<font size=3>Dana:<br><br>
I assume from your description that the top buss is lug fed.  
One would need to know the value of overcurrent protection feeding those
lugs to perform the calculations.<br><br>
Take the rating of a given buss (or feeder) and multiply by 120%. 
Subtract from the result the value of the breaker feeding that buss (or
feeder) and you have the maximum breaker size you can backfeed on that
buss (or to that feeder),<br><br>
William Miller<br><br>
PS:  The breakers labelled Main are not main disconnects.  They
are load breakers.  The split buss satisfies the "six
throws" rule.<br><br>
Wm<br><br>
<br><br>
<br>
At 05:19 PM 10/28/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Hi everyone,<br><br>
I'm working on two systems for homes that have the old style breaker
panels with no single main breaker. Instead, they have six breakers in
the upper part of the panel each labeled "main breaker," which
satisfies the six disconnect rule. The bus bar is split, with one of the
six upper breakers (60A) feeding a separate bus in the lower half of the
panel. It appears that the upper bus is rated for 200A, and the lower at
100A.  The sum of the main breakers does not exceed the 200A rating
of the upper bus. There are spare breaker slots on both the top and
bottom buses. How do I deal with 690.64 (B) (2) when there's no main
breaker? <br><br>
Thanks!<br><br>
Dana</font></blockquote></body>