Phil,<br>
Given the scenario that Mick presented, your advice is sound, and I'd
do as you suggest. But by changing the scenario just a bit, it brings
up a separate but related issue. <br>
<br>
Mick's scenario describes two 12V batteries in series, or a single
string. In that case all current flows through the one string, so a
series interconnect would need to be sized equal to the battery cables,
in this case 4/0. But if there were two (or more) parallel strings,
would the same size requirement apply? That is, if a battery bank had
two strings, in theory each would carry 180 max amps (your example,
8,000/22, shared by 2 strings), which is within the ampacity of 2/0
interconnects. In reality, this only applies if current is equally
spread among strings. Is it? <br>
<br>
It seems to me that a properly wired and torqued set will split current
paths equally until a cell fails, either prematurely or when the set
approaches end of life. If there are three strings, then failure of one
cell/string in this example would still not exceed ampacity on the
remaining 2/0 strings.<br>
<br>
As with many issues, the goal is to find a balance between safety and
performance versus cost and worst-case accommodation. I will always use
4/0 with one cell string and a 250A breaker, but I have never seen a
real-world problem using 2/0 interconnects, both series and parallel,
with 2 or more strings. Phil, what do you say? Others?<br>
<br>
<div class="moz-signature">
<meta http-equiv="Content-Type" content="text/html; ">
<meta name="ProgId" content="Word.Document">
<meta name="Generator" content="Microsoft Word 11">
<meta name="Originator" content="Microsoft Word 11">
<link rel="File-List" href="signature_files/filelist.xml">
<!--[if gte mso 9]><xml>
 <o:DocumentProperties>
  <o:Author>pe</o:Author>
  <o:LastAuthor>pe</o:LastAuthor>
  <o:Revision>2</o:Revision>
  <o:TotalTime>1</o:TotalTime>
  <o:Created>2009-12-09T22:29:00Z</o:Created>
  <o:LastSaved>2009-12-09T22:30:00Z</o:LastSaved>
  <o:Pages>1</o:Pages>
  <o:Words>52</o:Words>
  <o:Characters>298</o:Characters>
  <o:Company>pe</o:Company>
  <o:Lines>2</o:Lines>
  <o:Paragraphs>1</o:Paragraphs>
  <o:CharactersWithSpaces>349</o:CharactersWithSpaces>
  <o:Version>11.9999</o:Version>
 </o:DocumentProperties>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <w:WordDocument>
  <w:SpellingState>Clean</w:SpellingState>
  <w:GrammarState>Clean</w:GrammarState>
  <w:ValidateAgainstSchemas/>
  <w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
  <w:IgnoreMixedContent>false</w:IgnoreMixedContent>
  <w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
  <w:BrowserLevel>MicrosoftInternetExplorer4</w:BrowserLevel>
 </w:WordDocument>
</xml><![endif]--><!
--[if gte mso 9]><xml>
 <w:LatentStyles DefLockedState="false" LatentStyleCount="156">
 </w:LatentStyles>
</xml><![endif]-->
<style>
<!--
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {mso-style-parent:"";
        margin:0in;
        margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:12.0pt;
        font-family:"Times New Roman";
        mso-fareast-font-family:"Times New Roman";
        color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.il
        {mso-style-name:il;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.25in 1.0in 1.25in;
        mso-header-margin:.5in;
        mso-footer-margin:.5in;
        mso-paper-source:0;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 10]>
<style>
 /* Style Definitions */
 table.MsoNormalTable
        {mso-style-name:"Table Normal";
        mso-tstyle-rowband-size:0;
        mso-tstyle-colband-size:0;
        mso-style-noshow:yes;
        mso-style-parent:"";
        mso-padding-alt:0in 5.4pt 0in 5.4pt;
        mso-para-margin:0in;
        mso-para-margin-bottom:.0001pt;
        mso-pagination:widow-orphan;
        font-size:10.0pt;
        font-family:"Times New Roman";
        mso-ansi-language:#0400;
        mso-fareast-language:#0400;
        mso-bidi-language:#0400;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1"/>
 </o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal" style=""><span class="il"><b style="">Allan</b></span><b
 style=""> Sindelar</b><span style="font-size: 10pt;"><br>
<a href="mailto:Allan@positiveenergysolar.com" target="_blank"><span
 class="il">Allan</span>@positiveenergysolar.com</a><br>
NABCEP Certified Photovoltaic Installer<br>
EE98J Journeyman Electrician<br>
<b style="">Positive Energy, Inc.</b><br>
3201 Calle Marie<br>
Santa Fe, New Mexico 87507<br>
<b style="">505 424-1112</b><br>
<a href="http://www.positiveenergysolar.com/" target="_blank">www.positiveenergysolar.com</a></span></p>
</div>
</div>
<br>
<br>
Phil Undercuffler wrote:
<blockquote
 cite="mid:8a40c54d1002191128u3a3b199au1625e30c09aeb2a@mail.gmail.com"
 type="cite">The interconnects are part of the circuit.  Typical
flexible cables used with batteries are THW rated (75C column), so in
free air 2/0 interconnects would be good for 265 amps, before any
temperature derates.  Therefore, you'd be safe from a NEC point of
view.  However, if the inverter manufacturer has recommended 4/0
cables, then that recommendation would apply to all cables in the
circuit.  Battery based inverters are asked to surge many times their
rated capacity -- a 24V 4kW inverter surging to 2x capacity (pretty
normal circumstances) is going to draw over 360 amps (8,000 / 22), even
if only for a short period of time.  You don't want your interconnects
to be the weak link in the system, causing shutdowns due to
undervoltage unnecessarily.  <br>
  <br>
I'd use 4/0.<br>
  <br clear="all">
Phil Undercuffler<br>
Conergy<br>
  <br>
  <br>
  <br>
  <br>
  <br>
  <div class="gmail_quote">On Fri, Feb 19, 2010 at 12:01 PM, Mick
Abraham <span dir="ltr"><<a moz-do-not-send="true"
 href="mailto:mick@abrahamsolar.com">mick@abrahamsolar.com</a>></span>
wrote:<br>
  <blockquote class="gmail_quote"
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">Example:
12 two volt battery cells in one 24 volt string. 4kW inverter/charger
has 250 amp DC breaker size and 4/0 cables...as the inverter folks
would want.<br>
    <br>
So...do the "cell to cell" interconnect cables have to also be 4/0? In
the example above, 2/0 interconnects would suffice from the standpoint
of basic safety...and even from the voltage drop standpoint...right?<br>
    <br>
Inverter company people may be best qualified to answer this, but any
replies will be appreciated. While I'm at it: do the inverter folks
request oversize cables because they want more capacitance on the DC
input...or what?<br>
    <br>
Jolliness,<br>
    <br clear="all">
Mick Abraham, Proprietor<br>
    <a moz-do-not-send="true" href="http://www.abrahamsolar.com"
 target="_blank">www.abrahamsolar.com</a><br>
    <br>
Voice: 970-731-4675<br>
    <br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
    <br>
List Address: <a moz-do-not-send="true"
 href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
    <br>
Options & settings:<br>
    <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
 target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
    <br>
List-Archive: <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
 target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
    <br>
List rules & etiquette:<br>
    <a moz-do-not-send="true"
 href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
    <br>
Check out participant bios:<br>
    <a moz-do-not-send="true" href="http://www.members.re-wrenches.org"
 target="_blank">www.members.re-wrenches.org</a><br>
    <br>
    <br>
  </blockquote>
  </div>
  <br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
</blockquote>
</body>
</html>