Here's my challenge to all of you that want to design for 1% or 1.5%
voltage drop all the time:<br>
Take a 50-ft circuit carrying 40 amps at 12 volts, going to a C40
charge controller, select your wire size for 1% or 1.5% loss. You know
that's not a practical solution.  I know that it makes more sense to
replace the charge controller and run the PV circuit at a higher
voltage.<br>
<br>
<b>At % loss did it become impractical?</b>  Ray's answer and my answer
is "when there is a cheaper alternative -- lower cost per watt out or
lower cost per kWh over the project life."  And that answer works even
when you are considering a 400-kW PV array that is 1000 feet away.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>