Nick, <br><br>The answer would be technically yes, but with limitations and I'd question whether there would be any benefits, only downsides.<br><br>To elaborate -- yes it's possible to install two XWs on two different batteries, using two different arrays and charging sources, but sharing the same AC grid and backup generator (if the generator is big enough).  The key is, they'd be totally different systems, with totally different outputs to different protected load panels.  You might be able to stuff both systems into one shared XW PDP, but it 
would require custom wiring and bypass solutions, and any service work to one system would almost certainly mandate shutting both systems down.  No communications or shared components between the two systems -- so you just doubled your costs on balance of system and metering.  No master/slave relationship would exist (each inverter is master of its own system), so tare losses increase, and max surge capacity decreases.  Imbalanced loads between the two systems could deplete one battery bank and trigger a shutdown of those loads while the other bank had reserves left to spare.<br>
<br>I think your client would be better off investing in a high quality battery bank, and taking good care of it.<br><br clear="all">Phil Undercuffler<br>Conergy<br><br><br><br>
<br><br><div class="gmail_quote">On Tue, Mar 30, 2010 at 11:58 PM, Nick Vida <span dir="ltr"><<a href="mailto:nickvida@ymail.com">nickvida@ymail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div><div style=""><div>Hi wrenches,<br></div><div><br></div><div>I am looking at the xantrex XW system with 2 inverters, and I asked their tech support if it is possible to have 2 inverters synced to the same grid and backup power, but without being parraled on the battery bank. My hope was that the 2 inverters could switch between master and slave based on state of charge for 2 separate battery banks, with 2 separate charge controllers. The backup would be a generator, and could be 2 different gennies, one on each system, or perhaps one generator on a 2 inverter grid. I know it is a lot more inverter than what is probably needed, but i would really like to have 2 separate banks to avoid weaker cell issues. </div>
<div>do you wrenches have any thoughts on this little dream? and no, xw cannot sync the
 frequency without being on the same battery bank with one master and one slave in parallel according to what I was told.</div>      </div><br>

      </div><br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>