<font face="Arial">Esteemed Wrenches,<br>
<br>
I'm in the process of bidding a small government job.  They're
requiring the following tests.  I was wondering if any of you have
ever run across this before and if so how you went about it. <br>
<br>
<i>- Inspect   inverters   according   to   requirements   in   NETA
Acceptance   Testing <br>
Specifications. <br>
<br>
- Test  the  PV  system  under  prime  solar  design  conditions  to 
validate  system <br>
power  performance  rating.    Use  instruments  calibrated  within 
the  previous  six <br>
months according to NIST standards.   </i>(not easy since the site
they've chosen will shade some of the array all the time.  I should be
able to just explain this to them)<br>
<i><br>
- Simulate  malfunctions,  including  ground  faults,  to  verify 
protective  device <br>
operation.   </i>(I would create a GF and then replace the fuse for
this test)<br>
<i><br>
- Test  anti-islanding  shutdown  function  due  to  normal  utility 
source  failure, <br>
time delay and automatic restart after utility power restoration.  </i>(this
is an easy one)<br>
<i><br>
- Test  and  record  the  total  harmonic  distortion  (THD)  content 
of  output <br>
current at 25, 50, and 100 percent of system rating.  Comply with IEEE
519 <br>
at MDP point of connection. <br>
<br>
- Test  and  record  the  real  power  output  for  each  inverter, 
and  total  power <br>
delivered at the grid tie connection, for a 24 hour period.  The
continuous <br>
power   output   during   prime   solar   conditions   shall   meet  
or   exceed <br>
performance requirement under part I of this specification. <br>
<br>
- For  each  inverter,  record  DC  input  voltage  for  24  hours, 
to  demonstrate <br>
affects of maximum power point tracking (MPPT), voltage regulation
within <br>
inverter  rated  limits,  and  affect  of  partial  shading  on  solar 
modules.  <br>
Simulate  partial  shading  by  covering  50%  of  modules  during 
prime  solar <br>
conditions. <br>
<br>
- Record  of  Tests  and  Inspections:    Prepare  and  submit 
documentation  of  tests  and <br>
inspections,  including  references  to  manufacturers'  written 
instructions  and  other  test <br>
and inspection criteria.  Include results of tests, inspections, and
retests. <br>
<br>
</i><br>
Any advice would be gratefully accepted and appreciated!<br>
<br>
Best,<br>
<br>
Greg Egan<br>