<DIV><FONT size=2 face=Calibri>We usually figure that (for example) in a 
2-string bank, that one conductor could carry 2/3 of the current if the 
batteries are unbalanced for some reason. In other words, rather than cutting 
the amperage rating in half, we cut it by about 1/3. For 3 banks would cut it by 
1/2, etc.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV><FONT size=2 face=Calibri>Probably not ideal in theory, as in a worst case 
scenario you could have one totally failed bank, but on the other hand selling 
the customer on a full array of expensive 4/0 jumpers is not always an easy 
thing to do. In fact if someone is using that much battery, they should probably 
be using a 24 or 48 volt system.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV>..................................................................................................<BR>Northern 
Arizona Wind & Sun - Electricity From The Sun Since 1979<BR>Solar Discussion 
Forum: <A 
href="http://www.wind-sun.com/ForumVB/">http://www.wind-sun.com/ForumVB/</A><BR>..................................................................................................</DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=allan@positiveenergysolar.com 
  href="mailto:allan@positiveenergysolar.com">Allan Sindelar</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, February 19, 2010 10:03 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] single string 
  of batts: must the interconnects be inverter size cables?</DIV>
  <DIV><BR></DIV>Phil,<BR>Given the scenario that Mick presented, your advice is 
  sound, and I'd do as you suggest. But by changing the scenario just a bit, it 
  brings up a separate but related issue. <BR><BR>Mick's scenario describes two 
  12V batteries in series, or a single string. In that case all current flows 
  through the one string, so a series interconnect would need to be sized equal 
  to the battery cables, in this case 4/0. But if there were two (or more) 
  parallel strings, would the same size requirement apply? That is, if a battery 
  bank had two strings, in theory each would carry 180 max amps (your example, 
  8,000/22, shared by 2 strings), which is within the ampacity of 2/0 
  interconnects. In reality, this only applies if current is equally spread 
  among strings. Is it? <BR><BR>It seems to me that a properly wired and torqued 
  set will split current paths equally until a cell fails, either prematurely or 
  when the set approaches end of life. If there are three strings, then failure 
  of one cell/string in this example would still not exceed ampacity on the 
  remaining 2/0 strings.<BR><BR>As with many issues, the goal is to find a 
  balance between safety and performance versus cost and worst-case 
  accommodation. I will always use 4/0 with one cell string and a 250A breaker, 
  but I have never seen a real-world problem using 2/0 interconnects, both 
  series and parallel, with 2 or more strings. Phil, what do you say? 
  Others?<BR><BR>
  <DIV class=moz-signature>
  <META name=ProgId content=Word.Document>
  <META name=Generator content="Microsoft Word 11">
  <META name=Originator content="Microsoft Word 11"><LINK rel=File-List 
  href="signature_files/filelist.xml"><!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>2</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2009-12-09T22:29:00Z</o:Created>
  <o:LastSaved>2009-12-09T22:30:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>52</o:Words>
  <o:Characters>298</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>2</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>349</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!
--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]--> 
  <STYLE>@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.25in 1.0in 1.25in; mso-header-margin: .5in; mso-footer-margin: .5in; mso-paper-source: 0; }
P.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; COLOR: black; FONT-SIZE: 12pt; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
LI.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; COLOR: black; FONT-SIZE: 12pt; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
DIV.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"; COLOR: black; FONT-SIZE: 12pt; mso-style-parent: ""; mso-pagination: widow-orphan; mso-fareast-font-family: "Times New Roman"
}
A:link {
        COLOR: blue
}
SPAN.MsoHyperlink {
        COLOR: blue
}
A:visited {
        COLOR: blue
}
SPAN.MsoHyperlinkFollowed {
        COLOR: blue
}
SPAN.il {
        mso-style-name: il
}
DIV.Section1 {
        page: Section1
}
</STYLE>
<!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
  <DIV class=Section1>
  <P class=MsoNormal><SPAN class=il><B>Allan</B></SPAN><B> Sindelar</B><SPAN 
  style="FONT-SIZE: 10pt"><BR><A href="mailto:Allan@positiveenergysolar.com" 
  target=_blank><SPAN 
  class=il>Allan</SPAN>@positiveenergysolar.com</A><BR>NABCEP Certified 
  Photovoltaic Installer<BR>EE98J Journeyman Electrician<BR><B>Positive Energy, 
  Inc.</B><BR>3201 Calle Marie<BR>Santa Fe, New Mexico 87507<BR><B>505 
  424-1112</B><BR><A href="http://www.positiveenergysolar.com/" 
  target=_blank>www.positiveenergysolar.com</A></SPAN></P></DIV></DIV><BR><BR>Phil 
  Undercuffler wrote: 
  <BLOCKQUOTE 
  cite=mid:8a40c54d1002191128u3a3b199au1625e30c09aeb2a@mail.gmail.com 
  type="cite">The interconnects are part of the circuit.  Typical 
    flexible cables used with batteries are THW rated (75C column), so in free 
    air 2/0 interconnects would be good for 265 amps, before any temperature 
    derates.  Therefore, you'd be safe from a NEC point of view.  
    However, if the inverter manufacturer has recommended 4/0 cables, then that 
    recommendation would apply to all cables in the circuit.  Battery based 
    inverters are asked to surge many times their rated capacity -- a 24V 4kW 
    inverter surging to 2x capacity (pretty normal circumstances) is going to 
    draw over 360 amps (8,000 / 22), even if only for a short period of 
    time.  You don't want your interconnects to be the weak link in the 
    system, causing shutdowns due to undervoltage unnecessarily.  
    <BR><BR>I'd use 4/0.<BR><BR clear=all>Phil 
    Undercuffler<BR>Conergy<BR><BR><BR><BR><BR><BR>
    <DIV class=gmail_quote>On Fri, Feb 19, 2010 at 12:01 PM, Mick Abraham <SPAN 
    dir=ltr><<A href="mailto:mick@abrahamsolar.com" 
    moz-do-not-send="true">mick@abrahamsolar.com</A>></SPAN> wrote:<BR>
    <BLOCKQUOTE 
    style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" 
    class=gmail_quote>Example: 12 two volt battery cells in one 24 volt 
      string. 4kW inverter/charger has 250 amp DC breaker size and 4/0 
      cables...as the inverter folks would want.<BR><BR>So...do the "cell to 
      cell" interconnect cables have to also be 4/0? In the example above, 2/0 
      interconnects would suffice from the standpoint of basic safety...and even 
      from the voltage drop standpoint...right?<BR><BR>Inverter company people 
      may be best qualified to answer this, but any replies will be appreciated. 
      While I'm at it: do the inverter folks request oversize cables because 
      they want more capacitance on the DC input...or 
      what?<BR><BR>Jolliness,<BR><BR clear=all>Mick Abraham, Proprietor<BR><A 
      href="http://www.abrahamsolar.com" target=_blank 
      moz-do-not-send="true">www.abrahamsolar.com</A><BR><BR>Voice: 
      970-731-4675<BR><BR>_______________________________________________<BR>List 
      sponsored by Home Power magazine<BR><BR>List Address: <A 
      href="mailto:RE-wrenches@lists.re-wrenches.org" 
      moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
      & settings:<BR><A 
      href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
      target=_blank 
      moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
      <A 
      href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
      target=_blank 
      moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
      rules & etiquette:<BR><A 
      href="http://www.re-wrenches.org/etiquette.htm" target=_blank 
      moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</A><BR><BR>Check 
      out participant bios:<BR><A href="http://www.members.re-wrenches.org" 
      target=_blank 
      moz-do-not-send="true">www.members.re-wrenches.org</A><BR><BR><BR></BLOCKQUOTE></DIV><BR><PRE wrap=""><HR SIZE=4 width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <A class=moz-txt-link-abbreviated href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A>

Options & settings:
<A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A>

List-Archive: <A class=moz-txt-link-freetext href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A>

List rules & etiquette:
<A class=moz-txt-link-abbreviated href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A>

Check out participant bios:
<A class=moz-txt-link-abbreviated href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</A>

  </PRE></BLOCKQUOTE>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>