Wrenches,<br><br>Can anyone shed guidance on the following for me? Should these strings be fused:<br><br>Total Modules: 44<br>Total Strings: 4 strings of 11 <br>Total Inverters: 2<br><br>Modules: Silicon Energy 195 Watt @ 8A<br>

Each string feeding an independent MPPT input on an Aurora PVI 4.2kW Inverter (there are 2 / Aurora)<br>Inverter is transformerless (READ 690.35 (B))<br><br>Each strings passes through a shared SolaDeck jbox, no combining, and head directly to their own dedicated GE THN2261RDC DC Disconnect before entering a dedicated MPPT input on the inverter.<br>

<br>My big question is 690.9 (A) exception (b) which states I don't need ocpd as long as "The short circuit currents from all sources do not exceed the ampacity of the conductors."<br><br>Because all four strings pass through the same jboxs and conduit before reaching their disconnect and could potentially short together, should I fuse each string? <br>

<br>Or am I just up too late reading code....?<br><br>Thanks for being a resource.<br clear="all"><br>-- <br>Eric Thomas<br>Solar Epiphany LLC<br>(206) 919-3014<br><a href="http://www.solarepiphany.com" target="_blank">www.solarepiphany.com</a><br>