<font size=3>Dick:<br><br>
I don't believe you have solved Brian's dilemma yet.  It is my
understanding that if one is going to install a load side tape, the back
feed calculations need to work for every link of the distribution system
upstream to the meter.  In the scenario you suggest, that will not
be the case.  The 100 amp meter main on Brian's project will
still  accept only 20 amps of PV AC feed, still not satisfying his
requirements.<br><br>
I may not have read Brian's original post closely enough.  If Brian
needs to feed 40 amps of PV derived AC and he wants to do it via the load
side connection allowed by 690.63 (B), he has two choices: 
<br><br>
<x-tab>        </x-tab>A. He can
upgrade all of the distribution to 200 amps  from the meter to his
point of connection.  The arithmetic is simple:  200 * 120% =
240 amps.  240 -200 = 40 amps of PV feed allowed.<br>
<x-tab>        </x-tab>B. He can
upgrade all of the distribution to at least 125 amps capability and leave
the 100 amp main breaker.  This would require that all of his
distribution be upgraded, from the bus in the main disconnect to the
feeder wire to the sub-panels. 125 * 120% = 150 amps. 150 - 100 = 50 amps
of PV feed allowed.<br><br>
Logistically, there is not a lot if difference between A and B.<br><br>
See our web site,
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com/</a>,
for a point-of-connection calculator.  <br><br>
Thanks for the advice on Milbank.  I will not be needing any 200 amp
breakers as there is no need to up-size a breaker, instead I would be
generating more spare 200 amp main breakers.<br><br>
William<br><br>
<br>
At 12:20 PM 8/1/2009, you wrote:<br>
<blockquote type=cite class=cite cite>William,<br><br>
I stand corrected. Thank you. <br><br>
This is not a supply side tap. I should have said it was a tap on the
supply<br>
side of the panelboard main breaker. That said , I think it works and
meets<br>
code, provided the conductors spliced to the feeder are properly sized.
The<br>
panelboard busbar is protected by it's main breaker and cannot be
overloaded by<br>
the solar contributuion. <br><br>
On your other point, Milbank makes a 200 amp MMC that that can be
retrofitted<br>
with a 100 amp breaker. I have done this twice, but not because of a
solar<br>
install. We've had a couple 100 Amp, 300', underground service laterals
that<br>
required oversized conductors because of voltage drop. The Milbank 100
Amp<br>
equipment is physically too small to do this. In both cases we replaced
the very<br>
expensive 200 amp breaker with an also very expensive 100 amp breaker,
all by<br>
Milbank and labeled as such. I was told by my supplier it was impossible
to<br>
purchase a 200 amp Milbank MMC with the 100 A breaker preinstalled. The
100 A<br>
breaker is the same physical size as the 200 and fits right in, no
modifications<br>
required. I have two 200 amp Milbank breakers on my shelf if you need
them. The<br>
MMC units are very expensive to begin with. Here in VT / NH a basic meter
only<br>
enclosure is more often pared with a separate disconnect enclosure
through an<br>
offset or straight nipple. This combination might work for you,
substituting a<br>
load center for the disconnect.<br><br>
Dick Ratico<br>