<DIV><FONT size=2 face=Arial>Roof construction knowledge and roofing experience 
is essential if you are a solar designer and installer. You or people 
you work with must with have roof experience. If you do not have an 
experienced roofer in your organization, then you must work closely with an 
experienced roofing subcontractor (unless you like getting angry phone calls 
when it is raining).</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Framing and roofing a standing seam metal roof is 
not difficult. There is no need to guess or to ask inexperienced people 
what they think should be done. Good suppliers will provide specifications, 
instructions, and drawings and put you in touch with experts who can 
answer your questions.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>In 1996, I did the Unisolar standing seam roof 
at the University of California Irvine campus. See <A 
href="http://www.hamcontact.com/unisolar/roofapps.html">http://www.hamcontact.com/unisolar/roofapps.html</A> All 
we had was to start with was a 2nd floor deck and a contract with Southern 
California Edison (SCE) and the DOE UPVG (Utility Photovoltaic Group now called 
SEPA) who cost-shared the 5 kW new roof BIPV 
system. Unisolar provided standing seam metal roofing installation 
instructions but knew very little about roofing. I 
talked with McElroy, the manufacturer of the roofing Unisolar used for 
their SSR product. I also visited metal roofing jobsites during 
construction to see if anything new had been developed since I last did a metal 
roof a few years before. Then I designed the framing, building 
attachments, and the PV system and got SCE and Campus approval. I was 
concerned about my attachments to the roof deck knee-wall so I asked for the 
building structural drawings and really lucked out. The engineer who had 
designed the building still worked at his nearby office part-time even 
though he was 85 years old. (This old-timer still came to his office in a 
suit and tie to share his over 50 years of knowledge, experience, and 
wisdom. I love working in the construction industry.) He and I spent 15 minutes 
reviewing my design and he gave it his blessing.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>When I designed the solar roof, the 
University's Combustion Engineering Lab Director said that he might want to 
someday enclose the roof deck so we put in metal diagonal straps under the roof 
panels to brace the roof. The engineer said this was a good 
idea because it strengthened the roof in case of earthquakes.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>The construction went smoothly. We 
fastened the ledger and post attachments with lag bolts and attached the 
posts, beams and purlins. The SSR panels were laminated at the Unisolar factory 
and shipped from Troy, Michigan (a waste of time and money). When we started 
fastening the standing seam panels, I had to ask the University lab engineers to 
turn off the experimental natural gas fuel cell they were testing on the deck 
because the rising heat was cooking us on the roof like grilled hotdogs. We 
fastened clips 6 inches from panel ends and also every 12 inches using 
self-taping stainless steel screws (over-kill but it went fast). The slowest 
work was lapping the 12-feet panels over the 18-feet panels because each 
panel's standing seam had to be notched with a sidecutter and fit into 
place. The electrical work was conventional. The homerun in conduit went into 
the building to a Trace SWODE SW5548 that back-feeds to a 120 VAC breaker 
in a subpanel.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>A few years ago, I was on campus so I dropped 
by to inspect the system. The deck was enclosed and the space turned into 
offices and the Trace inverter was still working like new.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>----- Original Message ----- </DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=ntrei@1scom.net href="mailto:ntrei@1scom.net">North Texas Renewable 
  Energy Inc</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, October 22, 2010 7:47 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] The perfect 
  solar ready roof</DIV>
  <DIV><BR></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>Phil hits the nail on the 
  head, it sounds like we've both been down this road. Problem is it's not 
  always as simple as asking the roofers to do their job your way when you are 
  not signing their paycheck.</FONT></SPAN></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>I contracted a metal roof 
  PV installation a few years back but only got the job on the condition, by the 
  very fastidious homeowner, that I could verify that the installation 
  won't cause leaks or void the warranty on the <2 year old roof. He gave me 
  the roofers name and the roofing product and mfgr. I researched the 
  manufacturers installation requirements for our inland climate. Then I called 
  the roofer and asked if the 16" wide panels were installed per the mfgrs 
  specs. </FONT></SPAN></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>He proceeded to go 
  ballistic, telling me that if I put one module on 'his' roof he would void the 
  warranty. Even after sending him links to the S5 engineering test results 
  he refused to even talk to me. Finally the customer had to have a 
  long talk with the guy before he was convinced his roof had been installed 
  correctly. </FONT></SPAN></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>Bottom line you cannot 
  ever be certain about the quality of the installation by 
  someone else.  Besides, the homeowners insurance company 
  will have the last word on whether a PV mounted roof, found 
  across the street after a windstorm, was installed right or not. 
  </FONT></SPAN></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>CYA</FONT></SPAN></DIV>
  <DIV><SPAN class=468492414-22102010><FONT face=Arial>Jim 
  Duncan</FONT></SPAN></DIV>
  <BLOCKQUOTE style="MARGIN-RIGHT: 0px" dir=ltr>
    <DIV dir=ltr class=OutlookMessageHeader align=left><FONT size=2 
    face=Tahoma>-----Original Message-----<BR><B>From:</B> 
    re-wrenches-bounces@lists.re-wrenches.org 
    [mailto:re-wrenches-bounces@lists.re-wrenches.org]<B>On Behalf Of </B>Phil 
    Undercuffler<BR><B>Sent:</B> Thursday, October 21, 2010 10:29 
    PM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] The 
    perfect solar ready roof<BR><BR></FONT></DIV><FONT size=2><FONT 
    face=arial,helvetica,sans-serif>There is a big difference between standing 
    seam metal roofs and surface screwed metal roofs.  With surface screwed 
    (aka ProPanel or Ag Panel), screws penetrate through the roof skin and rely 
    upon a neoprene gasket under a cupped </FONT></FONT><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>washer to provide the weather-tight seal.  It 
    makes a pretty good seal and I've used it on my own home, but I don't think 
    I'd use it in Montana and I sure wouldn't try to attach PV over it. 
     The days of lagging L feet through the roof deck are thankfully 
    waning, and there is </SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>almost no practical way to use a flashed method of 
    mounting with surface screwed metal.</SPAN> 
    <DIV><FONT class=Apple-style-span 
    face="arial, helvetica, sans-serif"><BR></FONT></DIV>
    <DIV><FONT class=Apple-style-span face="arial, helvetica, sans-serif">With 
    standing seam roofs, the metal is formed into long U shaped pans. As each 
    pan is installed, the roofer nails L shaped "clips" to the deck with one 
    side of the clip butted up against the latest pan.  The next pan 
    is </FONT><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>butted up against the first, which captures the clip 
    between the two.  The </SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>upward facing legs of the U (and clip) are then 
    crimped and folded over, locking them together and </SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>forming a watertight seal</SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" class=Apple-style-span>. 
     I had a standing seam roof on my home in Cincinnati -- eighty years 
    old and still going strong.  </SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span><BR></SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>The biggest challenge with attaching PV to standing 
    seam roofs is not how well the modules are attached to the skin, but how 
    well the skin is attached to the structure.  Read the archives, but in 
    the end this really comes down to how close the roofer installed the clips. 
     This is where the 4" that Andrew mentioned comes into play (seems a 
    little excessive to me, but what the heck, I'm not a roofing dude and this 
    isn't something you want to do twice). </SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" class=Apple-style-span>The 
    dream scenario part comes in when you realize that YOU get to drive the bus 
    on how closely the clips are installed, as opposed to being presented with a 
    roof where you have no idea how many clips were used, what the spacing is, 
    or even whether nails or screws or bubble gum were used to connect them to 
    the deck.  The folks that make the S-5 clamp know metal roofs, and they 
    can help you determine what spacing works for your application.  Get 
    that into the contract, and make sure someone is on site providing oversight 
    when the roof is installed.</SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span><BR></SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>As far as some of the other options which were 
    presented -- yes, lagging into engineered I-beams is probably not a good 
    idea without checking with the manufacturer, but </SPAN><SPAN 
    style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>adding a second layer of ply doesn't suddenly make a 
    structural base for lag screws.  Lag screw pull-out resistance is 
    provided by inches of thread embedded into solid wood, and shiners 
    (fasteners that poke through the deck into the attic space) won't give any 
    real strength. If it's really 1/2" ply, adding a layer of 3/4 ply would give 
    you 1-1/4" of "wood" -- do the math and see if that's enough for your 
    climate. Adding 2x blocking would be an option if you have access to the 
    attic, but you need to make sure the loads transfer to the rafters 
    (I-beams), rather than concentrate on the deck.  Nailing the blocking 
    would be fine -- after all, that's how houses are built.  Lagging the 
    blocking as suggested by someone earlier, however, will not only be insanely 
    difficult but risk splitting the top chord of the beam.  If you split 
    that, I would immediately stop what you're doing and consult with the I-beam 
    manufacturer.  Big liability moment there.</SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span><BR></SPAN></DIV>
    <DIV><SPAN style="FONT-FAMILY: arial, helvetica, sans-serif" 
    class=Apple-style-span>But I'd avoid all that lags, nails, plywood and 
    blocking entirely, put on a standing seam metal roof with adequate clips and 
    install the PV with S-5 clamps.</SPAN></DIV>
    <DIV>
    <DIV>
    <DIV><FONT size=2><FONT 
    face=arial,helvetica,sans-serif><BR></FONT></FONT></DIV>
    <DIV><FONT size=2><FONT face=arial,helvetica,sans-serif>My 
    .02</FONT></FONT></DIV>
    <DIV><FONT size=2><FONT face=arial,helvetica,sans-serif><BR 
    clear=all></FONT></FONT>Phil Undercuffler 
    <DIV><BR></DIV>
    <DIV>
    <DIV><FONT face="arial, sans-serif"><SPAN 
    style="BORDER-COLLAPSE: collapse"><BR></SPAN></FONT></DIV></DIV><BR><BR><BR>
    <DIV class=gmail_quote>On Thu, Oct 21, 2010 at 11:52 AM, benn kilburn <SPAN 
    dir=ltr><<A 
    href="mailto:benn@daystarsolar.ca">benn@daystarsolar.ca</A>></SPAN> 
    wrote:<BR>
    <BLOCKQUOTE 
    style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" 
    class=gmail_quote>
      <DIV>andrew, 
      <DIV>a few comments added to your last email...</DIV>
      <DIV><BR></DIV>
      <DIV>
      <P 
      style="PADDING-BOTTOM: 0px !important; TEXT-INDENT: 0px !important; MARGIN: 0px; PADDING-LEFT: 0px !important; PADDING-RIGHT: 0px !important; PADDING-TOP: 0px !important">You 
      Wrote.... </P>
      <P 
      style="PADDING-BOTTOM: 0px !important; TEXT-INDENT: 0px !important; MARGIN: 0px; PADDING-LEFT: 0px !important; PADDING-RIGHT: 0px !important; PADDING-TOP: 0px !important">If 
      you ask me this is a dream scenario.  The scary thing about S-5!s is 
      that you rarely know how often the roofing panels are attached to the 
      decking and how well the decking is attached to the framing. <FONT 
      color=#0070c0>i'm not overly familiar with standing seam metal roofs (and 
      i know they are not all created equal) but aren't the screws holding the 
      metal roof panel to the decking visible at the bottom, at the top under 
      the vent cap and anywhere along the length of said panel?  i agree 
      about the 'unknown' attachments btwn the decking and the 
      framing </FONT>  In this case you can direct the roofer to 
      fasten the roof as often as you want.  I had a PE do an analysis for 
      a sure-fire acceptable attachment method for a standing seam roof given: 
      90 mph wind zone, 18" wide standing seam roofing panels, flush-mounted PV 
      array (modules to rail to S-5!s, no tilt legs), and his result was that if 
      the roofing panels are fastened every 4" along each seam you are in the 
      clear.  <FONT color=#0070c0>No doubt, that seems like quite a few 
      fasteners.</FONT>  He did not address the decking-to-framing 
      attachment, <FONT color=#0070c0>So worst case scenario, you get a 90+ mph 
      wind that takes the array, the metal roof <U>and the decking</U> for 
      a ride to the ground,</FONT><SPAN style="COLOR: rgb(0,112,192)"> (HAS 
      ANYONE SEEN OR HAD THIS HAPPEN?) </SPAN><FONT color=#0070c0>when it 
      is determined that the decking wasn't properly attached to the framing, 
      who do ya call?  PV installer, PE who stamped it, roofer?  I'm 
      not looking for a place to point fingers, I'm just looking for some 
      insight on this so i understand our responsibilities a bit better.  I 
      realize that it would be onerous to confirm the number and placement of 
      decking to framing attachments)  </FONT>but while the roof is off you 
      could add as many fasteners as you want.  If the structure of the 
      roof is in question I would definitely have a PE look at it and stamp the 
      plans before proceeding, but once you have everything under the roof 
      robust and approved, you are primed and ready for a worry-free, 
      penetration-free S-5!-to-standing-seam array install.</P>
      <DIV class=im>
      <P 
      style="PADDING-BOTTOM: 0px !important; TEXT-INDENT: 0px !important; MARGIN: 0px; PADDING-LEFT: 0px !important; PADDING-RIGHT: 0px !important; PADDING-TOP: 0px !important">In 
      another email string someone mentioned issues with S-5!s slipping down the 
      roof due to snow which is why I recommend attaching at every seam and 
      breaking out that torque-wrench when installing.  <BR 
      style="TEXT-INDENT: 0px !important"></P>
      <P 
      style="PADDING-BOTTOM: 0px !important; TEXT-INDENT: 0px !important; MARGIN: 0px; PADDING-LEFT: 0px !important; PADDING-RIGHT: 0px !important; PADDING-TOP: 0px !important">Good 
      luck!</P></DIV>...end of your msg</DIV>
      <DIV><BR></DIV>
      <DIV>in response to Kris' suggestion, don't the 2x6's need to be 
      toe-nailed into the 'rafters' on either side? or in this case toe-nailed 
      into the beams? which probably wouldn't be much different than the 
      'inadvisable' lag bolting into them.</DIV>
      <DIV><BR></DIV>
      <DIV>cheers,</DIV>
      <DIV>
      <DIV class=im>benn<BR><SPAN style="COLOR: rgb(0,32,96)"><FONT 
      face="'Franklin Gothic Medium'">DayStar Renewable Energy 
      Inc. </FONT></SPAN> 
      <DIV>
      <DIV><FONT face="'Franklin Gothic Medium'"><A 
      href="mailto:benn@daystarsolar.ca" 
      target=_blank>benn@daystarsolar.ca</A></FONT></DIV>
      <DIV><FONT face="'Franklin Gothic Medium'">780-906-7807 </FONT></DIV>
      <DIV><FONT face="'Franklin Gothic Medium'">HAVE A SUNNY DAY </FONT></DIV>
      <DIV><BR></DIV></DIV><BR><BR><BR><BR>
      <HR>
      </DIV>From: <A href="mailto:atruitt@gmail.com" 
      target=_blank>atruitt@gmail.com</A><BR>Date: Thu, 21 Oct 2010 11:30:40 
      -0600<BR>To: <A href="mailto:re-wrenches@lists.re-wrenches.org" 
      target=_blank>re-wrenches@lists.re-wrenches.org</A> 
      <DIV>
      <DIV></DIV>
      <DIV class=h5><BR>Subject: Re: [RE-wrenches] The perfect solar ready 
      roof<BR><BR><BR>If you ask me this is a dream scenario.  The scary 
      thing about S-5!s is that you rarely know how often the roofing panels are 
      attached to the decking and how well the decking is attached to the 
      framing.  In this case you can direct the roofer to fasten the roof 
      as often as you want.  I had a PE do an analysis for a sure-fire 
      acceptable attachment method for a standing seam roof given: 90 mph wind 
      zone, 18" wide standing seam roofing panels, flush-mounted PV array 
      (modules to rail to S-5!s, no tilt legs), and his result was that if the 
      roofing panels are fastened every 4" along each seam you are in the 
      clear.  He did not address the decking-to-framing attachment, but 
      while the roof is off you could add as many fasteners as you want.  
      If the structure of the roof is in question I would definitely have a PE 
      look at it and stamp the plans before proceeding, but once you have 
      everything under the roof robust and approved, you are primed and ready 
      for a worry-free, penetration-free S-5!-to-standing-seam array 
      install.<BR>In another email string someone mentioned issues with S-5!s 
      slipping down the roof due to snow which is why I recommend attaching at 
      every seam and breaking out that torque-wrench when installing.  
      <BR><BR>Good luck!<SPAN style="COLOR: rgb(0,102,0)"></SPAN><BR><SPAN 
      style="COLOR: rgb(0,102,0)"><BR>Andrew Truitt</SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"><BR>NABCEP Certified PV Installer<SPAN 
      style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">™</SPAN> (ID# 
      032407-66)</SPAN><SPAN style="COLOR: rgb(0,102,0)"></SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"><BR>Truitt</SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"> </SPAN><SPAN 
      style="COLOR: rgb(0,102,0)">Renewable</SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"> </SPAN><SPAN 
      style="COLOR: rgb(0,102,0)">Energy</SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"> </SPAN><SPAN 
      style="COLOR: rgb(0,102,0)">Consulting</SPAN><SPAN 
      style="COLOR: rgb(0,102,0)"><BR>(202) 486-7507</SPAN><BR><A 
      href="http://www.linkedin.com/pub/andrew-truitt/8/622/713" 
      target=_blank>http://www.linkedin.com/pub/andrew-<SPAN>truitt</SPAN>/8/622/713</A><BR><BR><SPAN 
      style="COLOR: rgb(0,153,0)"><SPAN 
      style="FONT-FAMILY: Calibri; COLOR: rgb(31,73,125); FONT-SIZE: 11pt"></SPAN></SPAN><BR><BR>"Don't 
      get me wrong: I love nuclear energy! It's just that I prefer fusion to 
      fission. And it just so happens that there's an enormous fusion reactor 
      safely banked a few million miles from us. It delivers more than we could 
      ever use in just about 8 minutes. And it's wireless!"<BR><BR>~William 
      McDonough<BR><BR><BR><BR><BR>On Wed, Oct 20, 2010 at 2:32 PM, Kristopher 
      Schmid <<A href="mailto:solman@legacysolar.com" 
      target=_blank>solman@legacysolar.com</A>> wrote:<BR>
      <BLOCKQUOTE><FONT color=#0000ff>What about screwing in double 2x6s flush 
        to the roof deck between the beams where your feet will attach and lag 
        bolting into that?  Definitely check with the beam manufacturer 
        first, though.</FONT><BR> <BR><FONT 
        color=#0000ff>Kris</FONT><BR>Legacy Solar<BR>864 Clam Falls 
        Trail<BR>Frederic, WI 54837<BR>715-653-4295<BR><A 
        href="mailto:solman@legacysolar.com" 
        target=_blank>solman@legacysolar.com</A><BR><A 
        href="http://www.legacysolar.com" target=_blank>www.legacysolar.com</A> 
        <BR></BLOCKQUOTE>
      <BLOCKQUOTE>
        <BLOCKQUOTE>-----Original Message-----<BR><B>From:</B> <A 
          href="mailto:re-wrenches-bounces@lists.re-wrenches.org" 
          target=_blank>re-wrenches-bounces@lists.re-wrenches.org</A> [mailto:<A 
          href="mailto:re-wrenches-bounces@lists.re-wrenches.org" 
          target=_blank>re-wrenches-bounces@lists.re-wrenches.org</A>] <B>On 
          Behalf Of </B>Scott McCalmont<BR><B>Sent:</B> Wednesday, October 20, 
          2010 12:00 AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: 
          [RE-wrenches] The perfect solar ready roof<BR>In general, you 
          shouldn't drill or cut the flanges on engineered wood beams. I think 
          that eliminates lag screws into the rafters. They probably wouldn't 
          have the same pull-out strength as a lag screw into a conventional 
          rafter, either. <BR><BR>Scott<BR><BR>On Oct 19, 2010, at 7:58 PM, 
          Chris Daum wrote:<BR></BLOCKQUOTE></BLOCKQUOTE><BR><BR><BR>
      <BLOCKQUOTE><SPAN 
        style="TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: medium Helvetica; WHITE-SPACE: normal; LETTER-SPACING: normal; WORD-SPACING: 0px">
        <DIV lang=EN-US>
        <DIV dir=ltr align=left><FONT color=#800000 
        face="Comic Sans MS"><SPAN>Dear Wrenches:</SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 
        face="Comic Sans MS"><SPAN></SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 face="Comic Sans MS"><SPAN>I 
        have a composite (shingle) roof at hand, and the owner wants to upgrade 
        it to a metal roof and install a 5kw+ array on it.   The 
        rafters are those (sort of) particle board I-beams covered with 1/2" 
        plywood (and shingles).  What's the best metal roofing you could 
        suggest--and would you beef up the wood to lag into?</SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 
        face="Comic Sans MS"><SPAN></SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 
        face="Comic Sans MS"><SPAN>Thanks for all your 
input.</SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 
        face="Comic Sans MS"><SPAN></SPAN></FONT></DIV>
        <DIV dir=ltr align=left><FONT color=#800000 face="Comic Sans MS"><SPAN>
        <DIV align=left>
        <DIV align=left><FONT color=#000080 size=2 face="Comic Sans MS">Chris 
        Daum</FONT></DIV>
        <DIV align=left><FONT color=#000080 size=2 face="Comic Sans MS">Oasis 
        Montana Inc.</FONT></DIV>
        <DIV align=left><FONT color=#000080 size=2 
        face="Comic Sans MS">406-777-4309</FONT></DIV>
        <DIV align=left><FONT color=#000080 size=2 
        face="Comic Sans MS">406-777-0830 fax</FONT><FONT color=#000080 size=3 
        face="Comic Sans MS"><SPAN></SPAN></FONT></DIV></DIV></SPAN></FONT></DIV>_______________________________________________<BR>List 
        sponsored by Home Power magazine<BR><BR>List 
        Address:<SPAN> </SPAN><A 
        style="COLOR: blue; TEXT-DECORATION: underline" 
        href="mailto:RE-wrenches@lists.re-wrenches.org" 
        target=_blank>RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options & 
        settings:<BR><A style="COLOR: blue; TEXT-DECORATION: underline" 
        href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive:<SPAN> </SPAN><A 
        style="COLOR: blue; TEXT-DECORATION: underline" 
        href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
        target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
        rules & etiquette:<BR><A 
        style="COLOR: blue; TEXT-DECORATION: underline" 
        href="http://www.re-wrenches.org/etiquette.htm" 
        target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out 
        participant bios:<BR><A style="COLOR: blue; TEXT-DECORATION: underline" 
        href="http://www.members.re-wrenches.org/" 
        target=_blank>www.members.re-wrenches.org</A><BR><BR></DIV></SPAN></BLOCKQUOTE><BR><BR>_______________________________________________<BR>List 
      sponsored by Home Power magazine<BR><BR>List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org" 
      target=_blank>RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options & 
      settings:<BR><A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
      <A 
      href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
      rules & etiquette:<BR><A 
      href="http://www.re-wrenches.org/etiquette.htm" 
      target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out 
      participant bios:<BR><A href="http://www.members.re-wrenches.org" 
      target=_blank>www.members.re-wrenches.org</A><BR><BR><BR><BR><BR 
      clear=all><BR>-- 
      <BR><BR><BR><BR></DIV></DIV>_______________________________________________ 
      List sponsored by Home Power magazine List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org" 
      target=_blank>RE-wrenches@lists.re-wrenches.org</A> Options & 
      settings: <A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A> 
      List-Archive: <A 
      href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A> 
      List rules & etiquette: <A 
      href="http://www.re-wrenches.org/etiquette.htm" 
      target=_blank>www.re-wrenches.org/etiquette.htm</A> Check out participant 
      bios: <A href="http://www.members.re-wrenches.org" 
      target=_blank>www.members.re-wrenches.org</A></DIV></DIV><BR>_______________________________________________<BR>List 
      sponsored by Home Power magazine<BR><BR>List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
      & settings:<BR><A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
      <A 
      href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
      target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
      rules & etiquette:<BR><A 
      href="http://www.re-wrenches.org/etiquette.htm" 
      target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out 
      participant bios:<BR><A href="http://www.members.re-wrenches.org" 
      target=_blank>www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR></DIV></DIV></DIV></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>