<font size=3>Dick:<br><br>
Just to follow up, below is the reply I received from the inspector when
I asked for clarification.  I had asked for clarification because I
admit ignorance to this section and I wanted to formulate a good response
on the first attempt:<br><br>
<i>There must be a main disconnect for panel C in the pump house. A
main<br>
circuit breaker in panel C would satisfy this requirement. If the
panel<br>
does not have a main circuit breaker (MLO) a maximum of six branch
circuits<br>
are allowed per NEC 225.33.<br><br>
</i>I prefer to approach these requirements with generic solutions. 
The broader a solution, the more likely it will apply to other
projects.  Also, a generic solution can box you in to a certain
design.  I did not know the number of circuit breakers and did not
want to drive out to the job to find out.  Instead I put this note
on the plans:<br><br>
<i>4. Panel C shall have 6 or fewer circuit breakers or implement
Documented Safe Switching Procedures per 225.32 Exception 1.<br><br>
</i>This proved to be acceptable and a permit was issued a few days
ago.  I have since found out that there are 5 existing
breakers.  One is in the off position and may be a spare.  We
will be installing two inverters, bringing the number of breakers to
7.  If I can remove one breaker, I achieve compliance that way. If I
can not remove a breaker, I write up a procedure, post it and I'm
good.<br><br>
Thanks for your input.<br><br>
William Miller<br><br>
<br><br>
At 06:33 PM 12/11/2009, you wrote:<br>
<blockquote type=cite class=cite cite>William,<br><br>
No, I mean what is your problem with complying with the request,
"Show the<br>
number of existing circuits and/or the  <br>
disconnecting means for panel C". Why not just do that?<br><br>
Dick<br><br>
<br><br>
--- You wrote:<br>
Dick:<br><br>
I too am mystifed.  I sent a request for clarification but have
not  <br>
heard back.  It may be some kind of power trip as we have been at
odds  <br>
over many issues.  I will report back.<br><br>
William Miller<br>
Millersolar.com<br><br>
On Dec 11, 2009, at 6:05 PM, Richard.L.Ratico@VALLEY.NET (Richard L 
<br>
Ratico) wrote:<br><br>
> William,<br>
><br>
> No direct specific experience with this, but, respectfully, what
is  <br>
> the problem?<br>
> The code sections seem clear and not unreasonable nor arduous.<br>
><br>
> Dick Ratico<br>
> Solarwind Electric<br>
><br>
><br>
> --- You wrote:<br>
> Friends:<br>
><br>
><br>
> I just received a plan correction for a grid-tie permit
application  <br>
> wherein<br>
> the inspector is questioning compliance with section 225. 
Below is  <br>
> the<br>
> text of the correction notice:<br>
><br>
> The existing panel C in the pump house must comply with NEC 225.31.
225.32<br>
> & 225.33. Show the number of existing circuits and/or the 
<br>
> disconnecting<br>
> means for panel C.<br>
><br>
> Has anyone ever had experience with this section being applied to
a<br>
> grid-tie system?  The inverters will be inside a pump house
remote  <br>
> from the<br>
> main residence.<br>
><br>
> Thanks in advance.<br>
><br>
> William Miller<br>
><br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 9.0.716 / Virus Database: 270.14.103/2558 - Release Date:
12/11/09 02:06:00</blockquote>