<html><body bgcolor="#FFFFFF"><div>That sounds right, which means that the existing wiring between the service disconnect and the transfer switch may also need to be evaluated since it will now have sources available at both ends. The rule applies to all bus bars and conductors "upstream" of the interconnection point  as I understand it.<br><br>Jason Szumlanski</div><div>Fafco Solar</div><div><br>On Oct 12, 2010, at 6:25 AM, "Mark Frye" <<a href="mailto:markf@berkeleysolar.com">markf@berkeleysolar.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>

<div dir="ltr" align="left"><span class="171243404-12102010"><font color="#0000ff" size="2" face="Arial">It doesn't sound like you have a "supply side connection". It 
sounds like you have a "load side connection" which is upstream of the transfer 
switch but still downstream of the service disconnect.</font></span></div>
<div dir="ltr" align="left"><br><span lang="en-us"><font size="2" face="Arial">Mark 
Frye</font></span> <br><span lang="en-us"><font size="2" face="Arial">Berkeley Solar 
Electric Systems</font></span> <br><span lang="en-us"><font size="2" face="Arial">303 
Redbud Way</font></span> <br><span lang="en-us"><font size="2" face="Arial">Nevada 
City,  CA 95959</font></span> <br><span lang="en-us"><font size="2" face="Arial">(530) 401-8024</font></span> <br><span lang="en-us"></span><a href="http://www.berkeleysolar.com/"><span lang="en-us"><u><font color="#0000ff" size="2" face="Arial">www.berkeleysolar.com</font></u></span></a><span lang="en-us"><font size="2" face="Arial"> </font></span> </div>
<div> </div><br>
<div dir="ltr" lang="en-us" class="OutlookMessageHeader" align="left">
<hr tabindex="-1">
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <b>On Behalf Of </b>Dave 
Palumbo<br><b>Sent:</b> Monday, October 11, 2010 9:15 PM<br><b>To:</b> 
'RE-wrenches'<br><b>Subject:</b> Re: [RE-wrenches] Supply side connection to a 
dedicated panel<br></font><br></div>
<div></div>
<div class="WordSection1">
<p class="MsoNormal">We are installing a 8kW grid tied PV system for a commercial 
client.  There is an auto start generator on the premises, therefore we 
will be utilizing a supply side AC point of connection. Inverter is an SMA 
SB8000. System owner plans on adding to system in the next few years. We are 
designing for a total of 24kW  of PV.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">We will install a 200A fused disconnect off the grid feed 
(line side of the generator transfer switch). My plan is install a dedicated 
breaker panel for the inverter 240VAC output(s). The SB8000 is rated at 29 Amps, 
so a 40A DP breaker will do for the point of connection. This panel will 
eventually have a total of (3) 40A DP breakers each with 8kW of inverter output. 
<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">My question has to do with the interpretation of the 120 
percent rule of the rating of the busbar in the panel. Do I need to use a 225 
Amp rated panel with a downsized 150A main breaker? 225A busbar x 1.2 = 270 Amps 
-150A MB = 120A total of inverter output allowed. Or, since this panel will only 
be used for inverter AC point of connection, and not for loads, is it allowable 
to label this panel as a “Dedicated Panel – connect no loads”. If that is the 
case we could use a 200A panel, or even a 150Amp panel. A local electrician 
proposed this “dedicated panel” to avoid the larger load center panel. I cannot 
find any mention of “dedicated panel” in the NEC. <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I think what I am proposing follows 690.64. Any opinions, or 
advice would be appreciated.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Dave Palumbo<o:p></o:p></p>
<p class="MsoNormal">Independent Power LLC <o:p></o:p></p>
<p class="MsoNormal"><i><a href="http://www.independentpowerllc.com">www.independentpowerllc.com</a> <o:p></o:p></i></p>
<p class="MsoNormal">NABCEP Certified PV Installer<o:p></o:p></p>
<p class="MsoNormal">Vermont Solar Partner<o:p></o:p></p>
<p class="MsoNormal">802.888.7194 <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p></div>
</div></blockquote><blockquote type="cite"><div><br></div></blockquote></body></html>