class=421442921-28012010>You did say you're using the neutral, so I'm assuming 
you've got the 5-jaw socket and meter (Form 12S). You also need to make sure the 
meter itself is non-detented. </SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=421442921-28012010><SPAN class=421442921-28012010>Once 
you reconfigure the socket to match the one shown in David's reference you 
should be good to go.</SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010>Not sure which aspect(s) of "utility grade" you need. 
I'll assume you mean "revenue grade" accuracy. The generally accepted threshold 
for this is +/-2% overall. </SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=421442921-28012010>A lot of analog meters (most) are 
not certified as "revenue grade" when running in the "backward" 
direction. Forget about "certified", they simply are all over the map with 
accuracy tolerance in the backward direction. For this reason, many were 
disqualified for use in Net Metering applications. Since your use is technically 
measuring the Net Generation, your accuracy may be off... Not as far off as some 
inverter manufacturers' displays have been in the past, but still 
p</SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010>ossibly quite a bit off, relatively 
speaking. Think in terms of up to +/-5%. </SPAN></FONT><FONT color=#0000ff 
size=2 face=Arial><SPAN class=421442921-28012010>Don't know if this matters for 
your purposes or not, but I thought I'd throw it out there so you don't have to 
go all the way through the learning curve by yourself. <SPAN 
class=421442921-28012010>Lonely curve, that one...</SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN 
class=421442921-28012010></SPAN></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>If Net Generation 
accuracy is critical, you have three fine choices and many that aren't so fine. 
</SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN 
class=421442921-28012010></SPAN></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>1)  The obvious 
"easy" one is to get confirmation that your meter is certified Bi-Directional 
&/or qualified/certified for Net Metering. Occupants of Meter 
Meter Neverland are particularly paranoid person-objects. Gaining a 
qualified confirmation of said information may take some sleuthing. Don't bother 
trying to get information from GE. </SPAN></SPAN></FONT><FONT color=#0000ff 
size=2 face=Arial><SPAN class=421442921-28012010><SPAN 
class=421442921-28012010>Start with the vendor who sold it to you. 
</SPAN></SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>If you have friends who 
work in the meter shop of the local electric utility, you might want 
to talk with them. <EM>Hint: If you get a blank stare from the meter guy 
when you say "Net Meter".... Just smile, excuse yourself, and go get a 
donut.</EM></SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN 
class=421442921-28012010></SPAN></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>2)  If #1 doesn't 
pan out, find a meter that does and use it.</SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN 
class=421442921-28012010></SPAN></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>3)  Use two meters 
and do some subtraction. </SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN 
class=421442921-28012010></SPAN></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010><SPAN class=421442921-28012010>Pray for 
Sun!</SPAN></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=421442921-28012010></SPAN></FONT><FONT color=#0000ff size=2 
face=Arial></FONT> </DIV>
<DIV dir=ltr align=left><SPAN class=421442921-28012010><FONT color=#0000ff 
size=2 face=Arial>Matt Lafferty</FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> David Brearley<BR></FONT></DIV>
<DIV></DIV><FONT face="Calibri, Verdana, Helvetica, Arial"><SPAN 
style="FONT-SIZE: 11pt">Is it a Form 12-S meter? If not, that’s the reason its 
not working. Here’s an article you can refer to:<BR><BR><A 
href="http://solarprofessional.com/article/?file=SP1_1_pg16_QandA_3&search=">http://solarprofessional.com/article/?file=SP1_1_pg16_QandA_3&search=</A><BR><BR><BR>On 
1/28/10 2:57 PM, "<A href="gary@arp-solar.com">gary@arp-solar.com</A>" <<A 
href="gary@arp-solar.com">gary@arp-solar.com</A>> 
wrote:<BR><BR></SPAN></FONT>
<BLOCKQUOTE><FONT size=2><FONT face="Verdana, Helvetica, Arial"><SPAN 
  style="FONT-SIZE: 10pt">I am using an analog GE kwh meter on an outback system 
  with battery backup to a protected loads panel.  The AC in to the 
  inverter is attached to the bottom of one leg of the meter and the AC out of 
  the inverter is connected to the top of the other leg. This should give me an 
  accurate record of just the production from the system. The idea is that the 
  AC IN that will power the protected loads panel at night will come in the 
  bottom of one leg and turn the meter backwards then exit through the top of 
  the meter going forward thus cancelling those kwh. out. I have a neutral 
  hooked to the meter because I am using it to record 120V but I am not getting 
  accurate readings with this configuration. Any suggestions on metering in this 
  case? I need a utility grade kwh 
  meter.  <BR> <BR></SPAN></FONT></FONT></BLOCKQUOTE></BODY></HTML>