<font size=3>Darryl:<br><br>
There is a scenario in which problems occur:  If your loads exceed
the generator capacity, the Outback system will fail.  The Xantrex
inverters are superior in this scenario in that they will transition to
invert mode to synchronize with the generator and support the generator
as long as the batteries will sustain the operation of the
inverter.<br><br>
William Miller<br><br>
<br>
At 12:21 PM 7/21/2010, you wrote:<br>
<blockquote type=cite class=cite cite>The propane and gasoline generators
both ar premixed combustion and have a low efficiency at part throttle/
part load.  The Diesel does the best job of maintaining efficency at
low load.   The outback can control its charging current to the
load limit of the generator.  If the AC loads need more power the
Outback can reduce the charging rate until the AC load diminishes. 
<br><br>
It takes a lot of words to describe and decide what is the correct
generator sizing.<br>
Darryl</font></blockquote></body>