I suggest that high rate recharge could be safely done but only with a charge algorithm more sophisticated than what is commonly found in renewable energy gear. <br><br>The chargers typically found in our industry deliver the same "bulk" charge amperage from initiation of the recharge all the way to when the absorption voltage is reached. So...if you set that for a high value the same high rate would be present not only when the battery is highly depleted but also when the battery is approaching 80% state of charge. That seems scary to me.<br>

<br>The electric vehicle industry may offer some good choices in chargers specifically for "rapid recharge". These would deliver highest amps at first but would diminish the amperage as the battery voltage ramps up--without waiting for the absorption voltage to be reached before the amperage taper begins.<br>

<br>You might like to ask the technicians at your battery manufacturer to make sure they're OK with your intended recharge method. Regards to all,<br><br>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br>

<br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">On Tue, Sep 15, 2009 at 9:11 AM, Walt Ratterman <span dir="ltr"><<a href="mailto:wratterman@sunenergypower.com">wratterman@sunenergypower.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">











<div link="blue" vlink="purple" lang="EN-US">

<div>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Peter,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">The DEKA charging manual that I have been working from for their
sealed batteries (AGM and Gel) quote 30% of C20.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">And….DEKA’s literature also has a maximum charging voltage of 2.35
VPC.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Not sure about the other brands.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Thanks,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Walt</span></p><div class="im">

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Peter
Parrish<br>
<b>Sent:</b> Tuesday, September 15, 2009 7:33 AM<br>
<b>To:</b> 'RE-wrenches'<br>
<b>Subject:</b> [RE-wrenches] Charging AGM Batteries</span></p>

</div>

</div>

<p> </p>

</div><p><span style="font-size: 10pt; color: navy;">I have been told that AGM batteries can withstand pretty aggressive
charging rates, with a bulk rate being ˝ of C/20. For example a MK 8A8D, with a
C/20 of 245 A-h, would start with 122 A. If this is okay, can I still use the
standard 14.6 V value for switching from Bulk to Absorb? What about ambient
temperature effects at high charge rates?</span></p><div><div></div><div class="h5">

<p><span style="font-size: 10pt; color: navy;"> </span></p>

<p><span style="font-size: 10pt; color: navy;">We have need from time to time to charge AGMs as quickly as we can
safely do so, so any information on high charge rates would be appreciated.</span></p>

<p><span style="font-size: 10pt; color: navy;"> </span></p>

<p><span style="font-size: 10pt; color: navy;">- Peter</span></p>

<div>

<p><span style="font-size: 10pt; color: navy;"> </span></p>

<p><br clear="all">
</p>

<p><span style="font-size: 10pt; color: navy;">Peter T. Parrish, Ph.D., President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
CA Lic. 854779, NABCEP TM Cert. 031806-26<br>
<a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a> 
<br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885     </span><span style="font-size: 9pt; color: navy;">                                                                                              </span></p>

<p><span style="color: navy;"> </span><span style="color: blue;"> </span></p>

</div>

</div></div></div>

</div>


<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>