Hi Folks,<div><br></div><div>Can anyone provide code reference or advice on this question?</div><div>Our customer has 100 amp service at the meter pedestal, 100 amp main breaker feeding 200 foot underground run to a 100 amp panel at the house. We need to land a 40 amp breaker, so are proposing to replace main panel at house with 200 amp panel. The AHJ says we need a 200 amp main breaker in this panel, which will work, but says this requires upsizing the feeder, main breaker at meter, and therefore utility service to 200 amps.</div><div><br></div><div>I've read on this list and elsewhere about downsizing the main breaker in a panel to create capacity to make the 120% rule. This AHJ says you can't put in a breaker smaller than the panel size, and furthermore, everything upstream would have to be upsized. Is this from the code?<br><br><div> <span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Palatino; font-size: 14px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-align: auto; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0; "><div>Bruce Erickson</div><div>Mendocino Solar Service</div><div>PO Box 1252</div><div>Mendocino, CA 95460</div><div>707-937-1701</div><div><br class="webkit-block-placeholder"></div></span><br class="Apple-interchange-newline"> </div><br></div></body></html>