<FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>Right, Kent, but 690.4(D) does require the use of products “identified and listed for the application.” So, for example, UL-listed combiner boxes are required per NEC 2008, whereas integrators could previously site build combiners using UL-listed parts. The appropriate listing for a PV combiner, everyone agrees, is UL1741. This code article lists most major components in a PV system, but not discos. I’m simply wondering if there is some activity I am unaware of seeking to add dc discos to this list or to the UL1741 standard. Just curious.<BR>
<BR>
<BR>
On 1/11/10 6:27 PM, "Kent Osterberg" <<a href="kent@coveoregon.com">kent@coveoregon.com</a>> wrote:<BR>
<BR>
</SPAN></FONT><BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>David,<BR>
<BR>
The NEC doesn't require UL listing. The most appropriate section of the code about this is Article 110, Requirements for Electrical Installations, it requires equipment to be approved. In many jurisdictions, such as Oregon, that means evaluated and approved by a testing lab such as UL.<BR>
<BR>
Kent Osterberg<BR>
Blue Mountain Solar, Inc.<BR>
<BR>
<BR>
David Brearley wrote: <BR>
</SPAN></FONT><BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> Re: [RE-wrenches] Square D DC disconnects Thanks, Bill.<BR>
<BR>
Glad to hear you think the HU series is still a good option.<BR>
<BR>
When I was making the rounds at SPI, I stopped by the Eaton booth and got the sense that they were gunning for Square D. They made light of Square D’s self-certification of the HU series discos. The rep also made a statement about the new Eaton dc discos being the only ones designed to meet UL1741 requirements. When I got home, the first thing I looked up was 690.4(D). This doesn’t say anything about dc disconnects needing to be listed to some special PV standard. <BR>
<BR>
Is there a movement in this direction? Is there a UL1741 standard for dc discos that is somehow different that the standard used for other dc disconnects?<BR>
<BR>
Best,<BR>
<BR>
David <BR>
<BR>
On 1/11/10 5:28 PM, "Bill Brooks" <<a href="billbrooks7@yahoo.com">billbrooks7@yahoo.com</a>> wrote:<BR>
<BR>
<BR>
</SPAN></FONT><BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><FONT COLOR="#1F497D">David and Kirpal,<BR>
<BR>
It is ultimately up to the AHJ whether or not they accept the Schneider/Square D self certification. That is a judgment call the installer needs to clear with the AHJ. That being said, having Square D behind the rating of a switch is a whole lot more than any one of the smaller companies making equipment for the PV industry. <BR>
<BR>
I will continue to use the 30, 60, and 100-amp versions in the way recommended by the manufacturer because it is a huge saving in cost and they are well made switches. I will also check with the local AHJ before installing them in case they are not going to pass it. You have to remember you are working with one of the largest electrical suppliers in the world. They have a huge reputation with local jurisdictions.<BR>
<BR>
Eaton has been in the process of trying to make a big deal out of this issue since they want a piece of the market. Fortunately, they are starting to build products specifically for the PV industry, which I applaud. However, they need to be given a hard time for the way they have tried to imply that all Square D switches are not properly listed. They won’t admit to that because they would end up in a legal battle, but that is essentially what they have been doing. Square D still has the largest selection of dc-rated equipment on the market. Eaton has a long way to go. <BR>
<BR>
In a recent project that I reviewed, the engineer pulled the Square D 400-amp disconnect and replaced it with an Eaton disconnect at the insistence of the Eaton rep. The Eaton product was not properly rated or listed for the voltage while the Square D product was. This is the insanity that needs to stop.<BR>
<BR>
Bill.<BR>
<BR>
<BR>
<BR>
</FONT> </SPAN></FONT><FONT SIZE="2"><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:10pt'><B>From:</B> <a href="re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <B>On Behalf Of </B>David Brearley<BR>
<B>Sent:</B> Monday, January 11, 2010 11:39 AM<BR>
<B>To:</B> RE-wrenches<BR>
<B>Subject:</B> Re: [RE-wrenches] Square D DC disconnects<BR>
</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>Kirpal,<BR>
<BR>
Have you checked out the SolarBOS disconnecting combiners? Their 28A version might be ideal for large resi or small commercial applications. For larger projects, Blue Oak PV Products and AMtec Solar also have disconnecting combiners.<BR>
<BR>
Thanks for sharing the updated Square D tech note. I had no idea that the Square D HU Series disconnects were not UL-listed when used as described in the older tech notes. The fact that this is not a UL-listed use of the heavy duty safety switch, pretty much means that it is not an option for integrators. As far as I know, there is no other product that is listed for this use. <BR>
<BR>
David Brearley, Senior Technical Editor<BR>
<I>SolarPro</I> magazine <BR>
NABCEP Certified PV Installer ™<BR>
<a href="david.brearley@solarprofessional.com">david.brearley@solarprofessional.com</a><BR>
<BR>
<BR>
On 1/9/10 4:14 PM, "Kirpal Khalsa" <<a href="solarworks@gmail.com">solarworks@gmail.com</a>> wrote:<BR>
<BR>
</SPAN></FONT><BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>Hi All......<BR>
<BR>
</SPAN></FONT></BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
I recently came across a revised technical bulletin from square D ( <a href="http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf">http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf</a> )......we have for years been using the Square D DC Disconnect of various amperages (30, 60, 100) as disconnects leading upto the inverter from the array.....we have frequently wired one string to each of the three poles of the disconnect......we have had this configuration inspected by inspectors regularly with approval everytime......this new revision of the document from Square D shows this is no longer a UL listed method.....they are now stating in this document that they are "self certifying" this technique.......have any of you come across this or know why Square D has back tracked? <BR>
<BR>
Something else I noticed is that they have raised the amperage rating on the 30A disconncect per pole by 2 amps from 18 to 20 which is good especially when using higher amperage modules like Evergreen ES-A series which would not have ben allowed to use the 30A disconnect as the short circuit current rating was too high for the derated poles. <BR>
<BR>
This is not a huge concern as more and more of the inverters we are using these days have an appropriate disconnect included with the inverter negating the need for an additional stand alone disconnect. <BR>
<BR>
On a side note............Are there any other manufacturers making <U>listed</U> muiti pole DC disconnects in which each pole can handle one string? Also there is definately a need for roof mounted multi string (1-4 strings) combiner boxes with integrated DC disconnects for residential applications that have a reasonable price.......any one know if any?<BR>
<BR>
<BR>
<BR>
<BR>
<BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'> <BR>
<BR>
</SPAN></FONT></FONT></BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'> <BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
<BR>
<BR>
<BR>
<HR ALIGN=CENTER SIZE="4" WIDTH="90%"><BR>
_______________________________________________<BR>
List sponsored by Home Power magazine<BR>
<BR>
List Address: <a href="RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><BR>
<BR>
Options & settings:<BR>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR>
<BR>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR>
<BR>
List rules & etiquette:<BR>
www.re-wrenches.org/etiquette.htm <<a href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>> <BR>
<BR>
Check out participant bios:<BR>
www.members.re-wrenches.org <<a href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>> <BR>
<BR>
<BR>
<BR>
<BR>
<HR ALIGN=CENTER SIZE="4" WIDTH="90%"><BR>
<BR>
No virus found in this incoming message.<BR>
Checked by AVG - www.avg.com <<a href="http://www.avg.com">http://www.avg.com</a>> <BR>
Version: 9.0.725 / Virus Database: 270.14.135/2615 - Release Date: 01/11/10 11:35:00<BR>
<BR>
<BR>
</SPAN></FONT></BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="95%"></SPAN></FONT><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'>_______________________________________________<BR>
List sponsored by Home Power magazine<BR>
<BR>
List Address: <a href="RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><BR>
<BR>
Options & settings:<BR>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR>
<BR>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR>
<BR>
List rules & etiquette:<BR>
www.re-wrenches.org/etiquette.htm<BR>
<BR>
Check out participant bios:<BR>
www.members.re-wrenches.org<BR>
<BR>
</SPAN></FONT></FONT></BLOCKQUOTE><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'><BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>David Brearley, Senior Technical Editor<BR>
<I>SolarPro</I> magazine <BR>
NABCEP Certified PV Installer ™<BR>
<a href="david.brearley@solarprofessional.com">david.brearley@solarprofessional.com</a><BR>
Direct: 541.261.6545<BR>
Fax: 541.512.0343<BR>
<B><BR>
</B>Visit our Web site at solarprofessional.com<BR>
<BR>
(Sample copy available for download at: solarprofessional.com/sample)<BR>
<BR>
<BR>
</SPAN></FONT>
</BODY>
</HTML>