No problem, so long as the insulation is rated for the highest voltage
conductor.  Conductors of other systems (like premise wiring) can
not be in the raceway.<br><br>
At 07:02 AM 9/24/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">Wrenchers,<br><br>
What's the deal with mixing AC and DC conductors in a raceway? The job in
question has a 6x6 wireway under the inverters. Conductors will have
their own conduits but is it ok for them to share the wireway?<br><br>
Thanks in advance for clarification on this,<br>
Nik<br>
 <br><br>
--<br>
Nicholas Ponzio<br>
Building Energy<br>
1570 South Brownell Road<br>
Williston, VT 05495<br><br>
t: 802-859-3384 x15<br>
f: 802-658-3982<br>
<a href="http://www.BuildingEnergyVT.com">www.BuildingEnergyVT.com</a><br>
<br>
"Building Solutions for a Sustainable Future"<br><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font size=1 color="#0000FF">TM 
</font><font color="#0000FF">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>