<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>CE is a self-certification that requires no 3rd party testing. In other words, if you think your product meets a standard and take the time to write a letter stating such, then you are CE certified. There are companies who you can pay to give you the letter, but it is easy to go on-line, learn the CE mark requirements and DIY.<BR></DIV>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Mick Abraham <mick@abrahamsolar.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> RE-wrenches <re-wrenches@lists.re-wrenches.org><BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Tue, September 14, 2010 12:17:34 PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [RE-wrenches] Delta LAs<BR></FONT><BR>Citel products do have a listing mark but this is European style CE, not American style UL/ETL. Citel is reputedly working on American certification but one would be advised to not hold one's breath.  
<DIV><BR></DIV>
<DIV>The Citel products which mount to a DIN rail have an LED indicator which goes dark once the surge elements have been sacrificed. Also some of their units have an auxiliary switch which can remotely indicate a blown condition. This is in the form of dry contacts..a normally open and a normally closed one, so various indicator circuits can be designed around that. The contacts have a low amp AC rating and also a (lower amp) DC rating but I do not remember the numbers at present. </DIV>
<DIV><BR></DIV>
<DIV>Jolliness,</DIV>
<DIV><BR clear=all>Mick Abraham, Proprietor<BR><A href="http://www.abrahamsolar.com/" rel=nofollow target=_blank>www.abrahamsolar.com</A><BR><BR>Voice: 970-731-4675<BR><BR><BR>
<DIV class=gmail_quote>On Tue, Sep 14, 2010 at 12:43 PM, R Ray Walters <SPAN dir=ltr><<A href="mailto:ray@solarray.com" rel=nofollow target=_blank ymailto="mailto:ray@solarray.com">ray@solarray.com</A>></SPAN> wrote:<BR>
<BLOCKQUOTE style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class=gmail_quote>
<DIV style="WORD-WRAP: break-word">You could buy several ground rods for the cost of one Delta. 
<DIV>Ground Impedance is the real issue. Both the Delta and the Polyphasor need a good ground to work. 
<DIV>While I haven't seen much of a correlation between Deltas and reduced lightning damage, (lots of system damage with and without)</DIV>
<DIV>I have found that well grounded systems (tied to a steel cased well) have never had a problem, even with direct strikes to a wind turbine (did lose the $40 turbine rectifier, but nothing else)</DIV>
<DIV><BR></DIV>
<DIV>I now own a clamp-on ground impedance tester, and the results were miserable. Some electrodes were over 800 ohms to ground! (code requires under 25 ohms)</DIV>
<DIV>I'd spend more time and money reducing ground impedance, and then if it makes you feel good inside, throw the little "lightning faeries" in, if the AHJ isn't looking.......</DIV>
<DIV><BR></DIV>
<DIV>If its really lightning country, and a really expensive off grid system, I use Polyphasor, but they have their own issues. (very expensive, no UL listing, loose internal connections, nuisance tripping, need a large J-box to mount them inside, etc.)</DIV>
<DIV>I haven't tried the Citel stuff, but it looks to be listed, and mounts on a DIN rail. After installing a couple hundred Deltas, I'd try something else at this point.</DIV>
<DIV><BR></DIV>
<DIV><BR>
<DIV><SPAN style="TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-SPACING: 0px 0px; BORDER-COLLAPSE: separate; FONT: 12px Helvetica; WHITE-SPACE: normal; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px">
<DIV>R. Walters</DIV>
<DIV><A href="mailto:ray@solarray.com" rel=nofollow target=_blank ymailto="mailto:ray@solarray.com">ray@solarray.com</A></DIV>
<DIV>Solar Engineer</DIV>
<DIV><BR></DIV>
<DIV><BR></DIV><BR></SPAN></DIV>
<DIV>
<DIV></DIV>
<DIV class=h5><BR>
<DIV>
<DIV>On Sep 14, 2010, at 10:22 AM, Kristopher Schmid wrote:</DIV><BR>
<BLOCKQUOTE type="cite">
<DIV>
<DIV><SPAN><FONT color=#0000ff size=2 face=Arial>My thought here is that nothing will protect the equipment from a direct strike, but a near strike that may induce a significant surge may be absorbed by the LA and protect the equipment.  I like the feedback so far.  It would not break my heart to stop using them altogether.:-}</FONT></SPAN></DIV>
<DIV><SPAN><FONT color=#0000ff size=2 face=Arial></FONT></SPAN> </DIV>
<DIV><SPAN><FONT color=#0000ff size=2 face=Arial>Kris</FONT></SPAN></DIV>
<P><FONT size=2>Legacy Solar<BR>864 Clam Falls Trail<BR>Frederic, WI 54837<BR>715-653-4295<BR><A href="mailto:solman@legacysolar.com" rel=nofollow target=_blank ymailto="mailto:solman@legacysolar.com">solman@legacysolar.com</A><BR><A href="http://www.legacysolar.com/" rel=nofollow target=_blank>www.legacysolar.com</A> </FONT></P>
<BLOCKQUOTE style="MARGIN-RIGHT: 0px">
<DIV></DIV>
<DIV dir=ltr lang=en-us align=left><FONT size=2 face=Tahoma>-----Original Message-----<BR><B>From:</B> <A href="mailto:re-wrenches-bounces@lists.re-wrenches.org" rel=nofollow target=_blank ymailto="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A> [mailto:<A href="mailto:re-wrenches-bounces@lists.re-wrenches.org" rel=nofollow target=_blank ymailto="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A>] <B>On Behalf Of </B>August Goers<BR><B>Sent:</B> Tuesday, September 14, 2010 10:39 AM<BR><B>To:</B> RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Delta LAs<BR><BR></FONT></DIV>
<DIV>All -</DIV>
<DIV> </DIV>
<DIV>I guess my thought is a little off topic, but are lightning arrestors even worth using at all? My logic has always been that if lightning does indeed strike that it's likely going to blow the arrestor and and inverter. We don't have much of a lightning issue issue in the Bay Area so I don't have any direct experience.</DIV>
<DIV> </DIV>
<DIV>Best,</DIV>
<DIV> </DIV>
<DIV>August<BR><BR></DIV>
<DIV class=gmail_quote>On Tue, Sep 14, 2010 at 6:29 AM, Kristopher Schmid <SPAN dir=ltr><<A href="mailto:solman@legacysolar.com" rel=nofollow target=_blank ymailto="mailto:solman@legacysolar.com">solman@legacysolar.com</A>></SPAN> wrote:<BR>
<BLOCKQUOTE style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class=gmail_quote>It is quite ironic that just a week after I posted a question to the group<BR>on testing the integrity of lightning arrestors, I had one apparently faulty<BR>out of the box.  The manifest of this was interesting: when the AC LA<BR>(LA302R) was connected in parallel on the AC input to a SB3000 inverter,<BR>there was 125vac neutral to L1, 125vac neutral to L2, and 1Vac L1 to L2.<BR>SMA tech support suggested the LA as the issue and sure enough, it was.<BR>Attempting to test good and faulty arrestors with an ohmmeter gave the same<BR>result - off scale open.<BR><BR>Any thoughts or comments from the group?<BR><BR>Kris Schmid<BR><BR>Legacy Solar<BR>864 Clam Falls Trail<BR>Frederic, WI 54837<BR>715-653-4295<BR><A href="mailto:solman@legacysolar.com" rel=nofollow target=_blank
 ymailto="mailto:solman@legacysolar.com">solman@legacysolar.com</A><BR><A href="http://www.legacysolar.com/" rel=nofollow target=_blank>www.legacysolar.com</A><BR><BR>_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <A href="mailto:RE-wrenches@lists.re-wrenches.org" rel=nofollow target=_blank ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options & settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List rules & etiquette:<BR><A href="http://www.re-wrenches.org/etiquette.htm" rel=nofollow target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out participant bios:<BR><A href="http://www.members.re-wrenches.org/" rel=nofollow target=_blank>www.members.re-wrenches.org</A><BR><BR></BLOCKQUOTE></DIV><BR><BR
 clear=all><BR>-- <BR>August Goers<BR>VP, Engineering<BR><BR>Luminalt Energy Corporation<BR>1320 Potrero Avenue<BR>San Francisco, CA 94110<BR>O: 415.641.4000<BR>M: 415.559.1525<BR><A href="mailto:august@luminalt.com" rel=nofollow target=_blank ymailto="mailto:august@luminalt.com">august@luminalt.com</A><BR></BLOCKQUOTE></DIV>_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <A href="mailto:RE-wrenches@lists.re-wrenches.org" rel=nofollow target=_blank ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options & settings:<BR><A href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel=nofollow target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: <A href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel=nofollow
 target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List rules & etiquette:<BR><A href="http://www.re-wrenches.org/etiquette.htm" rel=nofollow target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out participant bios:<BR><A href="http://www.members.re-wrenches.org/" rel=nofollow target=_blank>www.members.re-wrenches.org</A><BR><BR></BLOCKQUOTE></DIV><BR></DIV></DIV></DIV></DIV></DIV><BR>_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <A href="mailto:RE-wrenches@lists.re-wrenches.org" rel=nofollow target=_blank ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options & settings:<BR><A href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel=nofollow target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: <A
 href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel=nofollow target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List rules & etiquette:<BR><A href="http://www.re-wrenches.org/etiquette.htm" rel=nofollow target=_blank>www.re-wrenches.org/etiquette.htm</A><BR><BR>Check out participant bios:<BR><A href="http://www.members.re-wrenches.org/" rel=nofollow target=_blank>www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR></DIV></DIV></DIV></div></body></html>