<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:12pt"><div>hey Wrenches.<br><br>I opened my soon to be installed fronius IG Plus to see what was going on in there, and found myself a bit disappointed. There is a 6 string combiner in there which is fine, however there is no bypass for the fusing section and the terminals are rated at 20 amps. In a situation where you have 6 strings, you cannont combine on the roof and run down with a pair of conductors, instead you must run down with your strings. This means instead of running 3/4 conduit for 8awg pair and ground, I would have to run 1" conduit for 6 pairs of 10 awg and ground. <br>(thats a lot of flex for a 2x4!!)  So if I need a disconect on the roof, I would need 2 disconects, and correct me if im wrong-- but i would need 4 disconects in the future because this is a transformerless inverter.
 <br>I also noticed that they are still using those mediocre white plastic terminals for the ac connection that so many people found annoying.<br>And fyi, there are no fuses in the fusing section, so dont forget to order them.<br><br></div></div><br>