    Just musing here, Mark,<br>
    What if the coil of the contactor was energized by the grid. The
    benefit is that grid goes down and so does theinverter; grid goes up
    and the inverter waits 5 min, long enough for the ATS to transfer
    back to grid. I can see two downsides: 1) the continuous tiny load
    of the contactor coil, and 2) you would have to run signal cable
    from the grid point on the ATS (or ahead of it) to the contactor at
    the inverter.'s point of connection to AC.<br>
    <br>
    <div class="moz-signature">
      <style>p.MsoNormal, li.MsoNormal, div.MsoNormal { margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: "Times New Roman"; color: black; }a:link, span.MsoHyperlink { color: blue; }a:visited, span.MsoHyperlinkFollowed { color: blue; }span.il {  }div.Section1 { page: Section1; }</style>
      <div class="Section1">
        <p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
            style=""> Sindelar</b><span style="font-size: 10pt;"><br>
            <a href="mailto:Allan@positiveenergysolar.com"
              target="_blank"><span class="il">Allan</span>@positiveenergysolar.com</a><br>
            NABCEP Certified Photovoltaic Installer<br>
            EE98J Journeyman Electrician<br>
            <b style="">Positive Energy, Inc.</b><br>
            3201 Calle Marie<br>
            Santa Fe, New Mexico 87507<br>
            <b style="">505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank">www.positiveenergysolar.com</a></span></p>
      </div>
    </div>
    <br>
    On 9/26/2010 1:31 PM, Mark Frye wrote:
    <blockquote cite="mid:D633AB9D228F4318A20CBF22A2808198@marksdell"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="MS Exchange Server version
        6.5.7036.0">
      <title>Interconnection downstream of ATS</title>
      <!-- Converted from text/rtf format -->
      <p><font size="2" face="Arial">Folks,</font> </p>
      <p><font size="2" face="Arial">I am looking at doing a standard
          grid-dependent PV installation. The only catch is that the
          whole house is backed up by a generator with automatic tranfer
          switch.</font></p>
      <p><font size="2" face="Arial">Due to the layout of the various
          equipment, it would be a whole lot easier to interconnect the
          PV at a point downstream of the ATS. Because the ATS takes a
          minute or so to bring the generator up and transfer, the
          inverter would drop out when the line is lost. If I had a
          contactor on inverter output, with the coil held by line
          voltage and a reset switch, I could set it up so that the
          inverter output would be isolated from the generator upon line
          voltage loss, and manually reset once utility line voltage was
          restored.</font></p>
      <p><font size="2" face="Arial">I am wondering about the following
          4 considerations:</font> </p>
      <p><font size="2" face="Arial">1 - Code / AHJ acceptablity: Does
          the Code address the issue of load side connection downstream
          of an ATS?</font> <br>
        <font size="2" face="Arial">2 - Utility (PG&E)
          acceptability: I don't see how the utility would care.</font>
        <br>
        <font size="2" face="Arial">3 - Inverter manufacturer
          acceptability: The manufacturer might not warrant this
          application unless they were confortable that the inverter
          never sees generator voltage.</font></p>
      <p><font size="2" face="Arial">4 - Functional efficacy: Owner
          would have to reset inverters manually.</font> </p>
      <p><font size="2" face="Arial">Has anyone worked throught this
          scenario?</font> <br>
        <font face="Arial"> </font> <br>
        <font size="2" face="Arial">Mark Frye</font> <br>
        <font size="2" face="Arial">Berkeley Solar Electric Systems</font>
        <br>
        <font size="2" face="Arial">303 Redbud Way</font> <br>
        <font size="2" face="Arial">Nevada City,  CA 95959</font> <br>
        <font size="2" face="Arial">(530) 401-8024</font> <br>
        <a moz-do-not-send="true" href="http://www.berkeleysolar.com"><u><font
              size="2" color="#0000ff" face="Arial">www.berkeleysolar.com</font></u></a><font
          size="2" face="Arial"> </font> </p>
      <pre wrap=""><fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>