<DIV><FONT face=Arial size=2>Yes, </FONT></DIV>
<DIV><FONT face=Arial size=2>No  Transformers, Single inverter. 
</FONT></DIV>
<DIV><FONT face=Arial size=2>Another question, looking at the Fronius 10.1 and 
11.4-3, no battery backup of course, they both list 208v in the sizing 
tool. I need to look at a manual, but I'm not sure if I would need 
Delta, Wye, ..........</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thanks everyone!</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=bekahhren@yahoo.com href="mailto:bekahhren@yahoo.com">Rebekah 
  Hren</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=Allan@positiveenergysolar.com 
  href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</A> 
  ; <A title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, February 15, 2010 5:34 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] 3 Phase Grid 
  Tie with Battery Backup</DIV>
  <DIV><BR></DIV>
  <DIV 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'times new roman', 'new york', times, serif">
  <DIV></DIV>
  <DIV>Hi,</DIV>
  <DIV>Does the utility mean by "match" that they don't want the inverter output 
  transformed in any way? </DIV>
  <DIV>Could you not just use one 120V inverter? I've connected single 120 volt 
  inverters (albeit not outback but I don't see why not) to a 120/208 wye 
  without problems. You have to make sure the wires are sized correctly (solar 
  pro had a recent article on unbalanced 3 phase wire sizing). This of course 
  limits your backed up loads to 120V (w/out a transformer).</DIV>
  <DIV><BR></DIV>
  <DIV>Rebekah Hren</DIV>
  <DIV>North Carolina</DIV>
  <DIV><BR><BR></DIV>
  <DIV><BR></DIV>
  <DIV 
  style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><BR>
  <DIV 
  style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><FONT 
  face=Tahoma size=2>
  <HR SIZE=1>
  <B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Allan Sindelar 
  <allan@positiveenergysolar.com><BR><B><SPAN 
  style="FONT-WEIGHT: bold">To:</SPAN></B> RE-wrenches 
  <re-wrenches@lists.re-wrenches.org><BR><B><SPAN 
  style="FONT-WEIGHT: bold">Sent:</SPAN></B> Mon, February 15, 2010 6:51:12 
  PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [RE-wrenches] 
  3 Phase Grid Tie with Battery Backup<BR></FONT><BR>Yes you would. I don't 
  believe there is a single inverter that meets the utility's wishes. <BR><BR>
  <DIV class=moz-signature>
  <STYLE>
<!--
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman";color:black;}
a:link, span.MsoHyperlink
        {color:blue;}
a:visited, span.MsoHyperlinkFollowed
        {color:blue;}
span.il
        {}
 _filtered {margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
        {}
-->
</STYLE>

  <DIV class=Section1>
  <P class=MsoNormal><SPAN class=il><B>Allan</B></SPAN><B> Sindelar</B><SPAN 
  style="FONT-SIZE: 10pt"><BR><A href="mailto:Allan@positiveenergysolar.com" 
  target=_blank rel=nofollow 
  ymailto="mailto:Allan@positiveenergysolar.com"><SPAN 
  class=il>Allan</SPAN>@positiveenergysolar.com</A><BR>NABCEP Certified 
  Photovoltaic Installer<BR>EE98J Journeyman Electrician<BR><B>Positive Energy, 
  Inc.</B><BR>3201 Calle Marie<BR>Santa Fe, New Mexico 87507<BR><B>505 
  424-1112</B><BR><A href="http://www.positiveenergysolar.com/" target=_blank 
  rel=nofollow>www.positiveenergysolar.com</A></SPAN></P></DIV></DIV><BR><BR>All 
  Solar Inc. Jeremy Rodriguez wrote: 
  <BLOCKQUOTE type="cite">Thanks Darryl, <BR>Allen, would you have to use 3 
    Sunny Islands?  one for each phase? <BR>The Utility wants a single 
    inverter. <BR><BR>Jeremy <BR>----- Original Message ----- From: "Darryl 
    Thayer" <A class=moz-txt-link-rfc2396E href="mailto:daryl_solar@yahoo.com" 
    target=_blank rel=nofollow 
    ymailto="mailto:daryl_solar@yahoo.com"><daryl_solar@yahoo.com></A> 
    <BR>To: "RE-wrenches" <A class=moz-txt-link-rfc2396E 
    href="mailto:re-wrenches@lists.re-wrenches.org" target=_blank rel=nofollow 
    ymailto="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></A> 
    <BR>Sent: Monday, February 15, 2010 3:49 PM <BR>Subject: Re: [RE-wrenches] 3 
    Phase Grid Tie with Battery Backup <BR><BR><BR>I do not know what is going 
    on at Outback, but unless they reduced the product offering, they have the 
    capability.  I have such a system. <BR><BR>Use 3 of their 120 volt 
    single phase inverters connected 3-phase WYE (120/208) 3 phase.  Each 
    inverter is only a single phase, and you connect each inverter to the 
    neutral and one phase, you program one to be the Master, and the others to 
    be slaves on phase B and Phase C.  When you lose the grid, the Master 
    inverter starts its sine wave and it generates the usual 60 Hz square wave 
    on the Outback Bus and the following slave units delays the start of their 
    sin waves by the appropriate 120 degrees to generate 3 phases.  Each 
    inverter picks up and makes 60 hz 3 phase. <BR><BR>One thing, besure to get 
    a rotation meter and check that you are generating 3-phase the same rotation 
    as the grid. Else you will have big problems. (motors will reverse and you 
    may fry the OB transfer relay) <BR><BR>Next time you call outback ask a tech 
    if you can slave the GVFX to make 3 phase, <BR><BR>--- On Mon, 2/15/10, All 
    Solar Inc. Jeremy Rodriguez <A class=moz-txt-link-rfc2396E 
    href="mailto:allsolar@scswifi.net" target=_blank rel=nofollow 
    ymailto="mailto:allsolar@scswifi.net"><allsolar@scswifi.net></A> 
    wrote: <BR><BR>
    <BLOCKQUOTE type="cite">From: All Solar Inc. Jeremy Rodriguez <A 
      class=moz-txt-link-rfc2396E href="mailto:allsolar@scswifi.net" 
      target=_blank rel=nofollow 
      ymailto="mailto:allsolar@scswifi.net"><allsolar@scswifi.net></A> 
      <BR>Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup 
      <BR>To: <A class=moz-txt-link-abbreviated 
      href="mailto:starpower4u@juno.com" target=_blank rel=nofollow 
      ymailto="mailto:starpower4u@juno.com">starpower4u@juno.com</A>, 
      "RE-wrenches" <A class=moz-txt-link-rfc2396E 
      href="mailto:re-wrenches@lists.re-wrenches.org" target=_blank rel=nofollow 
      ymailto="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></A> 
      <BR>Date: Monday, February 15, 2010, 4:14 PM <BR>Jeff, <BR>That was my 
      first choice, but I was told by Outback <BR>that they do not offer <BR>a 
      120/208 inverter(s). I have not set up a three <BR>phase system yet, so 
      bare <BR>with me please. I was going to contact SMA next. <BR><BR>Jeremy 
      <BR><BR><BR>----- Original Message ----- From: "Jeff Oldham" <A 
      class=moz-txt-link-rfc2396E href="mailto:starpower4u@juno.com" 
      target=_blank rel=nofollow 
      ymailto="mailto:starpower4u@juno.com"><starpower4u@juno.com></A> 
      <BR>To: <A class=moz-txt-link-rfc2396E 
      href="mailto:Allan@positiveenergysolar.com" target=_blank rel=nofollow 
      ymailto="mailto:Allan@positiveenergysolar.com"><Allan@positiveenergysolar.com></A>; 
      <BR><A class=moz-txt-link-rfc2396E 
      href="mailto:re-wrenches@lists.re-wrenches.org" target=_blank rel=nofollow 
      ymailto="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></A> 
      <BR>Sent: Monday, February 15, 2010 3:03 PM <BR>Subject: Re: [RE-wrenches] 
      3 Phase Grid Tie with Battery <BR>Backup <BR><BR><BR>> You can also do 
      it w/Outback up to 10.8kW <BR>> <BR>>>From the Solar, Wind and 
      Hydro powered office of <BR>Jeff Oldham/Regenerative <BR>>>SOLutions 
      <BR><BR></BLOCKQUOTE><BR></BLOCKQUOTE></DIV></DIV>
  <DIV style="POSITION: fixed"></DIV></DIV><BR>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>