<DIV><FONT size=2 face=Calibri>I would go with #1. The solar is obviously 
undersized for the battery bank he has. Another panel + MPPT should give him 
about 25-40% more, depending on temps etc.</FONT></DIV>
<DIV><FONT size=2 face=Calibri></FONT> </DIV>
<DIV>..................................................................................................<BR>Northern 
Arizona Wind & Sun - Electricity From The Sun Since 1979<BR>Solar Discussion 
Forum: <A 
href="http://www.wind-sun.com/ForumVB/">http://www.wind-sun.com/ForumVB/</A><BR>..................................................................................................</DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=markf@berkeleysolar.com href="mailto:markf@berkeleysolar.com">Mark 
  Frye</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">'RE-wrenches'</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Thursday, December 03, 2009 10:22 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] Off-Grid Sizing 
  Case</DIV>
  <DIV><BR></DIV><!-- Converted from text/rtf format -->
  <P><FONT size=2 face=Arial>Folks,</FONT> </P>
  <P><FONT size=2 face=Arial>I have a customer with a 3 year old system  in 
  northern CA:</FONT> </P>
  <P><FONT size=2 face=Arial>8 - Deka 370AH, 6V, 2x4 banks - 740Ah @ 24V</FONT> 
  <BR><FONT size=2 face=Arial>2 - DR2424 120/240V series</FONT> <BR><FONT size=2 
  face=Arial>4 - EC-120-GL</FONT> <BR><FONT size=2 face=Arial>1 - C40 CC</FONT> 
  <BR><FONT size=2 face=Arial>1 - 5000W, old portable gas gen</FONT> </P>
  <P><FONT size=2 face=Arial>The problem is increased gen runtime probally due 
  to chronic undercharging.</FONT> </P>
  <P><FONT size=2 face=Arial>Based on estimated consumption in the home, I think 
  he needs about 2X the PV to meet the energy production needs in the summer (5 
  kWH/day)(30% DOD/day). But in order to get C10 charging during the summer he 
  would need 5X the PV?</FONT></P>
  <P><FONT size=2 face=Arial>Money is and issue. So what should I 
  recommend:</FONT> </P>
  <P><FONT size=2 face=Arial>1 - Increase PV 4X to 5X, add MPPT controller to 
  get to a PV based system with gen support</FONT> <BR><FONT size=2 face=Arial>2 
  - Get a 3K to 5K propane gen and and run as a gen based system with PV 
  support</FONT> <BR><FONT size=2 face=Arial>3 -?</FONT> <BR><FONT 
  face=Arial> </FONT> <BR><FONT size=2 face=Arial>Mark Frye</FONT> 
  <BR><FONT size=2 face=Arial>Berkeley Solar Electric Systems</FONT> <BR><FONT 
  size=2 face=Arial>303 Redbud Way</FONT> <BR><FONT size=2 face=Arial>Nevada 
  City,  CA 95959</FONT> <BR><FONT size=2 face=Arial>(530) 401-8024</FONT> 
  <BR><A href="http://www.berkeleysolar.com"><U><FONT color=#0000ff size=2 
  face=Arial>www.berkeleysolar.com</FONT></U></A><FONT size=2 
  face=Arial> </FONT> </P>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>