<DIV>Our most troublesome areas are in older parts of So Cal (i.e. Pomona) with 
higher AC loads.  The ancient and undersized transformers just can't 
compensate for the sag, especially at the end of the line.  Edison WILL 
replace the transformer after the DG customer and all of his fiends and 
neighbors harass customer service for about two years... or when it 
blows.  </DIV>
<DIV>The dream wrench org..... when we finally wake up and put one together I 
hope I'm still around. Right now CalSeia is just about the only game in CA town, 
as far as Big Tent SOLAR  is concerned and I gotta believe herding 
cats would be a good deal easier.</DIV>
<DIV>Pat Redgate</DIV>
<DIV>Ameco Solar</DIV>
<DIV>PS Yes, I think it is time to find an attorney.... and there's a whole 
bunch of 'em in Sacramento.  But I also think it's a legitimate idea to 
rethink voltage bandwidth at the PUC and PA forums. I believe all of Michael's 
assumptions are low.</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>
<DIV>In a message dated 8/16/2009 10:42:54 A.M. Pacific Daylight Time, 
michael.welch@re-wrenches.org writes:</DIV>
<BLOCKQUOTE style="PADDING-LEFT: 0px; MARGIN-LEFT: 0px"><FONT 
  style="BACKGROUND-COLOR: transparent" color=#000000 size=2 face=Arial>Please 
  check my math, I did it pretty quickly.<BR><BR>CA has over 450 MW of 
  distributed PV systems. At around, say, 4.5 average daily sun hours (it is 
  probably more, averaged over the state's systems), that would be 540,000 MWh 
  each year.<BR><BR>If the utilities are dropping out of spec, say, 1% of the 
  time, that's 5,400 MWh of loss each year. At 15 cents a kWh (the average is 
  probably more) that turns out to be $81,000 worth of losses to us.<BR><BR>That 
  does not seem like a whole lot , but the number will grow as fast as PV 
  installations are.<BR><BR>Maybe it is time for a class-action lawsuit against 
  the utilities. Or time for the dream Wrench organization to file with the CPUC 
  for relief in the form of stricter utility specs, or petition UL for looser 
  inverter specs.<BR><BR>One question, why are inverters required to drop out 
  for out of spec voltage and frequency? It seems to me that the UL requirements 
  are overly limiting in that regard. I mean, if the utility can do it with 
  their huge plants, why can't we with our little ones?<BR><BR>William Korthof 
  wrote at 10:06 AM 8/16/2009:<BR><BR>>I'm beginning to wonder if the allowed 
  voltage range for grid-tie inverters (+/-10%) is too sensitive in some 
  networks and contributes more harm than benefit. This is close to 
  home.<BR>><BR>>We actually have a significant number of customers who've 
  had trouble with grid voltage causing their systems to go offline at various 
  times. I think most or all are SCE 
customers.<BR><BR></FONT></BLOCKQUOTE></DIV></FONT><DIV CLASS="aol_ad_footer" ID="c23266eeeb99ffb621c211b85ac7ade4"><br/><font style="color:black;font:normal 10pt arial,san-serif;"> <hr style="margin-top:10px"/></font></DIV></BODY></HTML>