<DIV><FONT size=2 face=Arial>Geoff,</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Solar Integrated Technologies adheres its panels 
on ground covers over landfills to capture landfill gases and 
separately produce PV electricity. Perhaps a wrench with Powerlight experience 
can tell us why rigid modules are not laid on a ground cover.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT> </DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=geoff@third-sun.com href="mailto:geoff@third-sun.com">Geoff 
  Greenfield</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Thursday, August 20, 2009 8:35 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] ballasted roof 
  rack - on the ground?</DIV>
  <DIV><BR></DIV>
  <DIV 
  style="FONT-FAMILY: Times New Roman; COLOR: #000000; FONT-SIZE: 12pt">esteemed 
  wrenches (or just steamed if youve been out in the hot lately)
  <DIV><BR></DIV>
  <DIV>I'm curious why more folks don't use the same flat roof ballasted rack 
  approach for large ground mounts?  Geotech weed barier and off we go... 
   my initial calcs sat its a cost saver... my instinct says it viable, but 
  my other instinct says "if it were this easy I would see it all the time (and 
  I've never seen it)</DIV>
  <DIV><BR></DIV>
  <DIV>what's up?  frost heave/instability?  wav-i-ness of the ground? 
  better performance at steep angle worth all the extra cost (not according to 
  my pencil with today's mod costs).  Thoughts? <BR><BR>For a brighter 
  energy future,<BR><BR>Geoff Greenfield<BR>President<BR>Third Sun Solar & 
  Wind Power Ltd.<BR>340 West State Street, Unit 25<BR>Athens, OH 
  45701<BR><BR>740.597.3111     Fax 
  740.597.1548<BR>www.Third-Sun.com<BR><BR>Clean Energy - Expertly 
  Installed<BR><BR><BR><BR><BR><BR><BR>----- "Dave Click" 
  <daveclick@fsec.ucf.edu> wrote: <BR>> Thanks all.<BR>> <BR>> It 
  was my understanding that we should still be running the conductors <BR>> 
  of the same circuit through the same raceway, even if it is the DC input 
  <BR>> into the inverter since that DC oscillates slightly (nowhere near as 
  <BR>> much as AC). I wasn't concerned about eddy currents in the FNMC of 
  <BR>> course but the metal box itself, a concern being voiced on this list 
  <BR>> before. I'd be more concerned about this if it were a 1MW inverter 
  <BR>> rather than a 7kW, but still.<BR>> <BR>> Thanks for the info on 
  the GEC tap and I'm glad the split bolts work here.<BR>> <BR>> The 
  conduit in question doesn't seem to be there just for physical <BR>> 
  protection; the wire runs from the east end of the array for 100'+ and 
  <BR>> only the last 3' are in conduit. If it were only for protection I'd 
  be <BR>> fine with it being open-ended on both ends, but since it's there 
  to feed <BR>> the conductors into the box, that's why I was treating it as 
  a regular <BR>> conduit that required a cord grip at the other end. Where 
  do others make <BR>> the distinction?<BR>> <BR>> Thanks,<BR>> 
  DKC<BR>> <BR>> -------- Original Message --------<BR>> Subject: Re: 
  [RE-wrenches] DC positive and negative in same conduit, <BR>> other 
  inspection issues<BR>> From: Kelly Keilwitz, Whidbey Sun &  Wind 
  <kelly@whidbeysunwind.com><BR>> To: RE Wrenches listserve 
  <re-wrenches@lists.re-wrenches.org><BR>> Date: 2009/8/19 
  21:10<BR>> <BR>> > Dave,<BR>> > Only GEC's are subject to the 
  "continuous" rule (250.64C). It sounds like<BR>> > your are talking 
  about an EGC tapped from the GEC.<BR>> > <BR>> > When splicing PV 
  GEC's required under 690.47D, either together (from<BR>> > separated 
  arrays) or to the existing AC GEC (if close enough), we have been<BR>> > 
  allowed to use split bolts instead of irreversible splices, per 
  250.64D1,<BR>> > "Grounding Electrode Conductor Taps" (at end of 
  paragraph). I.E., the<BR>> > "continuous" rule is only being applied to 
  the main GEC.<BR>> > <BR>> > I agree with Kurt on the LTNMF being 
  used only as extra (not required) wire<BR>> > protection for the USE-2. 
  We often do this when running PV conductors<BR>> > between short 
  separations in modules or rails. I would think that only<BR>> > 
  temperature and fill corrections would apply - and only if the length<BR>> 
  > requires.<BR>> > <BR>> > -Kelly<BR>> > <BR>> > 
  Kelly Keilwitz, P.E.<BR>> > Whidbey Sun & Wind, LLC<BR>> > 
  Renewable Energy Systems<BR>> > NABCEP Certified PV Installer<BR>> 
  > 987 Wanamaker Rd, <BR>> > Coupeville, WA 98239<BR>> > PH 
  & FAX 360-678-7131<BR>> > sunwind@whidbeysunwind.com<BR>> > 
  <BR>> > On 8/19/09 2:41 PM, "Dave Click" <daveclick@fsec.ucf.edu> 
  wrote:<BR>> > <BR>> >> For the grounding electrode wiring, it 
  seems that it's fine to me since<BR>> >> they ran the continuous #6 
  to each rail and then to the rod, qualifying<BR>> >> as the 690.47(D) 
  supplemental electrode. But the split bolts tapping<BR>> >> that GEC 
  to "ground the disconnect," these are required to be<BR>> >> 
  irreversible connections to the ground bus in that disconnect, right?<BR>> 
  > <BR>> > <BR>> >  <BR>> > <BR>> > <BR>> 
  > <BR>> > _______________________________________________<BR>> 
  > List sponsored by Home Power magazine<BR>> > <BR>> > List 
  Address: RE-wrenches@lists.re-wrenches.org<BR>> > <BR>> > Options 
  & settings:<BR>> > 
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR>> 
  > <BR>> > List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR>> 
  > <BR>> > List rules & etiquette:<BR>> > 
  www.re-wrenches.org/etiquette.htm<BR>> > <BR>> > Check out 
  participant bios:<BR>> > www.members.re-wrenches.org<BR>> > 
  <BR>> > <BR>> _______________________________________________<BR>> 
  List sponsored by Home Power magazine<BR>> <BR>> List Address: 
  RE-wrenches@lists.re-wrenches.org<BR>> <BR>> Options & 
  settings:<BR>> 
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR>> 
  <BR>> List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR>> 
  <BR>> List rules & etiquette:<BR>> 
  www.re-wrenches.org/etiquette.htm<BR>> <BR>> Check out participant 
  bios:<BR>> www.members.re-wrenches.org<BR>> <BR>> </DIV></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>