<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv=Content-Type content="text/html; charset=us-ascii">
<meta name=Generator content="Microsoft Word 12 (filtered medium)">
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri","sans-serif";
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
-->
</style>
<!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang=EN-US link=blue vlink=purple>
<div class=WordSection1>
<p class=MsoNormal>We are installing a 8kW grid tied PV system for a commercial
client. There is an auto start generator on the premises, therefore we
will be utilizing a supply side AC point of connection. Inverter is an SMA
SB8000. System owner plans on adding to system in the next few years. We are
designing for a total of 24kW of PV.<o:p></o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal>We will install a 200A fused disconnect off the grid feed (line
side of the generator transfer switch). My plan is install a dedicated breaker
panel for the inverter 240VAC output(s). The SB8000 is rated at 29 Amps, so a
40A DP breaker will do for the point of connection. This panel will eventually
have a total of (3) 40A DP breakers each with 8kW of inverter output. <o:p></o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal>My question has to do with the interpretation of the 120
percent rule of the rating of the busbar in the panel. Do I need to use a 225
Amp rated panel with a downsized 150A main breaker? 225A busbar x 1.2 = 270
Amps -150A MB = 120A total of inverter output allowed. Or, since this panel
will only be used for inverter AC point of connection, and not for loads, is it
allowable to label this panel as a “Dedicated Panel – connect no
loads”. If that is the case we could use a 200A panel, or even a 150Amp
panel. A local electrician proposed this “dedicated panel” to avoid
the larger load center panel. I cannot find any mention of “dedicated
panel” in the NEC. <o:p></o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal>I think what I am proposing follows 690.64. Any opinions, or
advice would be appreciated.<o:p></o:p></p>
<p class=MsoNormal><o:p> </o:p></p>
<p class=MsoNormal>Dave Palumbo<o:p></o:p></p>
<p class=MsoNormal>Independent Power LLC <o:p></o:p></p>
<p class=MsoNormal><i>www.independentpowerllc.com <o:p></o:p></i></p>
<p class=MsoNormal>NABCEP Certified PV Installer<o:p></o:p></p>
<p class=MsoNormal>Vermont Solar Partner<o:p></o:p></p>