Thanks Robin.  I've long been suspicious that the CBI circuit breakers
should not be run at 100% for a couple reasons:<br>
1) I've seen too many 60-amp CBI breakers on charge controllers trip
habitually.  But a replacement 60-amp breaker works fine.<br>
2) Nothing in the CBI literature that is available on their web site
says the QY breakers are rated to operate at 100%.<br>
The published trip curve shows that the breaker is supposed to hold at
less than 105% of rating and trip at more than 130% of rating.  <br>
The trip curve for a QO breaker shows that it is supposed to hold at
100% of rating and trip at 130% of rating too.  Yet we know that it is
not intended for continuous operation at 100% of rating.  <br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>
<br>
<br>
boB Gudgel wrote:
<blockquote cite="mid:4BB7ABD7.9040608@midnitesolar.com" type="cite"><br>
Forwarding a message from Robin Gudgel...
  <br>
  <br>
Robin Gudgel wrote:
  <br>
  <blockquote type="cite">The CBI QY series of DC breakers have an arc
shoot that is required to
    <br>
quench a DC arc. This breaker would work just fine as an AC breaker
although
    <br>
is not marked as such. I am not sure if the AC breakers (QL, QZ and QZD
    <br>
series) have the arc shoot. I was told years ago by CBI that the AC and
DC
    <br>
breakers are built the same, but I had never broke one open to see if
the
    <br>
arc shoot is present on AC breakers until today. The AC breakers do in
fact
    <br>
have the same arc shoot as the DC breakers. CBI just marks the outside
of
    <br>
the breakers differently. You don't want to get called on the AC vs. DC
    <br>
issue by an inspector because you are going to lose that battle. It
makes
    <br>
things a bit confusing to have a DC breaker in an AC circuit even
though
    <br>
they are identical inside. I believe Allan Sindelar was in the field
and had
    <br>
a situation where it saved a bunch of time and hassle to use a QY
breaker
    <br>
instead of a QL that he did not have on hand. I had told him that the
DC
    <br>
breaker would function just fine as an AC breaker. That installation
was
    <br>
safe, but an inspector would probably make you change to an AC breaker.
    <br>
    <br>
I remember years ago seeing in print that a Hydraulic/Magnetic breaker
could
    <br>
be used at 100% duty rating where as a thermal breaker could only be
used at
    <br>
80%. I have searched and searched to find this written explanation
again to
    <br>
no avail. I thought it was in the NEC, but I now believe I was wrong.
If the
    <br>
NEC does not allow the use of H/M breakers to be used at 100% duty
cycle,
    <br>
then it just is not allowed. It is true that the H/M breakers are not
    <br>
affected by temperature like thermal breakers are, but that in itself
    <br>
doesn't overrule the NEC. I personally have been spreading this myth to
    <br>
hundreds of installers for 10 years. I now believe I was wrong. Sure
wish I
    <br>
could find that written explanation from years ago! Perhaps it came
from CBI
    <br>
or some other circuit breaker manufacturer? (see below) Maybe an old
version of the NEC?
    <br>
The NEC is the top authority, so please use the same de-rating
guidelines
    <br>
for CBI as for thermal breakers.
    <br>
Sorry for perpetuating this widely accepted myth.
    <br>
  </blockquote>
  <br>
PS.  Robin found this and thinks that this may have been one of the
texts but still
  <br>
does not override NEC requirements
  <br>
  <br>
  <blockquote type="cite">From Heinamann:
    <br>
  </blockquote>
  <br>
Continuous operation at 100%current.
  <br>
There is no such assurance with a thermal device, which may
  <br>
fail to carry rated current when subjected to above normal ambient
  <br>
temperatures. A Heinemann breaker rated at 20 amperes, for example,
  <br>
will sustain 20 amperes, even at elevated temperatures. Derating
  <br>
and other forms of temperature compensation are unnecessary.
  <br>
  <br>
  <br>
  <blockquote type="cite">Robin Gudgel
    <br>
MidNite Solar
    <br>
    <br>
  </blockquote>
  <br>
  <br>
  <br>
  <br>
  <br>
  <br>
  <blockquote type="cite">-------- Original Message --------
    <br>
Subject:     Re: [RE-wrenches] DC wire sizing
    <br>
Date:     Fri, 02 Apr 2010 16:35:49 -0600
    <br>
From:     Allan Sindelar <a class="moz-txt-link-rfc2396E" href="mailto:allan@positiveenergysolar.com"><allan@positiveenergysolar.com></a>
    <br>
Reply-To:     <a class="moz-txt-link-abbreviated" href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>, RE-wrenches
<a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a>
    <br>
    <br>
    <br>
    <br>
Yes, they are 100% duty rated. Also, a little-known fact about the CBI
breakers used by Midnite and Outback, gleaned from conversations with
Robin Gudgel: because of this hydraulic/magnetic construction, all are
capable of controlling both AC and DC, even if not listed as both.
    <br>
    <br>
*Allan** Sindelar*
    <br>
<a class="moz-txt-link-abbreviated" href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a>
<a class="moz-txt-link-rfc2396E" href="mailto:Allan@positiveenergysolar.com"><mailto:Allan@positiveenergysolar.com></a>
    <br>
NABCEP Certified Photovoltaic Installer
    <br>
EE98J Journeyman Electrician
    <br>
*Positive Energy, Inc.*
    <br>
3201 Calle Marie
    <br>
Santa Fe, New Mexico 87507
    <br>
*505 424-1112*
    <br>
<a class="moz-txt-link-abbreviated" href="http://www.positiveenergysolar.com">www.positiveenergysolar.com</a> <a class="moz-txt-link-rfc2396E" href="http://www.positiveenergysolar.com/"><http://www.positiveenergysolar.com/></a>
    <br>
    <br>
    <br>
    <br>
robert ellison wrote:
    <br>
 
    <blockquote type="cite">I believe that the breakers from CBI,
Midnite and Outback are hydraulic / magnetic and may be operated at
100% While the derating applies to all others that are Thermal /
magnetic,
      <br>
 
      <br>
Bob
      <br>
      <br>
On Fri, Apr 2, 2010 at 11:14 AM, Kent Osterberg <<a class="moz-txt-link-abbreviated" href="mailto:kent@coveoregon.com">kent@coveoregon.com</a>
<a class="moz-txt-link-rfc2396E" href="mailto:kent@coveoregon.com"><mailto:kent@coveoregon.com></a>> wrote:
      <br>
      <br>
    Erika,
      <br>
      <br>
    You should refer to NEC 690.8 this information.  There are two
      <br>
    issues that contribute to the 1.56 factor.  First is that the
      <br>
    maximum current from the PV array is considered the short circuit
      <br>
    current multiplied by 1.25 to account for higher than standard
      <br>
    irradiance such as cloud edge effect, high altitude, and high
      <br>
    operating temperature.  The second multiplier of 1.25 is because
      <br>
    PV current is considered to be continuous.  All conductors (and
      <br>
    breakers) operating continuously (over three hours I believe) that
      <br>
    are subject to NEC rules are limited to 80% of the ampacity in
      <br>
    Table 310.16.  The two 1.25 factors equals 1.56.
      <br>
      <br>
    For normal operation, wires selected under this criteria are
      <br>
    conservatively rated.  But it is also the objective of the NEC to
      <br>
    design power systems in a manner that they will remain safe under
      <br>
    abnormal circumstances.
      <br>
      <br>
    Kent Osterberg
      <br>
    Blue Mountain Solar, Inc.
      <br>
      <br>
      <br>
      <br>
      <br>
    Erika M. Weliczko wrote:
      <br>
   
      <blockquote type="cite">    To my understanding the 156% on PV
source and output circuits is
        <br>
    related to the ability of PV to deliver more than rated and be
        <br>
    continuous.
        <br>
        <br>
    Therefore, the wire has to be able to carry this current, so now
        <br>
    the temperature and fill corrections are applied to find the wire
        <br>
    capable of the 156%.
        <br>
        <br>
     <br>
    I am in a debate where the question is why correct for temp and
        <br>
    fill on 156% of ISC and spend all that extra money when the
        <br>
    normal operating is at Imp. Or why correct the 156% but why not
        <br>
    correct the Isc or Imp.
        <br>
        <br>
     <br>
    I am going to stick to the fact that the circuit has to carry the
        <br>
    156% under all conditions.
        <br>
        <br>
    Thoughts?
        <br>
        <br>
     <br>
    Erika
        <br>
        <br>
        <br>
      </blockquote>
    _______________________________________________
      <br>
    List sponsored by Home Power magazine
      <br>
      <br>
    List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
      <br>
    <a class="moz-txt-link-rfc2396E" href="mailto:RE-wrenches@lists.re-wrenches.org"><mailto:RE-wrenches@lists.re-wrenches.org></a>
      <br>
      <br>
    Options & settings:
      <br>
   
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
    List-Archive:
      <br>
    <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
    List rules & etiquette:
      <br>
    <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
      <br>
    <a class="moz-txt-link-rfc2396E" href="http://www.re-wrenches.org/etiquette.htm"><http://www.re-wrenches.org/etiquette.htm></a>
      <br>
      <br>
    Check out participant bios:
      <br>
    <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
<a class="moz-txt-link-rfc2396E" href="http://www.members.re-wrenches.org/"><http://www.members.re-wrenches.org/></a>
      <br>
      <br>
      <br>
      <br>
------------------------------------------------------------------------
      <br>
      <br>
_______________________________________________
      <br>
List sponsored by Home Power magazine
      <br>
      <br>
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
      <br>
      <br>
Options & settings:
      <br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
      <br>
      <br>
List-Archive:
      <br>
    </blockquote>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
    <br>
 
    <blockquote type="cite">List rules & etiquette:
      <br>
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
      <br>
      <br>
Check out participant bios:
      <br>
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
      <br>
      <br>
      </blockquote>
    <br>
    <br>
  </blockquote>
  <br>
_______________________________________________
  <br>
List sponsored by Home Power magazine
  <br>
  <br>
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
  <br>
  <br>
Options & settings:
  <br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
  <br>
  <br>
List-Archive:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
  <br>
  <br>
List rules & etiquette:
  <br>
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
  <br>
  <br>
Check out participant bios:
  <br>
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
  <br>
  <br>
  <pre wrap="">
<hr size="4" width="90%">

No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a> 
Version: 9.0.800 / Virus Database: 271.1.1/2787 - Release Date: 04/02/10 23:32:00

  </pre>
</blockquote>
</body>
</html>