<blockquote type=cite class=cite cite>Voltage is not the issue here, it
is current, and battery fault currents can be staggering - far more than
one would ever encounter in a typical AC system fed from a distribution
transformer.  I have seen a 200A Class T fail to act on an 48V
inverter fault which resulted in welding the metal tabs of the fuse
holder (which had been greased with copper-laden Penetrox E) to their
sockets.  That indicates a fault current well north of 200,000 amps,
quite possibly sseveral times that.   A fire ensued, which
triggered the gas protection system and fortunately resulted in almost no
peripheral damage.  It did cost about $10k to recharge and recertify
the Inergen system.  The inverter manufacturer was quite cagey on
warranty replacement until they saw the photos - at which point a
replacement miraculously arrived by overnight air.<br><br>