class=062260201-21112009>Hi Nick,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>Waddya mean "another supply side tap nightmare"? This 
isn't the first?</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>RE: "Void the listing..." </SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>Let's be honest. I don't know about you or anyone else 
on this list, but I'm pretty sure that e</SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=062260201-21112009>very single supply side connection 
I've seen in wall-mounted meter/main combination service panels has voided the 
listing on the thing. These were factory assembled and listed as 
such. </SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>Just because, "it's been done before", does not change 
the fact that it's not what the panel manufacturer had in mind when the 
thing originally left the factory. This applies to equipment with 
conductors as well as busbars. If they had intended connections such as this, 
they would have provided the means to do it and listed (no pun intended) the 
approved devices on the label inside the cover. The label that is no longer 
legible....</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>If an inspector plays the "all equipment must be listed 
for the use" card, you have a couple options. Smaller PV system on a load side 
connection comes to mind. Larger service panel comes to mind. Different 
service configuration <EM>(i.e. separate meter socket)</EM>, comes to mind. 
Paying for a NRTL to list the final product comes to mind, along with a few cuss 
words. </SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>Pissing up a rope trying to get the guy to back down 
from his 100% defensible position is not jumping out there as a viable 
option to me.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>I'm not exactly sure what you hoped to gain by swapping 
from TW to THHN from a code perspective.... I fully understand your service 
entrance feeder table concept, but what do you gain, really? Other than the 
fact that you will be violating the listing by tapping in that section anyway, 
you can theoretically put up to 110A of PV on that conductor and stay with the 
#1AWG TW (Table 310.16) under all the tap rules, etc. The utility is upstream of 
your connection and the downstream (house) is protected by the 100A main 
breaker. Unless it's an FPE, or Bulldog, or Zinsco... In those cases, Buddha 
alone knows how many amps shall pass and sparks shall fly before the 
breaker trips... </SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>Are you putting in more than 100A of PV on a 
utility service that is sized for 100A? If that's the deal, then a bigger 
service is necessary. <EM>(Side Note: </EM></SPAN></FONT><FONT 
color=#0000ff size=2 face=Arial><SPAN class=062260201-21112009><EM>IMHO, PV 
output capacity greater than the customer's service needs shouldn't qualify 
for Net Metering in any way shape or form.)</EM> </SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=062260201-21112009>Just because the whole listing thing 
around supply side connections is what it is, doesn't mean 
that</SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009> one could not SAFELY accomplish a supply side tap in 
<U><STRONG>some</STRONG></U> of these boxes. <EM>(Note: Double negative = 
positive, in case you missed it.)</EM> </SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=062260201-21112009>Some, but certainly not all. The 
problem is, "Safety" is subjective. What one person calls safe, I might 
not, and vice versa. This is where standards come into place. Standards, such as 
UL XXXX, are developed to define the conditions that constitute safety in 
various products depending on their use. NRTLs judge whether a product meets 
these conditions or not. If the product meets the conditions, the NRTL lists the 
product to such and such a standard. The NEC defers to listing as the 
be-all-end-all. As do building officials in many cases. Some use this as a club 
to hide their own incompetence, no question. That being said, 
we</SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>I wouldn't normally bring all this up in this venue, 
but from what I am seeing, the cat is out of the bag already... The horse has 
left the barn... I suspect that, in most cases, supply side 
connections will largely be a theoretical concept only in the very near 
future. </SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>We must push equipment manufacturers to develop 
products which facilitate safe, code-compliant interconnection at existing 
services. </SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>I would contact a company like 
Marwell  <A 
href="http://www.marwellcorp.com/">http://www.marwellcorp.com/</A>  and 
describe your supply side connection woes.... For small to modest size systems, 
I think going right in behind the meter is best done outside the box.... Look 
for an E/Z 1000-0 meter extender in the configuration you like from this 
page  <A 
href="http://www.marwellcorp.com/online-catalog/5-1000">http://www.marwellcorp.com/online-catalog/5-1000</A>. 
You can order it with KO up to 1". </SPAN></FONT><FONT color=#0000ff size=2 
face=Arial><SPAN class=062260201-21112009>It's not standard a standard 
option for this extender, but tell them you want </SPAN></FONT><FONT 
color=#0000ff size=2 face=Arial><SPAN class=062260201-21112009>NC-400-L clips on 
the load jaws. You will need to get them to buy off on it, but most 
utilities will accept it, though they may want to put a lock on it. 
</SPAN></FONT><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>The trick is getting your neutral conductor routed 
through it. </SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009>It's a place to start...</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=062260201-21112009></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><SPAN class=062260201-21112009><FONT color=#0000ff 
size=2 face=Arial>Matt Lafferty</FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Nick 
Vida<BR><B>Sent:</B> Friday, November 20, 2009 4:37 PM<BR><B>To:</B> 
wrenches<BR><B>Subject:</B> [RE-wrenches] "its a UL listed 
assembly"<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV style="FONT-FAMILY: times new roman,new york,times,serif; FONT-SIZE: 12pt">
<DIV>wow wrenches,<BR><BR>fun solar day for me. Another supply side tap 
nightmare.<BR><BR>Have any of you ran into a situation where the AHJ will not 
let you upgrade the feeders from the meter to the<BR> main breaker because 
it "voids the UL listing"? In this case I had 1 AWG feeding a 100 amp main, but 
it was<BR> type TW which is not on the feeder exception 310.16. In running 
into the typical daftness on 690.64 I asked<BR> if I could replace the 1 
AWG TW with Type THHN so the feeder chart would apply and there would be 
150<BR> ampacity wires feeding the 100 amp main. No luck, all 
frustration.<BR><BR>Any wrenches have any thoughts on this?<BR><BR>Nick 