    On 10/22/2010 10:25 AM, Allan Sindelar wrote:
    <blockquote cite="mid:4CC1C91E.7020006@positiveenergysolar.com"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      Ray,<br>
      I don't think Robin has posted anything, it just came in a
      conversation we had. As I understand it, service equipment must
      have nothing interfering with designated working clearance, within
      a few inches of depth allowed. With Outback, Magnum, and
      Xanschneider the breakers are on the front surface and are within
      the allowable depth. Midnite/Magnum and Midnite/Outback places
      them back toward the back wall with the inverter on the hinged
      cover; thus the battery enclosure technically sticks out too far.
      The XW Midnite panel doesn't have this issue, as it's a different
      layout. If necessary, one solution would be to mount the E-Panel
      several inches out from the wall surface.<br>
      Allan<br>
      <br>
      <div class="moz-signature">
        <style>p.MsoNormal, li.MsoNormal, div.MsoNormal { margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: "Times New Roman"; color: black; }a:link, span.MsoHyperlink { color: blue; }a:visited, span.MsoHyperlinkFollowed { color: blue; }span.il {  }div.Section1 { page: Section1; }</style>
        <div class="Section1">
          <p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
              style=""> Sindelar</b><span style="font-size: 10pt;"><br>
              <a moz-do-not-send="true"
                href="mailto:Allan@positiveenergysolar.com"
                target="_blank"><span class="il">Allan</span>@positiveenergysolar.com</a><br>
              NABCEP Certified Photovoltaic Installer<br>
              EE98J Journeyman Electrician<br>
              <b style="">Positive Energy, Inc.</b><br>
              3201 Calle Marie<br>
              Santa Fe, New Mexico 87507<br>
              <b style="">505 424-1112</b><br>
              <a moz-do-not-send="true"
                href="http://www.positiveenergysolar.com/"
                target="_blank">www.positiveenergysolar.com</a></span></p>
        </div>
      </div>
      <br>
      On 10/22/2010 10:56 AM, R Ray Walters wrote:
      <blockquote
        cite="mid:AB0030E8-F56A-4162-B171-3E7B10D8F351@solarray.com"
        type="cite">Why does the side mounted breakers make the Midnite
        non compliant?
        <div>Apparently I missed Robin's post on that.</div>
        <div>Or do I not want to know?<br>
          <div><br>
          </div>
          <div>Thanks,<br>
            <div><br>
              <div> <span class="Apple-style-span"
                  style="border-collapse: separate; border-spacing: 0px;
                  color: rgb(0, 0, 0); font-family: Helvetica;
                  font-size: 12px; font-style: normal; font-variant:
                  normal; font-weight: normal; letter-spacing: normal;
                  line-height: normal; text-indent: 0px; text-transform:
                  none; orphans: 2; white-space: normal; widows: 2;
                  word-spacing: 0px;">
                  <div>R. Walters</div>
                  <div><a moz-do-not-send="true"
                      href="mailto:ray@solarray.com">ray@solarray.com</a></div>
                  <div>Solar Engineer</div>
                  <div><br class="khtml-block-placeholder">
                  </div>
                  <div><br class="khtml-block-placeholder">
                  </div>
                </span></div>
              <div>
                <blockquote type="cite">
                  <div bgcolor="#ffffff" text="#000000">. Midnite
                    enclosures, with the breakers on the sides, are not
                    compliant, as Robin has acknowledged, but it has
                    never been a problem for us as the breakers are
                    still easy to access.<br>
                    <br>
                    <div class="moz-signature">
                      <style>p.MsoNormal, li.MsoNormal, div.MsoNormal { margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: "Times New Roman"; color: black; }a:link, span.MsoHyperlink { color: blue; }a:visited, span.MsoHyperlinkFollowed { color: blue; }span.il {  }div.Section1 { page: Section1; }</style>
                      <div class="Section1">
                        <p class="MsoNormal" style=""><span class="il"><b
                              style="">Allan</b></span><b style="">
                            Sindelar</b><span style="font-size: 10pt;"><br>
                          </span></p>
                      </div>
                    </div>
                  </div>
                </blockquote>
              </div>
              <br>
            </div>
          </div>
        </div>
      </blockquote>
    </blockquote>
    <br>
    <br>
    Allan, I don't remember saying our equipment is not compliant ?<br>
    The battery cabinet cannot obstruct access to the equipment.<br>
    The fact that the MidNite breakers are on the side actually<br>
    allows better access to servicing them.<br>
    <br>
    The front facing breakers have the connections on the back of<br>
    the breaker where you can't see them.  Our breakers are clearly<br>
    visible for all the connections compared to all of the alternatives.<br>
    <br>
    The battery boxes stick out 15" from the wall.  This is all the
    closer<br>
    you would be even if there was no battery box under the E-Panel.<br>
    <br>
    Robin<br>