<P></FONT><FONT size=3>Solar Pros,</FONT><FONT face=Arial size=1><FONT 
face=Arial size=1> </FONT></FONT></P>
<P>I've had real reservations about using traditional bus-type combiners that 
fit 2/0 down to #10 awg wires. They are almost always a poor fit and electrical 
connection for smaller gauge wires. </P>
<P></FONT><FONT face=Arial>A neat solution I found to make 100% 
contact with all screw-type connectors, I started using a "bootlace" 
ferrule on the wire ends. The thinwall copper/tin sleeve will crimp easily onto 
the wire and is easily compressed into a form matching the connector 
jaws. I use it exclusively on DIN rail type terminal blocks and would 
use it on larger wires >#10 but the Paladin 4-jaw crimper only goes up to 
#10.</FONT></P></DIV>
<DIV><FONT face=Arial>The internal jumper makes an excellent connection to 
any number of dist blocks using threaded rather than compression connections. 
</FONT></DIV>
<DIV><FONT face=Arial></FONT> </DIV>
<DIV><FONT face="Times New Roman"><SPAN 
id=ctl00_contentMain_repProductSummary_ctl00_uctlProductSummary_lblAlliedSKUTitle 
style="FONT-WEIGHT: bold">Alliedelec.com</SPAN>   </FONT></DIV>
<DIV><FONT face="Times New Roman"><SPAN 
id=ctl00_contentMain_repProductSummary_ctl00_uctlProductSummary_lblAlliedSKU><B><B>400-0144 
ferrule</B></B></SPAN></FONT></DIV>
<DIV><FONT face="Times New Roman"><SPAN><STRONG>889-1441 
crimper</STRONG></SPAN></FONT></DIV>
<DIV><FONT face="Times New Roman"><SPAN> <SPAN 
id=ctl00_contentMain_repProductSummary_ctl00_uctlProductSummary_lblAlliedSKU><STRONG>502-3240 
internal jumper</STRONG></SPAN></SPAN></FONT></DIV>
<DIV><FONT face="Times New Roman"><SPAN><SPAN> <SPAN 
id=ctl00_contentMain_repProductSummary_ctl00_uctlProductSummary_lblAlliedSKU><B><B>502-3744 
terminal blk</B></B></SPAN></SPAN></SPAN></FONT></DIV>
<DIV><FONT 
face="Times New Roman"><SPAN><STRONG></STRONG></SPAN></FONT> </DIV>
<DIV><FONT face=Arial><SPAN>Jim Duncan<BR>North Texas Renewable Energy 
Inc<BR>817.917.0527<BR><A 
href="mailto:ntrei@earthlink.net">ntrei@earthlink.net</A><BR><A 
href="http://www.ntrei.com">www.ntrei.com</A> </SPAN></FONT></DIV>
<DIV><FONT face=Arial><SPAN>
<HR>
</SPAN></FONT></DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=dan@foxfire-energy.com 
  href="mailto:dan@foxfire-energy.com">dan@foxfire-energy.com</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, July 27, 2009 6:17 AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] CBI circuit 
  breakers</DIV>
  <DIV><BR></DIV><SPAN 
  style="FONT-SIZE: 10pt; COLOR: #000000; FONT-FAMILY: Verdana">The only problem 
  I've had with them is that their connectors can allow multi stranded wire to 
  "broom out", (after installation) -- causing a loose / high resistance 
  contact. I've learned to torque / wiggle & twist and retorque all multi 
  strand connections. I have had one side of a 60A QO breaker go open out of the 
  blue. db<BR><BR><BR>Dan Brown<BR>President<BR>Foxfire Energy 
  Corp.<BR>Renewable Energy Systems<BR>(802)-483-2564<BR><A 
  href="http://www.Foxfire-Energy.com" 
  mce_href="http://www.Foxfire-Energy.com">www.Foxfire-Energy.com</A><BR>NABCEP 
  #092907-44<BR><BR>
  <BLOCKQUOTE 
  style="PADDING-LEFT: 8px; FONT-SIZE: 10pt; MARGIN-LEFT: 8px; BORDER-LEFT: blue 2px solid; COLOR: black; FONT-FAMILY: verdana" 
  webmail="1">
    <DIV>-------- Original Message --------<BR>Subject: Re: [RE-wrenches] CBI 
    circuit breakers<BR>From: Allan Sindelar 
    <allan@positiveenergysolar.com><BR>Date: Mon, July 27, 2009 1:36 
    am<BR>To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org><BR><BR>I 
    have had no problems to date, Kent. Can you be more specific as to 
    what<BR>problems you have had? <BR><BR>Allan 
    Sindelar<BR>Allan@positiveenergysolar.com<BR>NABCEP Certified Photovoltaic 
    Installer<BR>EE98J Journeyman Electrician<BR>Positive Energy, Inc.<BR>3201 
    Calle Marie<BR>Santa Fe, New Mexico 87507<BR>505 424-1112<BR><A 
    href="http://www.positiveenergysolar.com" target=_blank 
    mce_href="http://www.positiveenergysolar.com">www.positiveenergysolar.com</A><BR><BR>-----Original 
    Message-----<BR>Is it just me, or have other wrenches had problems with the 
    CBI circuit <BR>breakers used in the Outback or Midnite combiner 
    boxes?<BR><BR>Kent Osterberg<BR>Blue Mountain Solar, Inc.<BR><A 
    href="http://www.bluemountainsolar.com/" target=_blank 
    mce_href="http://www.bluemountainsolar.com/">http://www.bluemountainsolar.com/</A><BR><BR><BR>_______________________________________________<BR>List 
    sponsored by Home Power magazine<BR><BR>List Address: 
    RE-wrenches@lists.re-wrenches.org<BR><BR>Options & settings:<BR><A 
    href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" 
    target=_blank 
    mce_href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
    <A href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" 
    target=_blank 
    mce_href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
    rules & etiquette:<BR><A href="http://www.re-wrenches.org/etiquette.htm" 
    target=_blank 
    mce_href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A><BR><BR>Check 
    out participant bios:<BR><A href="http://www.members.re-wrenches.org" 
    target=_blank 
    mce_href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</A><BR><BR></DIV></BLOCKQUOTE></SPAN>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options & 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules & etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>