    Fellow Wrenches,<br>
    Three years ago a local homeowner installed a small off-grid system
    using modern hardware preassembled by a good local company. The
    array consists of four Solarworld SW165s on a pole-top rack, wired
    as two 48V strings feeding an MX60 controller and a 24V battery
    bank. The property was sold and the new owners are not able to live
    within the capacity of this small array. They have asked me to quote
    an array upgrade.<br>
    <br>
    As modules get larger, I find it gets harder to match old arrays to
    new. The SW165 is a 72-cell module with output at MPP of 4.68A at
    35.3 Vdc, or 70.6 Vmp for each string. I can get some SW175s, even
    though they are more-or-less discontinued by the manufacturer in
    favor of the 60-cell 235s. The SW175s are rated at 4.89A at 35.8
    Vdc, or one volt higher for each two-module string.<br>
    <br>
    The maximum power point difference between the existing and new
    modules is one volt (or maybe a bit more due to light-induced
    degradation and the three-year age difference). In this case, the
    difference is pretty small, but I'm using this situation to ask a
    bigger question, as I'm interested in what other Wrenches have
    learned. An MPPT charge controller (and even more so with the MPP
    tracking in a string inverter in a grid-tied system) will latch to
    the voltage at which the input current is greatest. In this case, if
    I add four 175s to the four existing 165s, both voltage and current
    will be defined by the new array. Module I/V curves drop off current
    output quickly when the MPP voltage is exceeded. Will the smaller
    array be forced to operate above its max power voltage (I think
    yes)? Will the output of the smaller array be reduced noticeably by
    being operated off the knee of the curve? <br>
    <br>
    OK, this isn't the best example, as the difference is one volt, or
    about 1 1/2%. But what if the original array had used SW155s (34.8
    Vmp, or two volts difference)? I'm often asked to add new modules to
    an older existing array, so this question comes up, and I could use
    others' experience as guidance about when to pay close attention to
    these differences and when to let them go.<br>
    <br>
    This was never an issue before MPPT charge controllers, and it never
    was an issue with new systems with matching modules. But as we
    regularly upgrade existing systems, and as modules quickly come and
    go and specs change, these mix-n-match issues could limit our module
    choices if we're seeking maximum performance. Thanks in advance for
    advice.<br>
    <div class="moz-signature">-- <br>
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="ProgId" content="Word.Document">
      <meta name="Generator" content="Microsoft Word 11">
      <meta name="Originator" content="Microsoft Word 11">
      <link rel="File-List" href="signature_files/filelist.xml">
      <!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>2</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2009-12-09T22:29:00Z</o:Created>
  <o:LastSaved>2009-12-09T22:30:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>52</o:Words>
  <o:Characters>298</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>2</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>349</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
      <style>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.il
        {mso-style-name:il;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
            style=""> Sindelar</b><span style="font-size: 10pt;"><br>
            <a href="mailto:Allan@positiveenergysolar.com"
              target="_blank"><span class="il">Allan</span>@positiveenergysolar.com</a><br>
            NABCEP Certified Photovoltaic Installer<br>
            EE98J Journeyman Electrician<br>
            <b style="">Positive Energy, Inc.</b><br>
            3201 Calle Marie<br>
            Santa Fe, New Mexico 87507<br>
            <b style="">505 424-1112</b><br>
            <a href="http://www.positiveenergysolar.com/"
              target="_blank">www.positiveenergysolar.com</a></span></p>
      </div>
    </div>
  </body>
</html>