Hi, knuckle-busters~<div><br></div><div>That's interesting information in the other thread about the actual solar throughput to grid with the Xantrex XW architecture. </div><div><br></div><div>May I now poll the group to learn what percentage throughput is likely if the inverter stack is instead an AC coupled blend of SMA SunnyBoy/SunnyIsland hardware?</div>

<div><br></div><div>Survey says...</div><div><br clear="all">Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">On Tue, Aug 24, 2010 at 8:40 PM, Maverick Brown [Maverick Solar] <span dir="ltr"><<a href="mailto:maverick@mavericksolar.com">maverick@mavericksolar.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">







<div lang="EN-US" link="blue" vlink="purple">
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">There is a XW6048 double-stack that has 11,760W PV and 
gets 8200+ W Output (in our Texas heat) and creates about 60kwh per 
day.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">That 8/11-ish number is right at 70%. I am sure the early 
spring will be better.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">I also suggest that 400Ah is the minimum battery bank size 
required for a proper sell-re that keeps the battery full enough to prevent 
sulfation, but limits overvoltage issues in puffy cloud 
conditions.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Good luck!</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Maverick</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2">
<div align="left">
<div align="left"><font size="2"><font face="Arial"><font color="#000000">Maverick 
Brown<br><span><font size="1">BSEET, NABCEP Certified 
Solar PV Installer ®</font></span></font></font></font></div>
<div align="left"><span><font color="#000000" size="2" face="Arial">President & CEO</font></span></div>
<div><font color="#000000" size="2" face="Arial"><strong>Maverick Solar<span> Enterprises, Inc.</span><br></strong></font><font color="#000080" size="1" face="Arial">12010 West Highway 290, Suite 230, Austin, TX 
78737<br></font><font size="1"><font face="Arial"><font color="#000080"><span>Office:       
512-919-4493<br><span>Fax:         
  
512-607-6398<br></span></span>Cell:          
512-460-9825<br>Store:<span>    </span>  <span>  </span></font></font></font><a title="blocked::http://www.mavericksolar.com/"><font color="#000080" size="1" face="Arial">http://www.mavericksolar.com</font></a><br><font size="1"><font face="Arial"><font color="#000080">Help:   <span>      
</span></font></font></font><a href="http://www.mavericksolar.net/" target="_blank"><font color="#000080" size="1" face="Arial">http://www.mavericksolar.net</font></a><span><br><font color="#000080" size="1" face="Arial">Corporate: 
</font><a href="http://www.mavericksolarenterprises.com/" target="_blank"><font color="#000080" size="1" face="Arial">http://www.mavericksolarenterprises.com</font></a></span></div></div></font></span></div></span></div>

<br>
<div dir="ltr" lang="en-us" align="left">
<hr>
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Travis 
Creswell<br><b>Sent:</b> Tuesday, August 24, 2010 4:11 PM<br><b>To:</b> 
'RE-wrenches'<br><b>Subject:</b> [RE-wrenches] Net AC kW Derate Factor for 
Xantrex XW inverter andXW opinions<br></font><br></div><div><div></div><div class="h5">
<div></div>
<div>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">Greetings Esteemed 
Wrenches,</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">What would you recommend I use for a 
total de-rate factor for a grid tied Xantrex XW system with 4.14 kW of Yingli 
230 watt modules?  Yingli’s are rated +/- 3% which probably means at least 
-5% to be safe.  Would a total of .7 be about right?  Battery bank 
will likely be one string of L-16’s or similar.</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">I’m helping a customer calculate 
annual production for his rebate.  At this point it’s just an estimate as 
Arkansas 
wisely bases their rebate on actual production and requires a dedicated meter 
for the system.  I’m using the Wiley Asset tool to adjust for shading and 
azimuth.  The Asset software uses .77 as a default but that’s for a 
battery-less system.</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">Probably before I head too far down 
this road what does anyone have to say about using the XW6048 for a grid tied 
application?  I’ve used a few XW’s off grid and have been pleased but never 
grid tied one.</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">Best,</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">Travis 
Creswell</span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="font-family:Arial;font-size:10pt">Ozark Energy 
Services</span></font></p></div></div></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>