<div>Hi All,</div>
<div> </div>
<div>Next to grounding, I find the calculation of the maximum amount of backfeed current allowed in a supply side connection to be the most vague issue in Article 690.  Let's assume we have a 400A, 480/277 service in a commercial building, a 400A main service disconnect, and the jurisdiction is under NEC 2008.  What is the maximum backfeed current allowed in a supply side connection?  The only place the code points you to is 230.82(6), which is no help, or to Article 705, which is no help either.  I know that in the draft version of NEC 2011, there is an expansion of 705.12(A) which states "<b><font size="2" face="Times New Roman"><font size="2" face="Times New Roman"> </font></font></b>Supply Side. An electric power production source shall be permitted to be connected to the supply side of the service disconnecting means as permitted in 230.82(6). The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service."  That is a helpful sentence from the Code, but as it is in draft form, what do we do under NEC 2008?  What have you used as a maximum backfeed current for supply side connections?</div>


<div> </div>
<div>Thanks,</div>
<div>Mike<br clear="all">--<br>Michael Kelly<br>Project Manager / Project Engineer<br>NABCEP Certified Solar PV Installer ™<br><br>SolarFlair Energy, Inc.<br>11 Mayhew Street<br>Framingham, MA 01702<br>Direct Mobile: 617-899-9840<br>

Main Phone: 508-293-4293<br>Main Fax: 508-293-4003<br><a href="mailto:mike@solarflair.com">mike@solarflair.com</a><br></div>