<div>I guess my thought is a little off topic, but are lightning arrestors even worth using at all? My logic has always been that if lightning does indeed strike that it's likely going to blow the arrestor and and inverter. We don't have much of a lightning issue issue in the Bay Area so I don't have any direct experience.</div>

<div> </div>
<div>Best,</div>
<div> </div>
<div>August<br><br></div>
<div class="gmail_quote">On Tue, Sep 14, 2010 at 6:29 AM, Kristopher Schmid <span dir="ltr"><<a href="mailto:solman@legacysolar.com">solman@legacysolar.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">It is quite ironic that just a week after I posted a question to the group<br>on testing the integrity of lightning arrestors, I had one apparently faulty<br>
out of the box.  The manifest of this was interesting: when the AC LA<br>(LA302R) was connected in parallel on the AC input to a SB3000 inverter,<br>there was 125vac neutral to L1, 125vac neutral to L2, and 1Vac L1 to L2.<br>
SMA tech support suggested the LA as the issue and sure enough, it was.<br>Attempting to test good and faulty arrestors with an ohmmeter gave the same<br>result - off scale open.<br><br>Any thoughts or comments from the group?<br>
<br>Kris Schmid<br><br>Legacy Solar<br>864 Clam Falls Trail<br>Frederic, WI 54837<br>715-653-4295<br><a href="mailto:solman@legacysolar.com">solman@legacysolar.com</a><br><a href="http://www.legacysolar.com/" target="_blank">www.legacysolar.com</a><br>
<br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>List rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>August Goers<br>VP, Engineering<br><br>Luminalt Energy Corporation<br>1320 Potrero Avenue<br>San Francisco, CA 94110<br>O: 415.641.4000<br>M: 415.559.1525<br><a href="mailto:august@luminalt.com">august@luminalt.com</a><br>