<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial,helvetica,sans-serif;font-size:12pt">The more we write on this subject, the more I realize that we are saying the same thing.  I think it is important to start with a design objective of 1% to 2% for PV systems.  As you mentioned it could be 1/2%, but that would be impractical to me.  On most systems, we will lose 1/2% just on the MC cables. I do not stock #8 USE-2 nor do I stock MC connectors and strain reliefs to manage #8 MC cables, so I accept a bit of loss with the #10 MC cables.  That leaves me another 1/2% or more on the THWN-2 wiring.<br>    If we did a cost analysis on every project, then we would not need to use a rule of thumb (or design objective.)  In the system I was designing recently, with a 900' DC run, the wiring was going to cost $50,000 to keep the loss at 2% during peak
 production.  The system cost $2.4 million, so each 1% of power would be worth ~$24,000.  I ran the numbers a bunch of different ways, and in the end, I did compromise on the wire size, to keep the wiring and conduit costs reasonable.  In the end, the wire and conduit did account for 2-3% of the cost of the system.  In my design, I designed the system with the lowest voltage the array would ever produce power at, and I used peak power production for my numbers, so I knew that my real world efficiencies would be even higher, so in the end, I am probably near 1.5% voltage drop, which is fine for me.  If I can design that system with a 1-2% voltage drop, then I doubt that many systems would justify a 3% loss. <br><div> </div>Nick Soleil<br>Project Manager<br>Advanced Alternative Energy Solutions, LLC<br>PO Box 657<br>Petaluma, CA 94953<br>Cell:   707-321-2937<br>Office: 707-789-9537<br>Fax:    707-769-9037<div><br></div><div
 style="font-family: arial,helvetica,sans-serif; font-size: 12pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font size="2" face="Tahoma"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Kent Osterberg <kent@coveoregon.com><br><b><span style="font-weight: bold;">To:</span></b> RE-wrenches <re-wrenches@lists.re-wrenches.org><br><b><span style="font-weight: bold;">Sent:</span></b> Mon, April 12, 2010 10:51:10 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [RE-wrenches] DC wire sizing<br></font><br>
<meta http-equiv="x-dns-prefetch-control" content="off">


  

I know you wouldn't, Warren.  Because it is much more economical (that
means more kWh/$) to use a MPPT controller.  But you would run a
100-volt 30-amp PV array to a MPPT charge controller that is 150 feet
away.  For that distance, it takes 1/0 wire to get the wire loss down
to 1%.  I'd probably settle for using 3 AWG copper with 2% loss.  With
the smaller wire, the looses are 29 watts more, but the system cost is
less by at least $700.  At $700/29 watts = $24/watt, the 1/0 wire is
not a good choice.<br>
<br>
My question is: what is the rational for using 1% loss as the design
objective.  Why not 1/2%?  Why not 2%?<br>
So far no one has offered an answer to that question; despite many
claiming that 1% or 1.5% is always their design objective.<br>
<br>
In Home Power issue 104, December 2004 - January 2005, I showed that
striving for low voltage drops in low-voltage systems doesn't mean
you've got a good (economical) design.  The spreadsheet I created for
that article is no longer available, but one that is easier to use is
available from Ray Walters' web site.  In SolarPro 3.2, February -
March 2010, Blake Gleason shows an example where upsizing the wire size
to get 2.6% loss is not economical.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>
<br>
<br>
Warren Lauzon wrote:
<blockquote type="cite">

  
  
  <style></style>
  <div><font size="2" face="Calibri">I would never design such a
system. That is what MPPT controllers are for. 10 years ago we did not
have that choice, but now we do, so there is no reason at all to design
a 40 amp 12 volt array circuit.</font></div>
  <div> </div>
  <div>..................................................................................................<br>
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979<br><span>
Solar Discussion Forum: <a target="_blank" href="http://www.wind-sun.com/ForumVB/">http://www.wind-sun.com/ForumVB/</a></span><br>
..................................................................................................</div>
  <blockquote style="border-left: 2px solid rgb(0, 0, 0); padding-left: 5px; padding-right: 0px; margin-left: 5px; margin-right: 0px;">
    <div style="font: 10pt arial;">-----
Original Message ----- </div>
    <div style="background: none repeat scroll 0% 50% rgb(228, 228, 228); font: 10pt arial;"><b>From:</b>
    <a rel="nofollow" title="kent@coveoregon.com" ymailto="mailto:kent@coveoregon.com" target="_blank" href="mailto:kent@coveoregon.com">Kent Osterberg</a> </div>
    <div style="font: 10pt arial;"><b>To:</b>
    <a rel="nofollow" title="re-wrenches@lists.re-wrenches.org" ymailto="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" href="mailto:re-wrenches@lists.re-wrenches.org">Wrenches</a> </div>
    <div style="font: 10pt arial;"><b>Sent:</b>
Saturday, April 10, 2010 9:22 AM</div>
    <div style="font: 10pt arial;"><b>Subject:</b>
[RE-wrenches] DC wire sizing</div>
    <div><br>
    </div>
Here's my challenge to all of you that want to design for 1% or 1.5%
voltage drop all the time:<br>
Take a 50-ft circuit carrying 40 amps at 12 volts, going to a C40
charge controller, select your wire size for 1% or 1.5% loss. You know
that's not a practical solution.  I know that it makes more sense to
replace the charge controller and run the PV circuit at a higher
voltage.<br>
    <br>
    <b>At % loss did it become impractical?</b>  Ray's answer and my
answer is "when there is a cheaper alternative -- lower cost per watt
out or lower cost per kWh over the project life."  And that answer
works even when you are considering a 400-kW PV array that is 1000 feet
away.<br>
    <br>
Kent Osterberg<br>