34:00</blockquote>
<x-sigsep><p></x-sigsep>
<u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>