    Wrenches:<br>
    The situation: Two Grundfos SQFlex stand-alone pump systems, each
    with IO101 AC switch and CU200 controller in a remote application,
    filling a common tank two miles away for a community water supply.
    As a float switch can't be used to shut off the pump when the tank
    is full, the mainstream pump company doing the full community water
    supply installation (we have contracted only the pumps and PV power)
    has specified and supplied a pressure transducer-based system called
    P2Flow (<a class="moz-txt-link-abbreviated" href="http://www.p2flow.com">www.p2flow.com</a>) as a stand-alone way to control pump
    operation using a high-accuracy pressure transducer at the well
    outlet to signal a programmable controller. The P2Flow control unit
    draws 40mA when "on" and 30mA when "off", running on 10-30 VDC,
    which I am supplying with PV. As 40mA @24 hours is one Ahr/day, I
    have specified a 10W module and 7 Ahr sealed battery at each well.<br>
    <br>
    The problem: The float switch control Grundfos CU200 controller is
    preprogrammed to "close on rise" - that is, continuity between the
    terminals turns the pump off. The P2Flow system is "close on fall",
    as would be used to directly interrupt continuity of power to the
    pump when the tank is full. These are opposite logics. How can I
    reverse the action in the simplest (for reliability) and
    lowest-power way? I could add a second relay to reverse the action,
    but that would increase the power consumption beyond what this tiny
    power supply can produce: at 0.9 VA coil current rating, an ice-cube
    relay would draw double the current of the P2Flow unit itself. I
    have heard of using a 10K ohm "pull-up resistor" but have no idea
    how it works. <br>
    <br>
    Any good ideas, please?<br>
    <br>
    <div class="moz-signature">-- <br>
      <style>p.MsoNormal, li.MsoNormal, div.MsoNormal { margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: "Times New Roman"; color: black; }a:link, span.MsoHyperlink { color: blue; }a:visited, span.MsoHyperlinkFollowed { color: blue; }span.il {  }div.Section1 { page: Section1; }</style>
      <div class="Section1">
        <p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
            style=""> Sindelar</b><span style="font-size: 10pt;"><br>
            <a href="mailto:Allan@positiveenergysolar.com"
              target="_blank"><span class="il">Allan</span>@positiveenergysolar.com</a><br>
            NABCEP Certified Photovoltaic Installer<br>
            EE98J Journeyman Electrician<br>
            <b style="">Positive Energy, Inc.</b><br>
            3201 Calle Marie<br>
            Santa Fe, New Mexico 87507<br>
            <b style="">505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank">www.positiveenergysolar.com</a></span></p>
      </div>
    </div>
  </body>
</html>