<font face="arial" size="4">"<span class="187435412-04102010"><font>The battery choice was the 
decision of the system owner."<br><br>Since when does the customer make these decisions?<br><br>Todd<br></font></span><br>On Monday, October 4, 2010 6:36am, "North Texas Renewable Energy Inc" <ntrei@1scom.net> said:<br><br>

<meta http-equiv="Content-Type" content="text/html; charset=utf-8">
<meta content="MSHTML 6.00.2900.6003" name="GENERATOR">
<div><span class="187435412-04102010"><font face="Arial"></font></span> </div>
<div><span class="187435412-04102010"><font face="Arial">Todd</font></span></div>
<div><span class="187435412-04102010"><font face="Arial">I've heard the same 
arguement, as well as its inverse. The battery choice was the 
decision of the system owner. I know they are more sensitive to 
charge/discharge abuse but I see the full charge rate last week at 
52.xx V, just like day 1and I trust the Trimetric and the Sunny 
Islands. </font></span><span class="187435412-04102010"><font face="Arial">We're 
taking down the entire system to upgrade & install a 400A transfer switch so 
the batteries will have time to stabilize for the VOC check & cleaning. 
</font></span></div>
<div><span class="187435412-04102010"><font face="Arial">I guess a more accurate 
question would be is it good enough to properly check cell VOC and not 
bother with the discharge capacity check? A compromise could be cap 
check 12V blocks of cells instead of all 24 separately. Or is the 
capacity checker a waste of money.</font></span></div>
<div><span class="187435412-04102010"><font face="Arial">Jim</font></span></div>
<div><span class="187435412-04102010"></span><font face="Tahoma" size="2"><span class="187435412-04102010"><font face="Arial" size="3"> </font></span></font></div>
<div><font face="Tahoma" size="2"><span class="187435412-04102010"></span></font> </div>
<div><font face="Tahoma" size="2"><span class="187435412-04102010"></span></font> </div>
<div><font face="Tahoma" size="2"><span class="187435412-04102010"> </span>----Original Message-----<br><b>From:</b> 
re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org]<b>On Behalf Of 
</b>toddcory@finestplanet.com<br><b>Sent:</b> Monday, October 04, 2010 2:23 
AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] Battery 
capacity testers<br><br></font></div><font face="Tahoma" size="2"></font>
<blockquote><font face="arial" size="4">I know many on this list disagree, but 
  this sounds SO typical for sealed batteries. It is why I never use em... 
  never! If they are 5 years old, you are probably at the limit of their life. 
  Replace em with flooded lead calciums and your customers (and you) will be 
  happy for 20+ years.<br><br>my .o2<br><br>Todd<br><br><br><br>On Sunday, 
  October 3, 2010 9:28pm, "North Texas Renewable Energy Inc" 
  <ntrei@1scom.net> said:<br><br>
  <meta content="MSHTML 6.00.2900.6003" name="GENERATOR">
  <div><font face="Arial"><span class="937293103-04102010">I have a customer with a 
  set of 24 Concord PVX-6480s that have twice failed during grid outages during 
  the night. No large loads are on the critical load panel and, since it's at 
  night when they drop to 50% dod, I'm not sure what's up with them. 
  </span><span class="937293103-04102010">I plan on cleaning and retightning all 
  the cable connections first to eliminate that possibility then checking 
  VOC of each cell.</span> </font></div>
  <div><font face="Arial"><span class="937293103-04102010">Eventually we'll install 
  a 25 kW genset but my first task is to find out the state of the batterys. The 
  system turns five next spring so I don't think they are near an early 
  death. </span><span class="937293103-04102010">The BOS is 2 Sunny Island 4248s 
  with upgraded chipsets and the charger is set to spec though that may need to 
  be bumped up. The only culprit I suspect is the high summer temperatures 
  in this unconditioned equipment room. </span></font></div>
  <div><font face="Arial"><span class="937293103-04102010">Finally it may be time to 
  invest in a capacity tester. What brand is popular among those 
  Wrenches with lots of experience in diagnosing a batterys health? The 
  Concord DC5000 only comes in 12 & 24 V models and these are 2V cells. 
  </span></font></div>
  <div><font face="Arial"><span class="937293103-04102010">Thanks as 
  always</span></font></div>
  <div><font face="Arial"><span class="937293103-04102010"></span></font> </div>
  <div>
  <div>Jim Duncan</div>
  <div>North Texas Renewable Energy</div>
  <div>486 W.N. Woody Road</div>
  <div>Azle Texas 76020</div>
  <div>
  <div>
  <div>NABCEP Certified Solar PV</div>
  <div>Installer No.31310-57</div>
  <div>TECL 27398</div></div></div>
  <div><a href="mailto:ntrei@1scom.net">ntrei@1scom.net</a> </div>
  <div>817.917.0527</div>
  <div><a href="http://www.ntrei.com/">www.ntrei.com</a></div>
  <div><font face="Arial"></font> </div><font face="Times New Roman"></font></div></font><br><br><br>Sent from Finest Planet 
  WebMail.<br></blockquote></font><br><br><br>Sent from Finest Planet WebMail.<br>