<font size=3>Dave:<br><br>
All options satisfy the requirement.  Option 2 requires some
research to see if a) a smaller amperage main is available or b) your AHJ
will allow a plug on to be used as a main.  Some interpretations
indicate a hold-down is the most that could be required for sub-option
b).<br><br>
William Miller<br><br>
<br><br>
At 11:35 AM 10/31/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Content-Type:
multipart/alternative;<br>
<x-tab>        </x-tab>boundary="----=_NextPart_000_00A9_01CB7908.D3531D90"<br>
Content-Language: en-us<br><br>
AC Point of Connection could be to a backfed 20A DP breaker in the
existing GE TM3210CCU load center (100A MB with 100A busbar) if the SMA
SB3800 inverter was still available. But a SB4000 requires a 25A breaker
which violates the 120% rule with the existing panel.<br>
Comments on the options below. <br>
 <br>
#1) Go with another 240v grid tie inverter in the 3800W range, so we can
use a 20 Amp breaker. I see PV Powered and Kaco have 3500’s listed. Any
3.7, or 3.8kW inverters?<br>
 <br>
#2) Is it possible to either, change out the Main Breaker in the above GE
load center to a lower amperage MB, or add a Plug In Breaker. There is a
GE “feeder type” breaker # THQL2190 (90 A DP). Could we use this as the
main breaker for the load center above? It is listed as a 10KAIC
breaker.<br>
 <br>
#3) Swap out existing 32 space load center and replace with 150AML panel
with 100A MB kit.<br>
 <br>
Thanks,<br>
Dave Palumbo</font></blockquote></body>