<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html;charset=ISO-8859-1" http-equiv="Content-Type">
  <title></title>
</head>
<body bgcolor="#ffffff" text="#000000">
Matt,<br>
<br>
There is a word on the KLKD time delay chart you referenced that is
hiding a very important fact.  Those are "average" curves.  To
illustrate what that means take a look at the time delay curve for the <a
 href="http://www.cbi-electric.com/show_pictures.php?title=Product%20Curves&path=/curves_products/6">CBI
breaker</a> commonly used for battery charging systems.  There is a
gray area that extends from 105% to 130% of rating.  Over that range,
the breaker may or may not trip.  While not shown on the KLKD fuse time
delay chart that you referenced, a very similar gray zone exists. 
These fuses and breakers are simply not precise enough devices to
distinguish between Imp and Isc at STC in the best of conditions.   <br>
<br>
if you did manage to select a fuse that would blow at Isc but not at
Imp, it still wouldn't blow during a short if the irradiance was 800
W/sq m.  An arcing fault at 800 W/sq m can still burn a big hole.  It
simply isn't possible to provide good fault protection for PV systems
with fuses.  What's needed is a ground fault protector/arc fault
protector that is located in the combiner box.  Until that exists, the
feeder between the combiner and inverter needs to be considered an
unfused conductor.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>
<br>
<br>
<br>
Matt Lafferty wrote:
<blockquote cite="mid:9367CF41CBD2444BB18821D1189E9CEE@GILLIGONE"
 type="cite">
  <meta content="text/html; charset=us-ascii" http-equiv="Content-Type">
  <meta name="GENERATOR" content="MSHTML 8.00.6001.18939">
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Hi Kent,</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Thanks for the 98% vote. Now I'm
gonna try to get the other 2% out of you.... You're a smart guy, so it
shouldn't be too difficult ;)</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">These aren't the days where we
were lucky to have a customer with barely enough money to afford a 300W
system. We are commonly dealing with >2500W strings of 200+ watt
modules. It's a new paradigm and the risks associated with faults
continue to grow. You are 100% right... OCP in a current-limited DC
application ain't simple.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">To be clear, I am completely in
favor of 1.56 ISC as a minimum for conductors. I want that inherent
protection and any case I describe hereafter assumes this condition.
Also to be clear, I am not proposing that our current-limited power
sources should be able to trip the OCP from the source based on
amperage alone.</font></span></font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2"><span class="093142120-07092010"></span></font></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2"><span class="093142120-07092010">To
your contention that "1.56 ISC isn't in any way responsible for the
danger"....</span></font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2"><span class="093142120-07092010"></span></font></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Compared to a lower fuse
rating.... Something like ISC for instance.... 1.56 ISC as a MINIMUM
OCP rating does indeed increase the hazards. To both persons and
property. By at least 40% in terms of raw amperage. By more than that
in terms of kCal/cm2. The biggest difference comes in terms of time to
blow and the amount of damage or injury caused during that period. They
call it Incident Energy.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">For those who have not studied
Time:Current curves of commonly used fuses, you should. </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">KLKD
is a typical fuse I hope we are all familiar with. <a
 moz-do-not-send="true"
 href="http://www.littelfuse.com/data/en/Data_Sheets/KLKD.pdf">http://www.littelfuse.com/data/en/Data_Sheets/KLKD.pdf</a> 
I'm using KLKD as an example because Littelfuse put a little table
right on the front of the datasheet to make it simple. Other commonly
used fuses have similar characteristics. </font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Note that this class of fuse
will take 135% of it's rating for up to 1 hour. 200% of its rating for
up to 2 minutes. Be sure to check out the fuse curves. These things
will take ~125% of their ratings for pretty much indefinitely. How much
damage is caused waiting for it to blow? What about when irradiance is
<800 W/M2? How long then? </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">Will
your conductor hold up during this time?</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">If you fault on the array side
of a combiner fuse in a 3-string system, you might NEVER BLOW that
fuse. (Example: 8.4A ISC module with 15A fuse). Especially if there is
an arcing DC fault. Temperatures of arcs are much higher than 90C. </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">Is
your conductor up to that? I have been called to troubleshoot a lot of
low-performing and broke-down systems. One resi rooftop had a spot
where an arcing fault burned through the side of a NEMA 3R steel
pull-can on the roof and never blew a CODE COMPLIANT combiner fuse.
This system had 3 strings and was down about 1/3 on power output after
the original installer replaced the GFP fuse following a
"ground-fault". He had checked the combiner fuses and they were good so
he called me to troubleshoot it. He was convinced that there must be a
bad module and wanted a third party to verify it for warranty claim.
Hated to show him what he missed and that it was his fault. (The fault
had burned clear so the GFP didn't blow again.)</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Another situation that I am
sadly familiar with  has been burning holes in a steel roof since 2007 <em>(I
told them not to do it over and over)</em>... At least one spot is
about the size of a softball. The others vary in size. Their common
characteristic is that you can see the sky thru them from inside the
building. </font></span><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">The first time it happened was
during an ice storm. This POS peel-n-stick system typically burns thru
the roof during low-irradiance periods. Most of the time it will
EVENTUALLY blow a combiner fuse, reducing the current feeding the
fault, and either weld to a short or burn clear (open). </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">This
is ~500kW on central inverters with marginal GFP protection. I hear the
Tefcel front sheet is a nice insulator.... You want to walk out on that
thing in the daylight? I don't. This case happens to be a classic
installer-was-either-drunk-or-on-drugs-because-nobody-can-be-that-stupid
situation. Rolling UniSolar right over loose screws on the pan? WTF!!!!</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">I
can list a lot of similar examples where damage has been caused and
fuses have either not blown or taken longer than they should have to
blow. </font></span><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">The key here is that the wiring
and OCP in ALL OF THESE CASES ARE CODE COMPLIANT!</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">I bring these cases up because,
if these things had fuses with smaller current ratings, the fuses would
blow before this much damage is done. It takes a lot of heat to burn
thru steel. You wouldn't think that a circuit with a 10 or 15A fuse
could do this much damage, but they do! Amperage = Heat. The more Amps,
the more Heat. When you use an Arc or Wire-feed welder, you adjust Amps
to get the heat you want. I want to minimize the amount of potential
Amps back-flowing into a fault to a lower level. A level that allows
safe and reliable NORMAL OPERATION, yet limits the catastrophic effects
in an ABNORMAL CONDITION.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">My contention is that the NEC is
flat out wrong requiring 1.56 ISC as a MIMIMUM OCP rating. It creates
undue hazard. It is in direct conflict with the spirit, intent, and
other long-standing precedents in the Code.... With the exception of
Emergency Fire Pumps and other mission-critical equipment that is
specifically intended to stay alive until it completely burns to the
ground</font></span><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">, all other minimum OCP ratings
are based on 125% CONTINUOUS OPERATING CURRENT of the equipment. In our
case, that equates to 125% Ipmax, as opposed to ISC. An example of an
AC equivalent to this asinine "minimum 1.56 ISC" OCP requirement would
be requiring motor circuits to be OCP at 156% of the </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">Locked
Rotor Amps. I'm sure you can imagine what this would do to the size and
cost of starters, etc. </font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Since the last time my favorite
6kW system put out 7.5kW was... NEVER.... I'm gonna have to guess that
a 1.25 Ipmax fuse would hold just fine. This would be 100% consistent
with the rest of the Code. It's also not gonna blow with cloud-edge
effect or other irradiance enhancing events. Especially when you
consider that it's gonna automatically withstand an extra 20-25%% for
an indefinite, possibly forever, period due to the Time:Current curve
relationship.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">My
NON-CODE-COMPLIANT-SELF prefers to size OCP at <em>"ISC or next larger
standard fuse rating not larger than the LISTED Series Fuse Rating of
the module"</em>. You've got a 6-7% headstart between Ipmax and ISC
plus the ~25% indefinite Time:Current characteristic. Ain't no way in
hell that a NORMALLY OPERATING SYSTEM will blow fuses rated this way.
And it's ~2/3 the amp rating (or less) that is now required as a
minimum. </font></span><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Which is exactly what we want.
Reliability during normal operation and safety.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">The only time we want an OCP
device to trip is during abnormal conditions such as a short circuit.
When we have this type of fault, we want that circuit to open up as
quickly as possible in order to minimize damage. At least I do. In the
case of 1.56 ISC, the NEC is GUARANTEEING GREATER DAMAGE AND INCREASED
HAZARDS compared to a lower-amp fuse. I have gone thru this logic with
numerous building inspectors over the years. Every single one agrees
with it. Some, but not all, have agreed to allow lower-amperage fuses.
The only, and I mean ONLY reason given by inspectors that have not
allowed lower-amperage fuses is because... <em>"The Code requires 1.56
ISC so I have to require it."</em> </font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2"><em></em></font></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">String inverters only bother me
so much in this regard. Central inverter systems are where the real bad
ju-ju starts to happen. <span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">For the sake of definitions, I
consider a string inverter to be one that has one or less combiners and
the modules are configured in series strings. A central inverter is one
that has string-level combiners and one or more re-combiners. </font></span></font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span><span
 class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">I am seeing more and more faults
in the DC feeders between string combiners and re-combiners in these
central systems. The power levels you are dealing with here are pretty
significant. 100% of the recent faults I've been seeing are due to
shi##y workmanship, particularly in conduit installation and
wire-pulling. Some of these faults would certainly have been avoided if
they had selected a tougher insulation such as XHHW-2, instead of
Quik-Nick THWN-2/THHN. (THWN stands for "This Heiffer Will Nick".
THWN-2 stands for "This Heiffer Will Nick 2wice")</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">I have zero tolerance for crappy
workmanship and even less sympathy for the people who do it. </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">Just
got off ANOTHER call this morning where the installer has re-pulled one
DC feeder four times and still can't pass megger testing. They have
re-pulled every feeder at least once. The spec only calls for 250 Mohms
even though wire and cable engineering formulas say the minimum should
be 688 Mohms for that size, length, and insulation type of wire. And
they can't even get it to 250. </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">Every
set of wires that has been pulled out has obvious physical damage. </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">The
sub is crying, wanting more money and to have the work accepted (NOT!).
Come to find out, one of the field guys working for the developer has
witnessed these guys beating on the 1/0 AWG with a mallet to get it
into the LB. </font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Says right here in my NECA
1-2006 Standard for Good Workmanship in Electrical Construction...
Section 9 Wire and Cable.... "c) Wires and cables shall be installed so
as not to damage the insulation or cable sheath." Sounds like this
electrician sub wannabe is in violation of his contract.... You know
that clause... "Workmanlike manner". <em>(Sub, if you are reading
this... I am NOT your friend in this case. You WILL re-pull these
feeders correctly, at your own expense. I will repeat the advice
already provided: Use pulling condulets. I will add some advice: Fire
your electricians.)</em></font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">The scary thing is, this
practice goes on every day. A LOT! </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">The
sad fact is that many (most?) of these systems are not having thorough,
comprehensive Insulation Resistance Testing performed. And IRT will
only catch SOME of the future faults! I have been involved with
post-mortem in two cases where 500kW AC feeders have been properly
IRT'd and blew up later. Not good! (Side Note: Each of these cases
involved big feeders in standard LB's. Make a note of it.)</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">It's
only a matter of time before these things go Pop Sizzle Smoke! These
failures WILL occur. A lot of them already have and the number is
growing. I hope and trust that most of us on this list practice Good
Workmanship on every project. That being said, none of us are perfect.
What about cases where we miss something or even cases like a tree
falling across one of our conduits?</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">My contention is that we should
do whatever we RESPONSIBLY can to minimize the damage when this happens
and the hazards when it's being troubleshot and repaired. It's a simple
principle. </font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">One RESPONSIBLE way we can
minimize the damage is to reduce the fuse size by ~40%. <em>(i.e. ISC
or next higher standard fuse rating)</em> This method will provide
adequate operational reliability. It will also </font></span><span
 class="093142120-07092010"><font color="#0000ff" face="Arial" size="2">ensure
that there is a better chance of the fuse blowing sooner when there is
a fault, thereby minimizing the damage caused. It will minimize the
hazard to personnel performing troubleshooting and repair because the
incident energy at the fault will be reduced in all cases. By ~40%.
Whether or not the fuse blew.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Happy to discuss this issue with
all who care and are not on NFPA 70 CMP. (Just kidding. You CMP guys
are welcome to discuss it, too... Just be ready to issue a
memorandum/addendum to the 2011 NEC allowing OCP with lower than 1.56
ISC...)</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Extra Credit for BOS Mfrs: Make
a Combination Device that has DC Arc-Fault Interruption and OCP that
fits in a standard fuse configuration. Start with midget-class so we
can simply drop it into our string combiner fuseholders.</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><span class="093142120-07092010"><font
 color="#0000ff" face="Arial" size="2">Pray for Sun!</font></span></div>
  <div dir="ltr" align="left"><span class="093142120-07092010"></span> </div>
  <div dir="ltr" align="left"><strong><i><span
 style="font-family: 'Monotype Corsiva';">Ma<span
 class="093142120-07092010">t</span>t Lafferty</span></i></strong></div>
  <div class="Section1">
  <p class="MsoNormal"><span
 style="font-family: Arial; font-size: 10pt;"><a moz-do-not-send="true"
 href="mailto:gilligan06@gmail.com">gilligan06@gmail.com</a></span><br>
  </p>
  </div>
  <div dir="ltr" class="OutlookMessageHeader" align="left" lang="en-us">
  <hr tabindex="-1"><font face="Tahoma" size="2"><b>From:</b>
<a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
[<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Kent
Osterberg<br>
  <b>Sent:</b> Tuesday, September 07, 2010 10:59 AM<br>
  <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
  <b>Subject:</b> [RE-wrenches] ground fault troubleshooting<br>
  </font><br>
  </div>
Matt,<br>
  <br>
I agree with you on about 98% of this.  You are 200% correct that a
faulted high-voltage or high-current PV array is a serious and
dangerous situation and that the person looking for the trouble in a
faulted PV array needs the proper tools and knowledge of how all the
components work.  But the 156% rule for fuse sizing per NEC 690 is not
in any way responsible for the danger.  The danger is a result of the
nature of the PV module: a power source with the current nearly
proportional to the illumination and a short circuit current that is
only 10% greater than the normal operating current.  If one were to
select a fuse that could blow when the array was shorted, occasional
edge of cloud irradiance enhancement would cause nuisance trips and it
still wouldn't clear a fault when the irradiance is 900 watts per
square meter.  There will never be a simple fuse that can provide the
protection that is needed.  The existing ground fault protection in the
inverters is inadequate and current plans for arc fault protection may
not be a satisfactory either. These have been slow incremental
improvements; much more is needed.<br>
  <br>
  <div class="moz-signature">-- <br>
Kent Osterberg<br>
Blue Mountain Solar<br>
541-568-4882<br>
  <a moz-do-not-send="true" href="http://www.bluemountainsolar.com/">www.bluemountainsolar.com</a><br>
  <br>
  <br>
  <pre>Wrenches all,
 
I 100% second Bill B's comment Correct that... I 200% second it. It should
be the law.... "Don't begin to troubleshoot a faulted PV circuit without a
reliable DC clamp meter."
 
The MOST DANGEROUS PV system is a wounded PV system. This includes danger to
persons and property. Safely and efficiently troubleshooting a faulted PV
circuit requires a voltmeter AND an ammeter. And PPE. And adequate knowledge
and understanding of operational and non-operational characteristics of PV
systems.
 
The simple reason for this is that, when one or more circuit conductors are
faulted to a short condition, the voltage between the faulted elements is
zero. Relying on just a voltage reading to determine whether or not to open
a circuit under this condition will result in an arc. The amount of energy
in that arc will depend on the amount of available sunlight and the amount
of PV that is feeding into it. The amount of potential hazard will
correspond to these factors as well.
 
Using a clamp style ammeter will allow you to understand where and how much
current is flowing in a circuit before you decide to open it. It is one
thing to know you have a 45 amp load in a circuit with a potential of ~450V
because you clamp it before you break it. With this knowledge you can assess
the situation. You can do something to mitigate or remove the potential
hazards... Cover the array, open a disconnect somewhere, put your PPE on and
go for it, select a different location to open the circuit, use insulated
cable cutters, wait 'til dark.... You have choices.
 
It is quite another to be surprised by the resulting arc in tight quarters
because you measured the voltage and figured it was a dead circuit! When you
react to the startlement (word?) by dropping your screwdriver and yanking
your hand back... Assuming you don't receive a shock, flash injury, or fall
off the roof in the process, of course.... The result just may be that the
now-dislodged conductor is arcing and zapping and spitting. Now you're gonna
have to stick something back into that box to deal with it. In the meantime,
a number of possible things can happen, most of which are not favorable....
Melting insulation and conductor material are the most common. The degree
(not just a pun) of damage and remaining hazard will be determined by the
amount of sunshine and amount of PV feeding into the arc.
 
The MOST DANGEROUS single point on the DC side of a PV system is ANYPLACE on
the Inverter side of a fuse(s). This is a simple function of the assinine
"1.56 ISC minimum fuse" rule in the NEC. The source cannot create enough
current to blow the fuse(s). If you have a fault between a combiner and the
inverter, you WILL have current flowing into the fault as long as the sun is
up! If you are relying on just a voltmeter in a central-inverter plant, you
could very well be in for a 15-20kW surprise, or greater!
 
The combination of shi##y wire, sloppy conduit installation, and crappy
wire-pulling methods have resulted in too many DC feeder faults to count. It
boggles my mind every time I hear of yet another guy nearly joining the dead
because he touched or opened up a connection somewhere in a faulted circuit
without de-energizing it. Time and time again I hear that they tested it for
voltage and it was "dead". Sometimes they even opened up the service
disconnect at the string combiner, "just to make sure". Time and again it's
a "journeyman electrician". I like it best when it's the same card-carrying
jackass who "built" the thing.
 
I consider THWN-2 to be on the list of shi##y wire types for DC, by the way.
I'm an XHHW-2 guy, personally. Why would anybody select an insulation that
is easy to nick/slice/tear when you can have a super-tough insulation for a
couple pennies more? Why would anybody select an insulation that only has
about 5% of the dielectric resistance of one that is a couple pennies more?
Why? Oh, I know... It's that race to the bottom on BOS costs... 
 
Which leads to the next step in stupidity... Designing and building LARGE PV
plants without sufficient DC SERVICE disconnects... This is what's going on
out there.... PV plants with 500kW Central-inverters being installed without
string-combiner disconnects. Without any DC service disconnects. 
 
The NEC considers the fuseholder in the combiner &/or the connector on the
module to be a "disconnect" and does not require a "service disconnect" in
the circuit. So these smart-ass engineers and project developers are out
there building this shi#. Some of these projects are being built by PV
module manufacturers masquerading as developers. "Vertically integrated..."
Others are being designed & built by formerly respected integrators who have
either sold out or lost their conscience altogether. The trend is to build
them to sell to PPA companies who ostensibly own and "operate" them. These
solar timebombs are being built on both sides of the fence. Frosty ain't the
only one with a solar flamethrower!
 
All in the race to the bottom of the $/Watt pile that they are now calling
LCOE. Har Dee Har Har! 
 
I hate to say this, but I hope somebody gets really hurt out there, and
soon. I hope it's the same smart-ass engineer (or his boss) who thought it
was alright to design this way after some field technician walks away from
it because it's dangerous. And then I hope his family sues the crap out of
the company and companies involved with designing, supplying, building, and
owning it so they STOP DOING THIS SHI#! And then I hope he takes his cooked
carcass on the road doing safety awareness training so others don't repeat
these stupid, avoidable catastrophes! And then I hope these cheap-ass
developers go out to every site that doesn't have sufficient disconnects and
re-fits the systems with them to avoid further injuries and $$$$
settlements. What is the levelized cost of energy for that system now, Mr.
CFO?
 
Unfortunately it isn't likely to be that smart-ass engineer. Or his boss. It
is far more likely to be a Wrench. A Wrench without a DC clamp and the
knowledge that he needs one. A Wrench without the proper PPE because he
"tested it and it was dead" so, even if he had his gear on to "test it", he
took his gloves and face-shield off to work on it. A Wrench who doesn't
fully understand the operation of GFP circuits. A Wrench who doesn't
understand that not all faults are ground faults and the characteristics of
a fault change in terms of potential and magnitude with varying
environmental conditions. A Wrench that doesn't fully understand that power
can be coming from both directions. A Wrench who figures he doesn't have the
time to completely isolate a section of a circuit because there AIN'T NO
REAL DISCONNECTS. I hope it's not your Wrench.
 
As the size of the inverter grows, so does the hazard. To a point. The
idiotic 1.56 ISC rule only increases the potential hazards. Central-inverter
plants should not be serviced by anybody who doesn't have an extremely
comprehensive understanding of these systems, and the tools and PPE to
safely work on it. For systems with inverter-integral re-combiners, the most
dangerous spot in these systems are the feeders between string combiners and
re-combiners. Anything between the output of a string combiner and the input
of a re-combiner. For systems with standalone re-combiners, a fault between
the re-combiner output and the line side of the next disconnect is the most
dangerous point, but certainly not the only dangerous point. If either of
these systems are built without load-break disconnects at the
string-combiner level, the cost to service goes thru the roof. It either
goes thru the roof to do it safely or it goes thru the roof in terms of risk
to do it not safely. Pick one.
 
There is an interesting dynamic between the potential hazard on a faulted DC
homerun feeder and the kW of the inverter. The less re-combiner inputs you
use, the greater the potential hazard on faulted input feeders. Again, this
is because of the UNSAFE AND STUPID 1.56 ISC rule. In systems with a
relatively low number of re-combiner inputs, there are large portions of
time when there isn't enough combined amperage in the non-faulted feeders to
blow the re-combiner fuse of the faulted feeder. If your system only has 4
or 5 re-combiner inputs and it's winter-time, it is quite likely that a
faulted feeder is being fed from both ends. (Commonly 100A fuses in the
re-combiner with ~60A ISC feeding a string-combiner) That feeder can be fed
from the re-combiner end, by anything up to about 105% of the fuse rating,
for pretty much ever without blowing the fuse. The more parrallel inputs
there are, the more likely there will be sufficient current generated by the
other feeders to blow the fuse. Since the vast majority of systems out there
don't have load-break disconnects at the re-combiner inputs, the technician
needs to be able to open disconnects at each string combiner in order to
isolate this feeder. But what about systems without DC service disconnects?
Repair at night?
 
My hope is that anybody on this list will refuse... Say it with me now...
R-E-F-U-S-E to install PV systems without adequate disconnect provisions to
isolate faulted feeders. And only allow technicians with proper knowledge
and equipment to work on a busted PV system. "Journeyman electrician" does
NOT automatically mean that person has the proper knowledge to do it safely.
Safely working on a faulted PV DC circuit requires ALWAYS clamping the thing
for starters. It might also mean "not working" on it until the sun goes
down. A technician with the proper knowledge and equipment should be able to
determine the proper course of repair.
 
In the case of the faulted lightning arrestor, it was "only" a small
circuit, but it got the guy's attention and apparently nobody got hurt. The
bigger these systems get, the bigger the potential hazard. 
 
To answer Tom's question about jumping around a fault: Maybe, maybe not,
depending on the nature of the fault (+/-, +/G, -/G) and the location of the
jumper relative the fault and the power source. Even if jumping to ground
eliminates the arcing when you are working with the terminal, you will still
have arcing when you land/un-land the jumper &/or remove the fault. If the
sun is shining and you have a DC fault, you will have arcing at some point
when you make/break the circuit. Hopefully it's safely contained and
localized to the contacts of a service disconnect!
 
Pray for Sun!
 
Matt Lafferty
  </pre>
  <br>
  </div>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
  <pre wrap="">
<hr size="4" width="90%">

No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a> 
Version: 9.0.851 / Virus Database: 271.1.1/3119 - Release Date: 09/06/10 23:34:00

  </pre>
</blockquote>
</body>
</html>