<font size=3>Daryl:<br><br>
I believe the Mate is the best option to start a generator and exercise
control over generator battery charging. Outboard units have proven
to be less intelligent about charging functions. I recommend you
work out your problems with the Outback and use the Mate.<br><br>
What kind of problems have you been having?<br><br>
William Miller<br><br>
<br><br>
At 12:36 AM 10/15/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Can anyone point me in the
direction of a good, autonomous generator auto<br>
start. We have an off grid system with a substantial array (8 kw)
and<br>
using a dual OutBack 3648 PP, but we have not had good luck with
generator<br>
auto start using the relays and Mate within the OutBack equipment. I
would<br>
like to try something whose function would be to sense battery voltage
and<br>
start based on adjustable settings. Any favorites out there? The
customer<br>
has a new Onan 12 kw gennie.<br><br>
Thanks,<br>
Daryl<br>
</blockquote>