<DIV><FONT size=2 face=Calibri>I would never design such a system. That is what 
MPPT controllers are for. 10 years ago we did not have that choice, but now we 
do, so there is no reason at all to design a 40 amp 12 volt array 
circuit.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV>..................................................................................................<BR>Northern 
Arizona Wind & Sun - Electricity From The Sun Since 1979<BR>Solar Discussion 
Forum: <A 
href="http://www.wind-sun.com/ForumVB/">http://www.wind-sun.com/ForumVB/</A><BR>..................................................................................................</DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=kent@coveoregon.com href="mailto:kent@coveoregon.com">Kent 
  Osterberg</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">Wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Saturday, April 10, 2010 9:22 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] DC wire 
  sizing</DIV>
  <DIV><BR></DIV>Here's my challenge to all of you that want to design for 1% or 
  1.5% voltage drop all the time:<BR>Take a 50-ft circuit carrying 40 amps at 12 
  volts, going to a C40 charge controller, select your wire size for 1% or 1.5% 
  loss. You know that's not a practical solution.  I know that it makes 
  more sense to replace the charge controller and run the PV circuit at a higher 
  voltage.<BR><BR><B>At % loss did it become impractical?</B>  Ray's answer 
  and my answer is "when there is a cheaper alternative -- lower cost per watt 
  out or lower cost per kWh over the project life."  And that answer works 
  even when you are considering a 400-kW PV array that is 1000 feet 
  away.<BR><BR>Kent Osterberg<BR>Blue Mountain Solar, Inc.<BR><BR>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>