Hi All.....I can't find it in any of the manuals for grundfos.....does anyone know if the wiring to the float switch carries current or not.  The float switch has 3 #14AWG wires.......I need to add about 700 feet of wire from the CU 200 controller to the storage tank.....I want to use #18AWG......is this okay?  most float switches I have used do not carry current they are simply signal wires and can use very small gauge for long distance.....<br>
Anyone know off the top of their head?<br>Thanks....<br clear="all"><br>-- <br>Sunny Regards,<br>Kirpal Khalsa<br>NABCEP Certified Solar PV Installer<br>Renewable Energy Systems<br><a href="http://www.oregonsolarworks.com">www.oregonsolarworks.com</a><br>