<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">I agree with the bundling of the DC conductors to separate them from the AC conductors and we do it all the time as our standard installation is inverters and discos over a gutter. We also label them. IE, 240vac and 350VDC. Never had a problem with that in a 4x4 or 6x6 gutter with an inspector in Oregon.<div>Bob-O</div><div><br></div><div><br><div><div>On Sep 24, 2009, at 6:12 PM, Glenn Burt wrote:</div><br class="Apple-interchange-newline">
<div>
<div dir="ltr" align="left"><span class="406405723-24092009"><font color="#0000ff" size="2" face="Arial">We typically bundle the AC separate from the DC conductors to 
retain the 'separated' wording in the code. All in same 4x4 steel 
gutter.</font></span></div>
<div dir="ltr" align="left"><span class="406405723-24092009"><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span class="406405723-24092009"><font color="#0000ff" size="2" face="Arial">-Glenn</font></span></div><br>
<div dir="ltr" lang="en-us" class="OutlookMessageHeader" align="left">
<hr tabindex="-1">
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <b>On Behalf Of </b>Nicholas 
Ponzio, Building Energy<br><b>Sent:</b> Thursday, September 24, 2009 7:02 
AM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> [RE-wrenches] AC & DC in 
Raceway<br></font><br></div>
<div></div>Wrenchers,
<div><br></div>
<div>What's the deal with mixing AC and DC conductors in a raceway? The job in 
question has a 6x6 wireway under the inverters. Conductors will have their 
own conduits but is it ok for them to share the wireway?</div>
<div><br></div>
<div>Thanks in advance for clarification on this,</div>
<div>Nik</div>
<div> </div>
<div><br>--<br>Nicholas Ponzio<br>Building Energy<br>1570 South Brownell 
Road<br>Williston, VT 05495<br><br>t: 802-859-3384 x15<br>f: 802-658-3982<br><a href="http://www.BuildingEnergyVT.com/">www.BuildingEnergyVT.com</a><br><br>"Building 
Solutions for a Sustainable Future"<br><br><br></div></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules & etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div><br></div></body></html>