Before I present a suggestion, here's a question:<br><br>If by chance William is able to energize the transformer without tripping the breakers, what if there is a brief break in the power...such as a half-second?<br><br>

I don't suppose there's capacitance here...more like magnetic flux...but would there be a brief window before the transformer bleeds down and requires another equally strong inrush current?<br><br>Or...would a tiny blip in the input power result in another big surge requirement?<br>

<br>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">2010/5/13 Richard L Ratico <span dir="ltr"><<a href="mailto:Richard.L.Ratico@valley.net">Richard.L.Ratico@valley.net</a>></span><br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">

Sorry for the additional post here, but it includes a typo correction:<br>
<div class="im"><br>
Bill,<br>
<br>
Not a lot of personal experience with this issue. The one time I had to deal<br>
with it, we were able to leave the circuit on, once we got it energized.<br>
As you know, the crux of the problem is the nature of the voltage relative to<br>
it's cycle when connection is attempted.<br>
<br>
An internet search resulted in this explanation that was very helpful. See:<br>
<br>
<a href="http://www.opamp-electronics.com/tutorials/inrush_current_2_09_12.htm" target="_blank">http://www.opamp-electronics.com/tutorials/inrush_current_2_09_12.htm</a><br>
<br>
As I understand it now, counterintuitively, you don't want to switch at the zero<br>
crossing. SS relays aren't my strong suit either, but if they connect at that<br>
moment.......<br>
<br>
Is your step up transformer actually designed by the manufacturer to be a step<br>
</div>up unit, or are you using a step down unit in reverse?<br>
<div><div></div><div class="h5">Again, according to information found in my search, not personal experience, the<br>
latter can contribute to higher than expected inrush.<br>
<br>
Dick Ratico<br>
<br>
<br>
--- You wrote:<br>
Thanks for the reply.  To clarify, we have tried his with one transformer<br>
and with two transformers.  Our success rate is lower powering one<br>
transformer.  My hunch is that the capacitance of the feeder is buffering...<br>
<br>
I wonder if I use a large solid state relay with zero crossing switching I<br>
might have better luck.<br>
<br>
<br>
William Miller<br>
<br>
<br>
At 06:23 PM 5/12/2010, Richard L Ratico wrote:<br>
>Bill,<br>
>Your branch circuit breaker is pretty small.<br>
>Are you energizing both transformers simultaneously? If so, it might help to<br>
>energize them individually.<br>
><br>
>The branch breaker can be up to 250% of the step up transformer's primary<br>
>rating. 10kVA/240V=41A.<br>
>41A x 2.5=100A. (round numbers). To do this you would also need overcurrent<br>
>protection on the transformer secondary.<br>
><br>
>Of course, you've already got the 100A main tripping. That's why I asked if<br>
>you're<br>
>energizing them simultaneously.<br>
><br>
>Transformer inrush can be a real problem.<br>
><br>
>Hope this helps.<br>
><br>
>Dick Ratico<br>
>Solarwind Electric<br>
><br>
>--- You wrote:<br>
>Friends:<br>
><br>
>I have on off-grid client that is trying to eliminate winter generator run<br>
>time.  He has a rental on another corner of the property that has grid<br>
>power.  When it was installed, he put in an extra meter, hoping to use it<br>
>to run a utility back up feeder to charge batteries.<br>
><br>
>We are now installing this feeder.  We purchased two 10KVA 240/600 volt<br>
>transformers to bump the voltage to 600 and then back down to 120/240.<br>
><br>
>Here's the problem:  when we energize the circuit breaker that feeds the<br>
>transformer, the circuit breaker AND the main breaker trip.  The<br>
>transformer is 10KVA, the main is 100 amps and the branch breaker is<br>
>60A.  The breakers hold sometimes but trip other times.  This is obviously<br>
>an inrush problem.  How do I correct this problem?<br>
><br>
>Thanks in advance,<br>
--- end of quote ---<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br>