<DIV><FONT size=2 face=Calibri>In your case, yes the battery cables should also 
be 4/0. They are carrying the same load as the inverter cables. Max amp rating 
on 2/0 is around 190 amps, and that inverter can surge to well over 250, even 
though at 4kw it would pull around 180.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV><FONT size=2 face=Calibri>And a nitpick - those  are not cells, they 
are batteries. Each battery has 6 cells.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV>..................................................................................................<BR>Northern 
Arizona Wind & Sun - Electricity From The Sun Since 1979<BR>Solar Discussion 
Forum: <A 
href="http://www.wind-sun.com/ForumVB/">http://www.wind-sun.com/ForumVB/</A><BR>..................................................................................................</DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=mick@abrahamsolar.com href="mailto:mick@abrahamsolar.com">Mick 
  Abraham</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, February 19, 2010 12:01 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] single string of 
  batts: must the interconnects beinverter size cables?</DIV>
  <DIV><FONT size=2 face=Calibri></FONT><FONT size=2 
  face=Calibri></FONT><BR></DIV>Example: 12 two volt battery cells in one 24 
  volt string. 4kW inverter/charger has 250 amp DC breaker size and 4/0 
  cables...as the inverter folks would want.<BR><BR>So...do the "cell to cell" 
  interconnect cables have to also be 4/0? In the example above, 2/0 
  interconnects would suffice from the standpoint of basic safety...and even 
  from the voltage drop standpoint...right?<BR><BR>Inverter company people may 
  be best qualified to answer this, but any replies will be appreciated. While 
  I'm at it: do the inverter folks request oversize cables because they want 
  more capacitance on the DC input...or what?<BR><BR>Jolliness,<BR><BR 
  clear=all>Mick Abraham, Proprietor<BR><A 
  href="http://www.abrahamsolar.com">www.abrahamsolar.com</A><BR><BR>Voice: 
  970-731-4675<BR>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>